View Full Version : What is nec 410.16?
tsrdesigns
Jul 13, 2010, 03:27 PM
Just a quick question.
stanfortyman
Jul 13, 2010, 04:00 PM
410.16 Luminaires in Clothes Closets.
(A) Luminaire Types Permitted. Listed luminaires of the following types shall be permitted to be installed in a closet:
(1) A surface-mounted or recessed incandescent luminaire with a completely enclosed lamp
(2) A surface-mounted or recessed fluorescent luminaire
(3) Surface-mounted fluorescent or LED luminaires identified as suitable for installation within the storage area
(B) Luminaire Types Not Permitted. Incandescent luminaires with open or partially enclosed lamps and pendant luminaires or lampholders shall not be permitted.
(C) Location. The minimum clearance between luminaires installed in clothes closets and the nearest point of a storage space shall be as follows:
(1) 300 mm (12 in.) for surface-mounted incandescent or LED luminaires with a completely enclosed light source installed on the wall above the door or on the ceiling
(2) 150 mm (6 in.) for surface-mounted fluorescent luminaires installed on the wall above the door or on the ceiling
(3) 150 mm (6 in.) for recessed incandescent or LED luminaires with a completely enclosed light source installed in the wall or the ceiling
(4) 150 mm (6 in.) for recessed fluorescent luminaires installed in the wall or the ceiling
(5) Surface-mounted fluorescent or LED luminaires shall be permitted to be installed within the storage space where identified for this use.
Stratmando
Jul 13, 2010, 06:32 PM
Stan, it bites that the Quick questions seldom have quick answers?
310.16 concerning ampacities is more interesting?
stanfortyman
Jul 13, 2010, 07:16 PM
310.16 is a mine field to the uninformed. :P
tkrussell
Jul 14, 2010, 07:30 AM
Which edition of the National Electric Code?
Stan quoted the current code in effect, 2008 edition.
The Section 410.16 in the 2005 edition was Means of Support.
This section is often mentioned in installation instructions of light fixtures that the installation of the fixture must comply with NEC Section 410.16.
The instructions may not have been updated.
stanfortyman
Jul 14, 2010, 09:33 AM
Good point TK, I never thought of that.
You'd think they would leave a few more numbers in between rather than leaving the section number the same and changing the topic.
Gotto love the NEC... NOT!