Have a Goodman GMT115-5B Natural Gas. Burners fire and blower comes on. If it has run for a longer period (not too long in my opinion), burner cycles on and off while blower is still running. Burner will ignite burn for 45-60 seconds and shut off then cycle back on again. Cycle will continue to repeat until thermostat reaches temp. Any thoughts?

Joshdta
Nov 9, 2009, 04:02 PM
Air filter dirty, gas pressure to high, return or supply registars closed. Or a week limit.

KC13
Nov 9, 2009, 05:08 PM
If the circuit board has a diagnostic LED, it will provide clues.

novicehvac
Nov 11, 2009, 03:54 PM
Have a Goodman GMT115-5B Natural Gas. Burners fire and blower comes on. If it has run for a longer period of time (not too long in my opinion), burner cycles on and off while blower is still running. Burner will ignite burn for 45-60 seconds and shut off then cycle back on again. Cycle will continue to repeat untill thermostat reaches temp. Any thoughts?

Now, the burners come on and fire for 12-14 second then shut off, and cycle repeats. I have checked and indicator light is not flashing, no error codes are showing.

Thoughts?

Joshdta
Nov 11, 2009, 03:57 PM
Could be the limit switch or the flame sencer

KC13
Nov 11, 2009, 03:59 PM
Try bypassing the thermostat to see if cycle is sustained. Connect "R" and "W" circuits together, either at thermostat location or at furnace.

novicehvac
Nov 11, 2009, 10:18 PM
could be the limit switch or the flame sencer

Cleaned the flame sensor, changed the filter, by-passed the stat. No change in propblem. Which limit switch and can I check it myself?

Joshdta
Nov 12, 2009, 03:36 PM
http://store.hamiltonhomeproducts.com/ProductImages/limitswitches/025-29041-005.jpg