View Full Version : Wire and Breaker size


JKc
Mar 2, 2008, 01:44 PM
I am installing a steam generator for a steam shower. The unit draws 38 amps. I need a GFCI breaker. The run is 35 feet. What size wire and breaker do I need?

Stratmando
Mar 2, 2008, 01:55 PM
2 #6's for hots, #10 for ground, and a #8 for Neutral. 50 Amp GFI breaker. 3/4" Conduit.

stanfortyman
Mar 2, 2008, 02:53 PM
I am installing a steam generator for a steam shower. The unit draws 38 amps. I need a GFCI breaker. The run is 35 feet. What size wire and breaker do I need?Is this 240V or 120/240V?
Most steam gennys I have wired were straight 240v thus requiring X/2NM cable w/ground.
In your case 6/2NM would be correct. Unless you run conduit the WHOLE way, then you can use two #8THHN with a #10 ground.