:confused: What should the pressure drop across the coil be on a chilled water unit ? I have a pressure of 40 psi incoming and 40 psi going out of the unit. I don't know the flow rate at this time but I'am working on it. Can someone help.

caibuadday
Aug 25, 2007, 02:04 PM
:confused: What should the pressure drop across the coil be on a chilled water unit ? I have a pressure of 40 psi incoming and 40 psi going out of the unit. I don't know the flow rate at this time but I'am working on it. Can someone help.normal 5 to 10 psi... you should have press drop... check your gauges...
Q = (FR x 60 x 8.33) TD
Q= total load in BTU per hr, 8.33 pound per gal of water, FR= flow rate in gal per minute, 60 minute, TD temps differential