![Ask Experts Questions for FREE Help !](custom/vgo/images/amhd_logo_os.png) |
|
|
![dryfly3's Avatar](/images/avatars/default_avatar.gif) |
New Member
|
|
Aug 11, 2010, 09:04 AM
|
|
Convert 220vac, 2-wire and ground, to 110vac
Is it possible to convert a 220vac, 10AWG, line with only 2 black hot wires and a bare ground wire to a 110vac line? Can the source at the main junction box, which has a 2-pole CB, be rewired to replace the 2-pole breaker with a 1-pole breaker and grab the neutral at the main box by connecting one of the black wires to neutral at the box?
Is it to code to use one of the 2 black hot wires as a neutral?
|
|
![Stratmando's Avatar](image.php?u=141352&dateline=1182281194) |
Uber Member
|
|
Aug 11, 2010, 09:14 AM
|
|
Tape the 1 wire with white tape at both ends, connect one end to neutral bar, the other to the white screw on the receptacle, install 1 20 amp single pole breaker.
You will have to wirenut a short piece of # 12 to allow making it around the screws.
|
|
![donf's Avatar](image.php?u=194608&dateline=1199242453) |
Printers & Electronics Expert
|
|
Aug 11, 2010, 09:18 AM
|
|
Absolutely not!
Neutral conductor insulation can be Gray (usually used in commercial installations) or White.
Please see NEC 2008, Chapter 2 article 200.6 (Neutral Identification) and 200.7 (Use of White or Gray)
Can you remove a 240 circuit and use one of the spots for a new 120 VAC circuit breaker, yes. However, you can only use a 20A or 15A breaker. You could use the cable that is installed already if it were a Black/White and bare ground. However, you would have to pigtail the receptacle to the 10AWG cable because it will not attach properly to the receptacle.
P.S. You are also required to cover the empty slot in the panel by using a blank on the panelboard cover grill.
|
|
![hwolfla's Avatar](/images/avatars/default_avatar.gif) |
New Member
|
|
Sep 7, 2016, 12:14 PM
|
|
If you get a 12 vdc power supply that will accept 220 vac 50 Hz (LED POWER SUPPLY) you take the 12 vdc output and connect it to a 120 vac inverter that runs off 12 vdc. A 12 vdc 30 amp power supply will provide enough power to run a 360 watt inverter. This will allow you to run equipment that needs 120 vac 60 hz off 220 vac 50 hz like in AU. You can wire the power supply to the inverter, tape the two together and you have a nice small package that will provide 120 vac 60 HZ for such things like motors that require 60 HZ, or other equipment rated at 120 vac 60 HZ. The cost of power supplies have come way down due to their use for LED power sources. Likewise, 360 watt inverters can be purchased for under $30. The total cost of a 360 watt
Power system can be just over $50. Easy to do, and works great.
Hank Wolfla
Greenfield, IN
Sept. 2016
|
|
![ma0641's Avatar](/images/avatars/default_avatar.gif) |
Uber Member
|
|
Sep 7, 2016, 12:31 PM
|
|
![Quote](custom/vgo/images/misc/quote_icon.png) Originally Posted by hwolfla
If you get a 12 vdc power supply that will accept 220 vac 50 Hz (LED POWER SUPPLY) you take the 12 vdc output and connect it to a 120 vac inverter that runs off 12 vdc. A 12 vdc 30 amp power supply will provide enough power to run a 360 watt inverter. This will allow you to run equipment that needs 120 vac 60 hz off 220 vac 50 hz like in AU. You can wire the power supply to the inverter, tape the two together and you have a nice small package that will provide 120 vac 60 HZ for such things like motors that require 60 HZ, or other equipment rated at 120 vac 60 HZ. The cost of power supplies have come way down due to their use for LED power sources. Likewise, 360 watt inverters can be purchased for under $30. The total cost of a 360 watt
Power system can be just over $50. Easy to do, and works great.
Hank Wolfla
Greenfield, IN
Sept. 2016
Why spend the money when all you need to do is make 1 wire white and possibly pigtail a wire or two?
|
|
![stanfortyman's Avatar](/images/avatars/default_avatar.gif) |
Electrical & Lighting Expert
|
|
Sep 7, 2016, 05:27 PM
|
|
![Quote](custom/vgo/images/misc/quote_icon.png) Originally Posted by ma0641
Why spend the money when all you need to do is make 1 wire white and possibly pigtail a wire or two?
Hank could also check the dates of the posts he is replying to and see that it is six years old.
|
|
![ma0641's Avatar](/images/avatars/default_avatar.gif) |
Uber Member
|
|
Sep 7, 2016, 05:46 PM
|
|
Dummie Brian too!
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Convert 220 VAC 1Phase to 2-110VAC circuits
[ 6 Answers ]
I have a 220VAC single phase 30 amp circuit that I would like to split into two 110VAC circuits. The 220VAC circuit has 3 wires and if I measure across the two main terminals I get the 220VAC and if I measure between a main terminal and what appears to be ground, I get the 110VAC. If I take one of...
How to convert 220vac to 110vdc
[ 2 Answers ]
I have a shunt release with 220vac power supply but actually the line power supply is 110vdc,what should I do?
How to wire a 220VAC outlet from 2) 120VAC feeds?
[ 5 Answers ]
In my garage, I have a subpanel, which has the supply coming in on three black (one has white tape around it--I'm assuming this one is the neutral wire) heavy duty wires. 2 of the wires have 115VAC each. There's a grounding rod about 3 feet from the panel. A thick bare wire in a flex conduit...
Can you use Metal Conduit as ground to convert 2 wire to 3 wire?
[ 3 Answers ]
I need to convert an old cinder block house from 2 wire outlets to 3 wire by adding a ground to all outlets.
Since the entire house is cinder block, all the circuits from the basement breaker box are in flexible metal conduit and metal outlet boxes...
Is it possible to use the metal conduit...
View more questions