    Bowler's Avatar
    Bowler Posts: 133, Reputation: 2
    Junior Member
     
    #1

    Sep 5, 2008, 07:03 PM
    Portable generator No Output
    I have a Generac 5500 Watt generator model 09778-3 that has approx 5 hours of total use on it. I went to use it a couple of weeks ago to power a 1-1/2 HP pump that draws approx 9 amps at 240 volts. I had used this generator for this purpose before with good results. This time the generator ran under load for approx 30 seconds and all of a sudden speeded up a bit. Further checks showed that there was no output of any kind. Even the solenoid voltage for the idle slowdown under no load conditions, wasn't there. Absolute zero on any plug. Each pushbutton circuit reset button was pushed and no results.
    I checked with all the "Authorized" Service centers here locally and all but one didn't work on the generator portions. I took to the one service center and they took the generator to work on. First of all, they were very cautious about taking it at all, because "they usually didn't work on generators."
    Their prognosis was that the stator was shorted. I hadn't noticed any smoke, smell or anything when it had quit generating. The mechanic admitted that he had taken his readings with an analog meter, and my being an electrician by trade, I know that motor/generator readings are so low that an analog meter won't give you accurate readings. I can take readings with a fluke digital meter and I do have a wiring diagram, but I have no idea what these readings should be. Can any one be of any help. This generator looks brand new and has an 11 HP B&S motor that runs like a top. I have talked to Generac and because the whole unit is 4 years old, it is out of warranty, even though it only has the 5 hours on it. Mechanic quoted $785.00 plus shipping plus labor to install stator. Pretty steep for a generator that you can buy new for less than $600.00. Brushes, comutator etc look like new.
    I would really like to check it out a little further myself. Does anyone have suggestions or know where I can get resistance readings for stator. I sure would appreciate it.
    Credendovidis's Avatar
    Credendovidis Posts: 1,593, Reputation: 66
    -
     
    #2

    Sep 5, 2008, 07:12 PM
    Hello Bowler

    Actually you have already found the cause of the problem.
    You stated : "Even the solenoid voltage for the idle slowdown under no load conditions, wasn't there." I would spend my time on checking WHY there is no such voltage, as that voltage is normally used to induce the start magnetic field on which the generator can generate the full magnetic field and the output electric power.
    Look at the magnets that generate that solenoid voltage. Are they still sufficiently magnetized? If not replace them (Radio Shack). Or disconnect the output of that selenoid and see if there is a short on that line elsewhere in the generator.

    Success !

    :)
    Bowler's Avatar
    Bowler Posts: 133, Reputation: 2
    Junior Member
     
    #3

    Sep 6, 2008, 09:38 AM
    I will be out there checking today. But I am not quite sure what magnets I am looking for. Are we talking about the magnets inside of the generator or is there something I am missing here? Surely the magnets inside the generator can't be replaced at Radio Shack.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    Sep 6, 2008, 09:57 AM
    I'd be looking for some kind or short circuit, or open circuit, in the load sensor. Try disconnecting completely to see if you can get any output to the receptacles.
    Bowler's Avatar
    Bowler Posts: 133, Reputation: 2
    Junior Member
     
    #5

    Sep 8, 2008, 12:06 PM
    I have schematic for this generator and the idle control solenoid voltage comes right out of the system control board. The DPE windings come out of a power regulation board. Boards are expensive. Is there any way to check these out? If anyone is interested, schematic of this generator is in a pdf format at
    http://www.generac-portables.com/doc...8_7EN2W_LO.pdf
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #6

    Sep 8, 2008, 12:41 PM
    This is almost like infant mortaility. I'd check any connections you can find for corrosion and/or looseness. Then I'd disconnect al the generator points and measure the resistance and the resistance to the case. I expect all readings to be low except the ones to the case. You won't be able to measure 1 ohm or less, so don't worry about it.

    Write down the readings and we'll go from there. There isn't much troubleshooting info there when there is no equlivelent circuit diagram on the control boards.

    I'd also be interested in the voltage between 11 and 44 with and without the power regultor board disconnected.
    Bowler's Avatar
    Bowler Posts: 133, Reputation: 2
    Junior Member
     
    #7

    Sep 8, 2008, 05:07 PM
    At this point, I suspect the power reg board myself. I will get back to you. Already took all thee resistance readings but didn't write them down. All looked normal to me with total infinity to ground. Will recheck in the morning and get back to you. Thanks for your interest.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #8

    Sep 8, 2008, 06:09 PM
    Double check your model number and cinfirm back to us. Generac has a breaker protecting the out put but you've checked that by now, right?
    Bowler's Avatar
    Bowler Posts: 133, Reputation: 2
    Junior Member
     
    #9

    Sep 8, 2008, 10:29 PM
    Model 09778-3 There are 4 pushbutton circuit reset buttons. One for each circuit. I have not found one for a main circuit breaker. Yes I have checked the 4 I found. Even if one was tripped, the others would work the way it's wired.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #10

    Sep 9, 2008, 06:10 AM
    Are you checking for continuity across the circuit breakers or just resetting? From the wiring diagram it appears that if a 30 amp is tripped it affects one of the 20 amps.
    Bowler's Avatar
    Bowler Posts: 133, Reputation: 2
    Junior Member
     
    #11

    Sep 9, 2008, 09:39 AM
    By the way, if you are looking for the model # somewhere else, use 09778 Don't use the -3 as this is apparently a sub model # or something. All schematics etc come up just using the 09778.
    Bowler's Avatar
    Bowler Posts: 133, Reputation: 2
    Junior Member
     
    #12

    Sep 9, 2008, 03:32 PM
    Well gentlemen... I am giving up on this generator and will post on Craig's list as is... but I did get the readings as requested. All readings were taken with a Fluke digital meter. The generator output across #11 and #44 was identical with or without the power regulator board connected or disconnected. Started at about 7 volts AC and dwindled down to about 1.75 volts.

    Main power windings read .36 and .38 ohms All readings were taken with leads disconnected and coming directly out from generator. Specs supposed to be from .26-.36 ohms.

    DPE exciter leads lifted and they read 2.14 ohms. Specs 2.26-2.8 ohms

    Across wire terminals 1 and 4, ( field leads) .56 ohms

    There is one big discrepancy and that the Clymers book that I just purchased, says that there should be infinity between DPE and power leads. I only have about 2.5 ohms between these leads. Infinity to ground. I question this infinity reading between leads, as I look at the Generac circuit on this generator and see Wire #2 and Wire #22 are connected and that would be 0 ohms between the leads. I have tried flashing the fields, both with a drill motor and with a 12 volt battery. Didn't do anything.

    I thank all of you for your input and if you do have some more input, I'll gladly look it over.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #13

    Sep 9, 2008, 07:34 PM
    I would not give up just yet unless a genrac authorized repair/dealer says its not worth fixing. We sent thousands of this model top Iraq as did Nato. Somebody must know how to fix it.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #14

    Sep 9, 2008, 10:05 PM
    You looked at the wrong voltages:

    Look at DPE (2,6) with and without the power regulator board connected.

    Also look at the field (+,-) as a DC voltage when the regulator board is connected.

    What probably happens is this:

    DPE creates an AC voltage using the residual madnetism in the generator. It's rectified to a DC voltage and turned on and off by the shield gate signal and this excites the field. This is similar to a car alternator EXCEPT that there is no residual magnetism. The snubber feedback is probably a current limit. The residual magnetism is probably coming from the field, hence flashing the field.

    So, I am expecting an AC voltage at DPE when the power regulator board is connected and disconnected. If that's not there, then you have a generator problem.

    The shield gate signal is probably relative to pin 22.

    Bet you don't hava an AC voltage at DPE with power regulator board disconnected and you don't have a DC voltage across the field terminals.

    Then you need to look at the shield gate signal. The question is What's it relative to? Pin 22?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #15

    Sep 9, 2008, 11:50 PM
    The rest of the circuit depends on a few things. The idle coil could be a voice coil positioner or a stepper or a motor. No idea.

    Low oil pressure lights a LED and kills the engine.

    The idle switch determines if it runs at the proper frequency all the time. i.e. If the idle speed reduces under no load. Have no idea of the sense of the switch from the schematic.

    The idle control transformer is really a current transformer. Note that it's in SERIES with the output. A voltage between 155 and 156 determines whether current is flowing. If it is then the idle control coil maintains 60 Hz.

    Looks like some voltage feedback might be between pins 22 and 11. That could be used for overvoltage protection. Just a guess.

    It looks as though the output is isolated UNLESS the customer ground lug is used.

    PS: I didn't read the manual. Just the schematic pages 14 and 15.
    rohmell's Avatar
    rohmell Posts: 5, Reputation: 1
    New Member
     
    #16

    Jan 24, 2010, 11:26 AM
    I suggest reading this article:

    http://www.endtimesreport.com/dead_gen.html
    Bowler's Avatar
    Bowler Posts: 133, Reputation: 2
    Junior Member
     
    #17

    Jun 28, 2010, 06:47 PM

    I finally gave up on this generator. I found someone that was willing to buy the unit and wanted to take the generator off and install a portable water pump. Worked for him and it worked for me. Thanks all for the help and interest.
    bigjim161's Avatar
    bigjim161 Posts: 1, Reputation: 1
    New Member
     
    #18

    Feb 23, 2012, 08:36 PM
    I have a 750w 1994 Motomaster portable generator. It has no power output
    nevadalenny's Avatar
    nevadalenny Posts: 1, Reputation: 1
    New Member
     
    #19

    Nov 4, 2012, 01:18 PM
    First off you need an analog meter with Rx1 setting and a .5 on the 0 side before getting to one, or a digital meter withy rx1 or rx10, most digital meterhave a variance arounf.7 so you won't read anything other wise.
    The RV generators have more wires however the ohms readings are below 1 on a Rx1 scale. The good reading on a big rv for instance is 0.327 acroos the stator when the wires are tested. That bis even for 4 wire highes watt the first pair will read that and so will the second pair. The regulator plug with thinner wire will read around 2.089 ohms on the Rx1. These readings are from a 4kw rv genset with circuit boards
    Hope this helps
    dawsonstone's Avatar
    dawsonstone Posts: 2, Reputation: 1
    New Member
     
    #20

    Jan 11, 2013, 12:39 PM
    http://www.endtimesreport.com/dead_gen.html... helpful info for recharging generator field... have used both methods listed with success

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

Portable generator doesn't generate [ 1 Answers ]

I have a small gas portable generator that sat idle in the barn for several years. I have cleaned out the carberator and the engine runs fine. The problem is it is only producing 5 volts of electricity. What may be the problem?

Most output from generator [ 6 Answers ]

I plan on buying a portable generator to hook up my house for emergency power, going to instal a manual transfer switch. I was wondering most generators have numerous outlets on them do I have to rewire the panel on the generator to get max output or does the 240 receptacle put out the max, I plan...

Portable generator [ 2 Answers ]

QUOTE=tkrussell]The 100 volts is a bit low. Electrical device operate on +/- 10% , so the lowest volts supplied should be no lower than 108 volts. Incandescent lamps and electric heat will work fine on 100 volts. But any motors may overheat using 100 volts. Volts is usually changed on the...