    #1

    Mar 15, 2008, 07:28 AM
    Goodman Heat Pump compressor keeps running
    In Heat mode, compressor outside continues to run even when the blower inside is not running. If I switch the thermostat switch from Heat to off, the compressor stops but sometimes kicks back on, even with the thermostat switch still in the off position. At this point, I have to cut power via the breaker to stop the compressor. I'm assuming this is a control board problem, but don't know the troubleshoot steps.

    Thanks,

    Brent
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Mar 15, 2008, 08:26 AM
    I would check the starter /contactor for the compressor. It is also possible that one of the 24 volt low voltage wires from the thermostat to the air handler or air handler to the outside unit has shouted out causing this intermittent problem.

    If you have a dog that is outside the wires could have been chewed on also.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heat pump compressor failure ? [ 1 Answers ]

Our heat pump started making a funny sound, like it wanted to start but would stall out. The fan was workingg though, the unit was not cov'd in ice, the pipes outside were cool to touch,the aux heat was already on, which is normal , as it has been very cold here, the heat was keeping up to what...

Heat pump compressor won't go off and red light on tstat comes on [ 3 Answers ]

I have a comfortmaker climate control heat pump/electric furnace. The compressor, (I think) the unit outside, doesn't seem to want to shut off and since it runs continuously even when the furnace backup (fan) turns off. I think because of this, it makes a red light on the tstat come on and it...

Goodman AC/heat pump [ 1 Answers ]

I bought a new goodman AC/heat pump unit got it all installed and wired the inside unit fan runs great but the condensing unit fan and pump will not run after the timer goes off the condensing unit has an electrical hum but it won't start?? any idea what going on ?

Just switched to AC on Heat Pump - compressor trouble [ 2 Answers ]

Need some help. Last night I decided to turn on my heat pump to the cool cycle for the 1st time this season. When I turned it on, the compressor starting clicking and then blew the breaker inside. I decided to go outside and reset the breaker on the control box and then threw the breaker inside...

Heat Pump compressor fan problem [ 1 Answers ]

I have a Trane XE 1000 heat pump manuf. In 2002. Yesterday, the A/C started having a problem, I checked the units inside and out and found the compressor fan not operating. The outside unit was hot and louder than usual. I turned it off overnight and this morning turned it on to find the fan...


View more questions Search