    Please Read Last Post how to calculate wire size to a breaker
    If I have a circuit that draws 21amps what size breaker would I use 20 amp 25 amp 30 amp or 40 amp also is there a book that can help me with these kind of questions
    mike albrecht's Avatar
    mike albrecht Posts: 2, Reputation: 1
    New Member
     
    #2

    Jun 25, 2012, 07:29 PM
    [QUOTE=mike albrecht;3168383]if I have a circuit that draws 21amps what size breaker would I use 20 amp 25 amp 30 amp or 40 amp also is there a book that can help me with these kind of questions a math book with electrical calculations or wire calculations.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #3

    Jun 25, 2012, 08:23 PM
    Is that a continuous draw or peak draw? You should only load your breaker at 80% of its rating even though it is designed to handle 100%, NEC wants only 80% for safety. You need a 30 amp breaker. http://static.schneider-electric.us/...0600DB0101.pdf You may also wish to copy/paste this http://www.groverelectric.com/howto/...%20Wattage.pdf for future reference.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Jun 26, 2012, 04:35 AM
    Quote Originally Posted by mike albrecht View Post
    if i have a circuit that draws 21amps what size breaker would i use 20 amp 25 amp 30 amp or 40 amp also is there a book that can help me with these kind of questions
    It all depends on the circuit and what it is used for. If this is a general use receptacle circuit then it cannot be on a larger than 20A breaker.

    What is on this circuit?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Jun 26, 2012, 04:38 AM
    Quote Originally Posted by ballengerb1 View Post
    Is that a continuous draw or peak draw? You should only load your breaker at 80% of its rating even though it is designed to handle 100%, NEC wants only 80% for safety.
    Sorry, but this is simply not true. There is no "80% for safety" rule, or even rule of thumb.

    A properly wired circuit and breaker is designed to handle 100% of it's capacity. There are rules that limit use to 80%, such as water heaters, electric heat and continuous loads. But there is no blanket 80% rule.

    If you look at general 15, 20 and 30 amp circuits you'll see that the wire is already over sized compared to it's actual ampacity.
    See 240.4(D)
    Kyle_in_rure's Avatar
    Kyle_in_rure Posts: 341, Reputation: 10
    Full Member
     
    #6

    Jun 26, 2012, 06:30 PM
    Quote Originally Posted by mike albrecht View Post
    if i have a circuit that draws 21amps what size breaker would i use 20 amp 25 amp 30 amp or 40 amp also is there a book that can help me with these kind of questions
    You might want to describe the specifics (i.e. what type of circuit this is, what appliance(s) are being used, etc.) so that the best answer can be given.

    Usually, wire size to breakers is as follows:
    20 amp: 12 AWG
    30 amp: 10 AWG
    40 amp: 8 AWG
    However, this all depends on the circumstances of the circuit.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #7

    Jun 27, 2012, 06:31 AM
    Here is more info for you to read/save http://www.fs.fed.us/database/acad/e...sicdesigns.pdf
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #8

    Jun 27, 2012, 12:20 PM
    Quote Originally Posted by ballengerb1 View Post
    Here is more info for you to read/save http://www.fs.fed.us/database/acad/e...sicdesigns.pdf
    No thanks. There is so much misinformation in there it's not funny.
    I like to get my facts from the source, not some summary someone wrote.

    See Table 210.24 for more accurate summary information.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #9

    Jun 27, 2012, 12:45 PM
    210.23 reads "(1) Cord- and Plug-Connected Equipment. The rating
    of any one cord- and plug-connected utilization equipment
    shall not exceed 80 percent of the branch-circuit ampere rating
    unless listed and marked to inform the user of the necessity
    for providing an individual branch circuit.
    (2) Utilization Equipment Fastened in Place. The total
    rating of utilization equipment fastened in place, other than
    luminaires (lighting fixtures), shall not exceed 50 percent of
    the branch-circuit ampere rating where lighting units, cordand
    plug-connected utilization equipment not fastened in
    place, or both, are also supplied. (ROP 2-1, 2-142a)
    (B) 30-Ampere Branch Circuits. A 30-ampere branch
    circuit shall be permitted to supply fixed lighting units with
    heavy-duty lampholders in other than a dwelling unit(s) or
    utilization equipment in any occupancy. A rating of any one
    cord- and plug-connected utilization equipment shall not
    exceed 80 percent of the branch-circuit ampere rating." How would we understand this to not be 80%.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #10

    Jun 27, 2012, 01:03 PM
    Read it again, and don't use logic. You canot use logic when reading the NEC.

    It says:
    The rating
    Of any one cord- and plug-connected utilization equipment
    Shall not exceed 80 percent of the branch-circuit ampere rating
    This particular 80% limitation is for any ONE PIECE OF EQUIPMENT plugged into a general use circuit. NOT the whole circuit.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #11

    Jun 27, 2012, 01:07 PM
    Here is the NEC Table 210.24:
    http://code.necplus.org/pdfs/7011/Table_210.24.pdf

    See where it says "Maximum Load"?
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #12

    Jun 27, 2012, 01:08 PM
    I guess we need the OP to more clearly tell us what he has on this circuit. I see your point about one cord/plug but when you said there was no 80%, I thought I had read about one. It may or may not apply but it does exist.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #13

    Jun 27, 2012, 01:16 PM
    My point was that there is no blanket across the board 80% rule, like that site you linked says, and many other people say. It is simply not true.

    Sure, there are plenty of other specific 80% rules out there, but none like at the beginning of that forestry service site.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #14

    Jun 27, 2012, 02:33 PM
    I just saw this,

    Quote Originally Posted by stanfortyman View Post
    Read it again, and don't use logic. You canot use logic when reading the NEC.
    So true.

    Some confusion comes from the NEC where it states "shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load." that is applied in various locations. This statement comes from the UL listing of circuit breakers.

    From the 2003 UL white book
    CIRCUIT BREAKERS, MOLDED-CASE AND CIRCUIT BREAKER ENCLOSURES (DIVQ)

    MAXIMUM LOAD
    Unless otherwise marked, circuit breakers should not be loaded to exceed 80 percent of their current rating, where in normal operation the load will continue for 3 hours or more.

    This is difficult to apply to the typical general purpose lighting circuits. Since no one really knows how the circuit will be used or rarely used more than 3 hours.

    From NEC 2008 Edition:

    Article 210
    II. Branch-Circuit Ratings

    210.19 Conductors — Minimum Ampacity and Size.

    (A) Branch Circuits Not More Than 600 Volts


    (1) General. Branch-circuit conductors shall have an ampacity not less than the maximum load to be served. Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the minimum branch-circuit conductor size, before the application of any adjustment or correction factors, shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load.

    And:

    210.20 Overcurrent Protection.
    Branch-circuit conductors and equipment shall be protected by overcurrent protective devices that have a rating or setting that complies
    With 210.20(A) through (D).

    (A) Continuous and Noncontinuous Loads. Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the rating of the overcurrent device shall not be less than the noncontinuous load plus 125 percent of the continuous load.


    While Table 210.24 states Maximum Load under each circuit rating column, each column refers to specific paragraphs of Section 210.23 A thru D

    210.23 Permissible Loads.
    In no case shall the load exceed the branch-circuit ampere rating. An individual branch circuit shall be permitted to supply any load for which it is rated. A branch circuit supplying two or more outlets or receptacles shall supply only the loads specified according to its size as specified in 210.23(A) through (D) and as summarized in 210.24 and Table 210.24.

    (A) 15- and 20-Ampere Branch Circuits.
    A 15- or 20- ampere branch circuit shall be permitted to supply lighting units or other utilization equipment, or a combination of both, and shall comply with 210.23(A)(1) and (A)(2)

    (1) Cord-and-Plug-Connected Equipment Not Fastened in Place.
    The rating of any one cord-and-plug-connected utilization equipment not fastened in place shall not exceed 80 percent of the branch-circuit ampere rating.

    (2) Utilization Equipment Fastened in Place.
    The total rating of utilization equipment fastened in place, other than luminaires, shall not exceed 50 percent of the branch circuit ampere rating where lighting units, cord-and-plug connected utilization equipment not fastened in place, or both, are also supplied.

    This is why we always need to know the purpose of the circuit.


    Unless the circuit is a general purpose lighting circuit, the circuit should not be loaded more than 80%.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #15

    Jun 27, 2012, 02:44 PM
    Thanks TKS, a little more complicated than much of what I deal with. It would help if the OP would answer my questions.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #16

    Jun 27, 2012, 03:16 PM
    Sometimes, and I am not sure how to solve this, often we, those answering questions, end up conversing with each other, which is fine, but tends to get off topic, or a difference of opinion, or interpretation of Code, and the person seeking help is bored with those going back and forth, or just goes away.

    And I am guilty also.

    Somehow we need to figure out how to answer questions and have our discussions elsewhere, and the get them best answer.

    Any idea?

    Anyone?

    This goes on in many other forums also, and I wish I had the solution.

    You may have noticed, I try to answer each question with more questions before I try to give the solution.

    Can we try that?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #17

    Jun 28, 2012, 05:29 AM
    Don't everyone answer or comment at once.
    dclynch's Avatar
    dclynch Posts: 202, Reputation: 19
    Full Member
     
    #18

    Jun 28, 2012, 09:09 AM
    I'm not the original poster, but I very much enjoy and learn from the expert back and forth discussions.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #19

    Jun 28, 2012, 09:32 AM
    In my first post I asked a question but to this day never received an answer from the OP. Yes that is a good approach but I think I need to stop responding when the OP does not come back with more info.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire Size and Breaker Size [ 2 Answers ]

I am looking at a 125 ft run of cable to feed a branch circuit in an adjoining building. I have lots (490 ft) of left-over #2 copper cable from another project and a 125 Amp Cutler Hammer panel w/main disconnect that I could use. I have in the main house a 200 Amp Cutler Hammer panel. --Can I...

Wire size wire & circuit breaker do I need for a 15.8 range [ 2 Answers ]

What size circuit breaker & wire size do I need rfor a 15.8 raqnge ?


View more questions Search