    Drillsgtmg's Avatar
    Drillsgtmg Posts: 1, Reputation: 1
    New Member
     
    #1

    Mar 8, 2008, 05:37 PM
    Hot tub 240 volt wiring
    I am wiring a hot tub. I have a 50ft run from the circuit breaker panel to the hot tub CGCI box, and another 35ft from the GFCI box to the hot tub. The specs call for a 50 amp 4 wire system. My question is, what size wire should I use? # 6 #8 ?
    biggsie's Avatar
    biggsie Posts: 1,267, Reputation: 125
    Ultra Member
     
    #2

    Mar 8, 2008, 06:21 PM
    This is a good diagram -- Hope it helps

    Seimens GFCI wiring

    The distance of the run will have the largest impact on the choice of wire size.

    Consult your local codes to make the appropriate decision.

    SpaSupport: Electrical Installation, 230 Volt Spa/Hot Tub
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Mar 8, 2008, 09:12 PM
    Quote Originally Posted by Drillsgtmg
    I am wiring a hot tub. I have a 50ft run from the circuit breaker panel to the hot tub CGCI box, and another 35ft from the GFCI box to the hot tub. The specs call for a 50 amp 4 wire system. My question is, wat size wire should I use? # 6 #8 ?
    This depends on the inside wiring portion. If it is NM cable then you must use #6. If the run will be ALL in conudit then you can get away with #8.
    For the outside portion of the wiring to a hot tub or spa you have NO choice but to run conductors in conduit with an insulated ground.

    I hope you know all the other important codes with regard to wiring a spa...
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Mar 8, 2008, 09:33 PM
    Your disconnect must be "line of sight". Is it? 35' seems excessive.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #5

    Mar 9, 2008, 08:57 PM
    From PM:
    Quote Originally Posted by Drillsgtmg
    This is the message:

    I am wiring a hot tub. I have a 50ft run from the circuit breaker panel
    to the hot tub CGCI box, and another 35ft from the GFCI box to the hot
    tub. The specs call for a 50 amp 4 wire system. My question is, wat
    size wire should I use? # 6 #8 ?

    The tub is going in a basement and the 35 ft is from the spa box on one
    wall , overhead, and down the oppisite wall to the hot tub. Would
    braid wire be better?
    #4 for 50 Amp continuous load (operates more than 3 hours). This will give you a 2.8% voltage drop or 3.3 volts. This is below the 3% required.
    The grounding conductor could be less - not sure how to size.

    Stranded won't make any difference.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Mar 10, 2008, 04:18 AM
    This is not a 50A continuous load. It is a 50A circuit.

    Use #6 cable. Either 6/3 or 6/2 depending on whether the tub requires a neutral.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #7

    Mar 10, 2008, 06:40 AM
    OK, for a 40 amp continuous load (0.8*50), #6 will give you a 2.8% voltage drop. If the continuous load is less than 40A, then use #6.

    To get the continuous load rating, you multiply by 1.25. So 40 * 1.25 = 50 A.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #8

    Mar 10, 2008, 10:11 AM
    What are you basing your VD numbers on?
    85' is not really that far to even be worried about VD.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #9

    Mar 10, 2008, 10:28 AM
    170', #6 Copper, 120 V.

    We don't know what the nameplate says. Without that information, you can go either way in terms of sizing. In the latter case, the breaker could not support a 50 A load continuusly.
    Once you have the load, do the vd calcs. Then the CB can be upsized accordingly. There is a motor load involved and I wasn't paying attention to that.

    I do believe you are right that, for instance, a 15A 120V circuit should only be loaded to 80% capacity if operating continuously.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #10

    Mar 10, 2008, 11:30 AM
    Quote Originally Posted by KeepItSimpleStupid
    170', #6 Copper, 120 V.
    This totally NOT the correct way to figure VD in a 240v circuit.
    If the circuit is 240v then you use 240v, NOT 120v times double the distance.
    One reason for this is because a 240v circuit has substantially less voltage drop than a 120v circuit.




    Quote Originally Posted by KeepItSimpleStupid
    Once you have the load, do the vd calcs. Then the CB can be upsized accordingly.
    You mean the wire size would be upsized, right? The CB would stay the same regardless of VD.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #11

    Mar 10, 2008, 02:56 PM
    I disagree, because he said a 4 wire 240 V circuit, that means the Vd is calculated for the legs or 120 V. Agreed, that N carries the difference current, but if all 40 A was on L1 and L2's load was 0.1 A, what voltage would you use to calculate Vd. N would be 39.9 A.

    No, say for instance the caclulated current is 47 A. You can upsize to the next size breaker of 50A, since a 47 A breaker is not available.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #12

    Mar 10, 2008, 03:15 PM
    Quote Originally Posted by KeepItSimpleStupid
    I disagree, because he said a 4 wire 240 V circuit, that means the Vd is calculated for the legs or 120 V. Agreed, that N carries the difference current, but if all 40 A was on L1 and L2's load was 0.1 A, what voltage would you use to calculate Vd. N would be 39.9 A.
    Come on now. If you've ever wired a hot tub, or any other 120/240v appliance, you'd know that the VAST majority of the load is 240v. The 120v portion of the load is negligible. Besides, any 120v loads would be at least (tried to) be balanced by the manufacturer.

    I guess you can do it your way and I'll do it mine.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #13

    Mar 10, 2008, 04:31 PM
    I didn't imply my example was a hot tub. It was purposely far etched to illustrate a point.

    So, how might you size a service entrance cable? Assume that L1 and L2 are nearly balanced and use 240 V?

    At least you get the idea. The point is: We don't know the load.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #14

    Mar 10, 2008, 06:12 PM
    Quote Originally Posted by KeepItSimpleStupid

    So, how might you size a service entrance cable? Assume that L1 and L2 are nearly balanced and use 240 V?
    According to the code and what the POCO requires. As you said, we don't know the load, but yes, I'd use 240v.

    Besides, VD is NOT a code issue. There is nothing code enforceable about VD. It is simply a design/performance issue.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #15

    Mar 10, 2008, 07:40 PM
    I refer you to tkrussel's post who says you need to check both:

    https://www.askmehelpdesk.com/electr...on-166806.html

    But, then if you do it for the lower voltage, it should be OK for the higher one.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #16

    Mar 10, 2008, 08:17 PM
    I mean no disrespect, but TK saying you need to check both holds just as much water as me saying you do not.
    Then again this is just my own opinion on the matter.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #17

    Mar 10, 2008, 08:53 PM
    Page 113, 2nd paragraph from the bottom, right hand side:

    Master Electrician's Review - Google Book Search

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How do I get 240 volts AC to the hot tub? [ 9 Answers ]

Hello, everyone. My name is Mike and I live in Dunsford, Ontario, Canada. My wife recently purchased a new hot tub and has lovingly assigned the task of installing this monster to me... I have an older house with the old fashioned screw-in fuses, and 200 amp service. I had one spot remaining...

240 volt wiring using a single pole RLV430 thermostat [ 8 Answers ]

Using a single pole RLV430 honeywell thermostat I need to wire a 240 volt heater. In my box I have 2 live and 2 neutral wires. The thermostat has 2 wires. http://www.homedepot.ca/wcsstore/HomeDepotCanada/images/catalog/b7867367-6c05-4c82-a97c-648044b91564.pdf

240 volt wiring [ 1 Answers ]

When wiring my weldershould I use neut bus or grnd bus to grnd the machine

Hot tub 240 [ 1 Answers ]

I have a 240 hot tub but no 110 close. I was thinking about running a line to the hot tub controls and use 1 leg of 240 circuit to make a 110 outlet. Bad idea?

Replacing a 240 volt outlet with a 120 volt oulet [ 1 Answers ]

We've switched to a central air conditioning system and no longer need the 240 volt outlet by the dining room window. The house was built in 1928, updated in 1957, and again a couple of ad hoc times thereafter. The wiring is at times very old, brand new or somewhat old. My guess is that the 240...


View more questions Search