    Gfci spa panel tripping
    I just installed a spa with 4 wires. The house is old and while the neutral & ground bus bars are separate in the spa panel, they are all on the same bar in the main panel. Do I need to install a ground rod by the spa panel to keep the gfci from tripping? (instead of running the ground back to the main panel neutral/ground bus bar)
    jamlove's Avatar
    jamlove Posts: 78, Reputation: 2
    Junior Member
     
    #2

    Dec 21, 2005, 01:14 PM
    Ground fault
    Hi,
    It sounds like either the wiring is incorrect, or you have a problem with the spa equipment. Something is grounding out (shorting out) that causes the GFCI to trip.

    I'd stay out of that water until you can get the equipment checked by an electrician...

    Ground and Neutral are on the same bus in my panel, no problem there. Double-check that you've wired correctly, but maybe corrosion has caused one of your pumps or motors to ground-fault?

    Good luck, j
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Dec 21, 2005, 05:25 PM
    First of all, do not install a ground rod. This will not solve your problem with the GFI, and is a code violation. Too much detail to explain here why,please take my word for it.

    The GFI breaker has a neutral wire coming off it that must go the neutral bar in the panel. The white load wire, from the spa must connect to the screw terminal under or near this white wire on the GFI breaker. Many times this white wire from the load is connected improperly. Check to be sure this is done correctly. The terminal for the white load wire on the breaker sometines is hard to see. I know because I have missed it myself. This is a popular reason for GFI to trip on a new spa.

    The neutral and equipment ground are to be connected at the main panel, only, and separate at any subpanel, so that's correct.

    Check the GFI breaker to be sure the load white is connected properly, I bet that is the problem.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Dec 21, 2005, 06:43 PM
    There are 2 people here you want to follow their instructions exactly, tkrussel and Tom in plumbing. Before they came, I didn't realize how little I knew.

    Your question sounded like it should work, but I didn't know what to tell you to look for.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #5

    May 15, 2007, 09:46 AM
    Unplug or disconnect spa motor, GFI doesn't trip? Change motor.
    Repeat for other features. Blower etc...

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Window Air Conditioner & Circuit Tripping [ 7 Answers ]

We installed a window air conditioner two days ago. Unit operated fine with no problems up until yesterday when it began tripping the circuit breaker. The unit is 120V and is the only thing plugged into the circuit (We have unplugged every other single item). The tripping of the circuit happens...

Window mount AC tripping circuit breaker [ 4 Answers ]

Hi All, I have a new air conditioner that is on it's own circuit. The breaker is new and rated at 15 amps. The air conditioner is supposed to use 15 amps at peak. I believe the wire to the outlet is rated at 15 amp. The air conditioner has it's own circuit breaker on the plug which has...

Gfci [ 1 Answers ]

Is there ever a situation where it makes sense to have a GFCI outlet on the same circuit as a GFCI breaker? Will having a GFCI outlet on the same circuit as a GFCI breaker cause any damage? I recently bought a house and found the situation noted above.

A/c power breaker tripping [ 2 Answers ]

I have dual a/c units to control the upstairs and downstairs of my residence. I have isolated my problem of no cold air to the breaker panel. I need help identifying what the possible reasons may be for the breaker tripping. There are two breakers (one coming directly from the a/c units with a...

GFCI on breaker panel trips, 3 way, how to find the problem? [ 1 Answers ]

Periodically one GFCI in the panel trips This particular circuit runs an outside outlet, one light in the basement and it seems to work 2 switches and a plug in the family room The problem with the 2 switches in the family room at opposite ends are suppose to turn the plug off and on as a 3...


View more questions Search