New Member
|
|
Apr 20, 2005, 05:55 PM
|
|
Wiring Hot Tub and using a 50 Amp Double Pole GFCI Circiut Breaker
:confused: I keep getting the GFCI breaker tripping after wiring my hot tub.
I wired 2 hot Red and Black to the proper terminals and the White to the neutral and the Bare Copper to the ground Post at the tub. I am using 6-3 w/G per instructions. Could the GFCI breaker be bad? When
I wire without the GFCI breaker in the line everything works... this is using a 50AMP double pole breaker at the main panel.
HELP!
|
|
|
Uber Member
|
|
Apr 20, 2005, 07:50 PM
|
|
GFCI's can be touchy. It is always possible one was bad out of the box. What kind of wire are you using? If I remember correctly, say TW will cause more nuisance tripping that THHN. Try installing the breaker and trying it with no wires connected, and then adding one more wire checking it each time, finally with the load. Also, if you try to feed a sub panel with the neutral and ground connected, it will trip.
|
|
|
Uber Member
|
|
Apr 21, 2005, 01:38 AM
|
|
The white or neutral from the hot tub controller must be connected to the sliver terminal that is on the GFI breaker. The GFI breaker has a short white wire that must connect to the neutral bar of the panel.
The neutral terminal on the breaker can be difficult to see right off. Look closely near the white pigtail and you should find it. If the neutrals are wired in any other fashion the breaker will trip.
If this has been done, then it is possible for the breaker to be defective.
Connecting the tub with a standard breaker for testing purposes is fine, however do not leave it, or at least do not get yourself in the tub. This GFI breaker must work properly before anyone uses the ub, so be patient, and be sure the problem is corrected.
|
|
|
New Member
|
|
Aug 4, 2007, 01:39 PM
|
|
If there is a gfci breaker on the tub is it safe to wire the tub directly to a standard breaker circuit?
|
|
|
New Member
|
|
Aug 4, 2007, 01:59 PM
|
|
I had the hot tub running perfectly this way but after running for about 2 hrs it just stopped completely and it doesn't seem to have tripped any breakers. Thanks!
|
|
|
Uber Member
|
|
Aug 4, 2007, 02:48 PM
|
|
Unplug or Disconnect Pump Motor, and turn on GFI. If it doesn't trip, Motor leaking to ground, or Corrosion, Rust. Try disconnecting blower or other accessories, Til Tripping stops. Repair or replace Parts that are leaking to ground.
|
|
|
New Member
|
|
Aug 4, 2007, 04:37 PM
|
|
Thanks, I will give that a try. How could it be leaking to ground all of a sudden? Thanks a lot!
|
|
|
Uber Member
|
|
Aug 4, 2007, 06:18 PM
|
|
Corrosion and rust grow, saltwater air, if near ocean, and then you have the pool chemicals. Isolate problem(s), And Take apart, Majority of the time, the problem will be visible. Piece of rust shaking free from vibration could cause problem.
And at the Spa, White needs to go to Neutral only, no connection to ground.
|
|
|
New Member
|
|
Oct 10, 2007, 09:24 PM
|
|
If your hot tub is over 50ft from the GFCI breaker you may be getting nuisance trips, caused by a slight imbalance in the current between your hot conductors and the neutral.
The only way to resolve this problem is to buy a spa GFCI box and place it close to the hot tub (more than 5Ft away). Use a conventional breaker in the main panel to feed your GFCI at the spa.
|
|
|
New Member
|
|
Oct 30, 2013, 09:47 PM
|
|
It is another scenario, when the heater is leaking current to the ground, and that can cause the breaker to trip. Without the GFCI the hot tub works fine but is nit safe, So, you need to replace the heater, which of course can be expensive. Good luck.
|
|
|
Ultra Member
|
|
Oct 31, 2013, 04:48 AM
|
|
Poli... you realize you are replying to a six year old post?
Always check the dates before joining... and welcome to the site!
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
20 amp double pole gfci
[ 9 Answers ]
I am working on an addition and am installing a whirlpool tub. The tub requires 2 - 20 amp GFCI protect circuits: 1 for the pump and 1 for the heater. I ran 12/3 wire in the walls thinking I could have the BLACK wire go from 1 GFCI breaker to the pump outlet and the RED wire go from a 2nd GFCI...
Warm GFCI Breaker
[ 1 Answers ]
In our electrical panel we have 2 AFCI breakers next to each other. One is for the master bedroom the other is for 2 guest bedrooms. Each of these breakers is warm to the touch. We have had no electrical problems in either room and it has never tripped. I just thought it was strange that these...
Double breaker?
[ 3 Answers ]
Hi, I have recently put in a new 200 amp. Service and had to install a large J-box to extend the wiring to the new location, (not very far). My problem is that I have a new 2-pole 40 amp. Breaker for the "A/C", and a 15 amp. Breaker for the "furnace". My confussion is that either of these breakers...
Gfci breaker popping
[ 8 Answers ]
After installing a second outdoor fan, I tied into an existing fan under an enclosed porch.I decided it would be smart to install a gfci breaker to protect them (vs the standard breaker).
The circuit is tied into my kitchen an outdoor spot lights. With all the individual light circuits either...
Gfci breaker
[ 2 Answers ]
My question is I have a 50 amp GFCI breaker that I will be installing in the breaker box. I have another 50 amp GFCI breaker box that must be installed within 5 feet away from the hot tub. Is it OK to install both 50 amp GFCI breakers for this hot tub I realize I don't need two GFCI's but I...
View more questions
Search
|