    Wiring replacement heat pump fan motor and capacitor
    Hi. My heat pump fan motor died. I got a replacement motor and capacitor but the wiring is a bit different for the new parts and I was hoping you could help me sort it out. The old capacitor had three terminals while the new one has only two.

    In the old setup, there were 5 wires to deal with:
    Code:
    brown:  motor -------------------> cap (terminal labeled "fan")
    purple: motor -------------------> cap (terminal "0" or something like that)
    black:  motor -------------------> circuit board (contactor?)
    orange: cap (terminal "herm") ---> somewhere else
    red:    cap (terminal "0") ------> somewhere else
    By "somewhere else" I mean this wire goes somewhere other than the cap or the motor, so it doesn't seem too important for this job. If it is, let me know and I'll happily provide more info...

    The new motor has two wiring diagrams printed on it. The first is:
    Code:
    brown/white --------> cap
    brown --------------> cap
    purple (common) ----> L1
    black --------------> L2
    green --------------> ground
    The second is labeled "optional 3 wire connection":
    Code:
    brown/white ---> insulate
    brown ---------> cap
    purple --------> cap ----------> L1
    black -------------------------> L2
    So my questions are:
    -What are L1 and L2?
    -The optional 3 wire connection looks more similar to the old setup--should I wire it this way?

    Any help would be greatly appreciated! :)
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 18, 2010, 11:51 AM
    I figure your heat pump motor is 220/240 volts.

    The easiest way is to just

    Use the two brown to go to the new capacitor.
    Use L1 and L2 to power the motor up from the load side of the contactor so when the unit turns on and the contactor makes the connection the new motor will also come on.

    By wiring this way you prevent having to mess with the wires for the compressor Orange/Red. The old capacitor is also powering the compressor and needs to be hooked up to it just as it is now.
    You can remove the wires from the original capacitor that were used for the old fan motor if you wish or just tape up and leave alone. That is your option.

    NOTE: if there is a short green wire make sure it goes to ground which is the unit metal.
    DrJosh's Avatar
    DrJosh Posts: 6, Reputation: 1
    New Member
     
    #3

    Jan 18, 2010, 12:33 PM

    Thanks for your swift reply! I appreciate your expertise.

    I'm still not clear on what "Use L1 and L2 to power the motor..." means.

    Black: motor ----> contactor (as before)
    Purple: motor --->?

    I guess the contactor is L2. What's L1? What do I connect purple to?

    There is a little green wire coming off the motor. I'll be sure to secure it to the unit chassis. Thanks again.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jan 18, 2010, 01:32 PM
    You need to hot legs to power up the motor. L1= Line one 120 volts and L2=Line 2=120 volts. When wired to a 220/240 volt motor both lines of 120 are used to get the 240 volts needed so the motor will run.

    On the contactor there are two power terminals for the power in and 2 for the power out. The power in comes from the house or disconnect for the unit. The two for the power out (out after activation by the 24 volt control circuit). The two for the power out are used to run the compressor and the condenser fan motor which you are replacing so blcak to one side and purple to the other side of the contactor. They will be put on the same side that is also used now for the compressor.

    NOTE: There are probably an extra wire or so that feeds the old condenser fan motor circuit. If you know what you are doing those can be eliminated IF NOT let them alone and just attach the purple and black.
    DrJosh's Avatar
    DrJosh Posts: 6, Reputation: 1
    New Member
     
    #5

    Jan 23, 2010, 01:01 PM
    I was finally able to take another look at the unit and try to apply
    Your advice. However I'm still not clear on how to proceed. To
    Make things a little clearer I took some pics:





    As you can see I reinstalled the old cap and reconnected red and
    Orange as per your advice. In the old setup the brown and purple
    Wires ran from the fan motor to the cap terminals and the black
    Wire ran from the fan motor to the black "ZETTLER" box on the
    Circuit board (right). In my previous posts I assumed this was the
    Contactor but maybe that was wrong?

    Anyway would it be bad if I just forgot about the new cap (5uF) and
    Connected everything as before? Old cap is 7.5uF.

    How would you rig this up? Again, I thank you for your time.

    Josh
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Jan 24, 2010, 02:52 AM
    Post the brand name

    Post the exact model number

    I need to see the wiring diagram for this unit and with the above info I will try to look it up. I believe the top of the contactor is the side you want to use to power the motor I want to be sure.

    The answer to your question is NO you need to use the capacitor that was sized for the new motor. While the difference is small (7.5 to 5) the long term problem could cause motor failure.
    DrJosh's Avatar
    DrJosh Posts: 6, Reputation: 1
    New Member
     
    #7

    Jan 24, 2010, 07:56 AM

    Old motor
    Emerson K55HXFHD-7740
    RPM 825
    Volt 200-230
    Hz 60
    Amp 1.9
    Ph 1
    HP 1/4
    Thermally protected

    I got the replacement motor through Grainger. Told them the
    Old model number and they sold me the following replacement:

    New motor
    Dayton 4M226J
    RPM 825
    Volts 208-230
    Hz 60
    Amp 1.6-1.9
    Ph 1
    HP 1/4
    Protection auto
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Jan 24, 2010, 09:12 AM
    Brand name of unit

    Exact model number of unit

    The motors make little difference it is the units brand and exact model number I need. I need to be able to follow the units wiring diagram not the motors since I know how the motor works but I do not know for sure how the motors wiring is incorporated into the unit due to the circuit board
    DrJosh's Avatar
    DrJosh Posts: 6, Reputation: 1
    New Member
     
    #9

    Jan 24, 2010, 09:18 AM

    Oh, sorry about that. Here's the unit info:

    Date: 4/98
    Model#: Trane TWR042C100B2
    Min circuit ampacity - 28.0 amps
    rec. fuse/breaker - 40
    Max fuse/breaker - 45
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #10

    Jan 24, 2010, 09:52 AM
    Here is the wiring diagram for your unit.With this and the info I supplied in my other posts you should be able to wire your unit. If not then I suggest you contact a local HVAC professional to help you since I cannot wire it from here.

    Note: The one motor leed has to go on to the circuit board and attach to the black Zettler relay. If the relay or circuit board is damaged or defective it will also need to be replaced. This is the defrost control for the heat pump and must be used if the heat pump is to function correctly.
    Attached Images
  1. File Type: pdf Doc1.pdf (62.1 KB, 883 views)
  2. DrJosh's Avatar
    DrJosh Posts: 6, Reputation: 1
    New Member
     
    #11

    Feb 1, 2010, 01:58 PM

    A little follow-up: last week I installed the new motor according to the "optional 3-wire connection" indicated in my first post (integrates well with the original wiring diagram). It's been working great!
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #12

    Feb 1, 2010, 02:05 PM
    As long as you got it working that is all that counts. I am sure you used a new capacitor on your install.
    harvestpride's Avatar
    harvestpride Posts: 3, Reputation: 1
    New Member
     
    #13

    Apr 13, 2011, 09:16 PM
    If you used the grainer motor replacement that Dr. Josh was so kind in sharing. All the wire colors should match. There is a brown and white wire you will not use. Tape this wire off.

    Thanks Dr. Josh!! Just did mine today and it works like a champ. $120 motor with shipping.

    harvestpride's Avatar
    harvestpride Posts: 3, Reputation: 1
    New Member
     
    #14

    Apr 13, 2011, 09:19 PM
    Comment on hvac1000's post
    All the wire colors should match. You will not used the brown and white wire. Tape this off. Works great!
    harvestpride's Avatar
    harvestpride Posts: 3, Reputation: 1
    New Member
     
    #15

    Apr 13, 2011, 09:20 PM
    Comment on DrJosh's post
    All the wire colors should match. You will not used the brown and white wire. Tape this off. Works great!
    BR14648's Avatar
    BR14648 Posts: 2, Reputation: 1
    New Member
     
    #16

    Sep 3, 2011, 03:35 PM
    I hooked up my cental a/c with the new capacitor and it works great! You are the best!
    Linda

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Condenser Fan Motor Wiring for Goodman AC Heat Pump 3 Ton [ 5 Answers ]

Condenser Fan Motor Wiring for Goodman 3 Ton -------------------------------------------------------------------------------- Hello Everyone, I have a GOODMAN A/C Heat Pump Model# CPLE 36-1 installed 3 years ago. Last week I turned the unit on, the compressor hums (not run)about 3-5...

Wiring replacement Condenser Fan motor [ 10 Answers ]

I replaced the condenser fan motor on my old Tempstar A/C, but I am a little uncertain about the wiring on the new motor. Attached is a picture of the way I have it wired right now and the wiring diagram that came with the motor. The old motor had 3 wires: Black - wired to T2 contactor ...

Correct wiring from fan motor to capacitor [ 5 Answers ]

I have a goodman ac unit I changed out my capacitor but think I wired it back up wrong can anyone help me

AC Fan Motor Capacitor Wiring? [ 3 Answers ]

HI! 1st Post Here. I replaced my AC Fan Motor and the Capacitor that came with it was 1/4 the size of the original capacitor. It had 2 Posts (4 Connectors each) and the original had 3 Posts 3 Connectors each) which were labeled. No labeling on new Capacitor G21-930. New motor is 1100rpm, 1...

Wiring issue from fan motor to capacitor [ 3 Answers ]

I am changing out the condenser fan motor on my Carrier Comfort series ac unit. I had a GE 1/4hp motor with three wires and I went to Grainger and got a universal replacement for it. However this motor has four wires of different color. So my original motor had Yellow (common) and Black (line) from...