New Water Pipe Size
We are putting new plumbing in the house. The size of the meter is 3/4".
Can we put 1" pipe from the meter to the house, or should there be 3/4" pipe?
Our contractor put 3/4" pipe from the main and then he put 1" pipe after the cut off.
Is this right?
|
|
|
Ultra Member
|
|
Jun 26, 2009, 02:53 AM
|
|
Originally Posted by njain
We are putting new plumbing in the house. The size of the meter is 3/4".
Can we put 1" pipe from the meter to the house, or should there be 3/4" pipe?
Our contractor put 3/4" pipe from the main and then he put 1" pipe after the cut off.
Is this right?
If the fixture demand (calculated by assigning a fixture unit value to each plumbing fixture and then adding up the number of fixture units) requires a 1" feed and the water line from the meter was replaced, then your plumber should have run a minimum of 1" from the meter.
There are other factors involved, of course: Pressure at the meter, length of run from meter to house, rise in elevation from meter to highest fixture in house etc.. .
|
|
|
Eternal Plumber
|
|
Jun 26, 2009, 05:27 AM
|
|
Growler,
Correct me if I'm wrong but if you have a 3/4" meter would raising the water service to 1 inch increase the volume that the meter would produce? I don't think so. But I value your opinion so I'm asking. I always though a "one inch feed" to the house included a one inch meter. Was I wrong? Regards, Tom
|
|
|
Ultra Member
|
|
Jun 26, 2009, 05:53 AM
|
|
Originally Posted by speedball1
Growler,
Correct me if I'm wrong but if you have a 3/4" meter would raising the water service to 1 inch increase the volume that the meter would produce? I don't think so. But I value your opinion so I'm asking. I always though a "one inch feed" to the house included a one inch meter. Was I wrong? Regards, Tom
The meter can and should be upgraded -- But doing so will be at the homeowners expense.
But upgrading a 3/4" meter to a 1" meter is not compulsory, at least not in my area.
OTOH, if the fixture unit demand for the dwelling requires an 1-1/4" feed or larger, then the Inspector would likely require a meter upgrade before signing off the job.
|
|
|
Eternal Plumber
|
|
Jun 26, 2009, 06:09 AM
|
|
Thanks growler, But it would choke down the volume produced Correct? I mean isn't it like "unringing the bell"? Once the volume's choked down at the 3/4" meter you can't increase the volume produced by jumping the service up to 1". Am I correct in assuming this? Regards, tom
|
|
|
Ultra Member
|
|
Jun 26, 2009, 06:36 AM
|
|
Originally Posted by speedball1
Thanks growler, But it would choke down the volume produced Correct? I mean isn't it like "unringing the bell"? Once the volume's choked down at the 3/4" meter you can't increase the volume produced by jumping the service up to 1". Am I correct in assuming this? Regards, tom
You're correct, but you still need to size the water line and water piping inside the house to meet the fixture demand.
What the Plumber did was hamstring the owner from upgrading their water meter at a later date -- Something that definitely wouldn't fly in my neck of the woods.
|
|
|
Eternal Plumber
|
|
Jun 26, 2009, 06:48 AM
|
|
I agree and thanks growler. Tom
|
|
|
Plumbing Expert
|
|
Jun 27, 2009, 06:30 AM
|
|
In my area we would install 1" water main even if you have 3/4" meter. Sometimes, water company comes and upgrades meter at no cost to you. 3/4" meter used to be adequate in the 50's but with size of today's houses 1" is minimum. FYI: I have 2" meter in my own house.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Water well pipe size
[ 5 Answers ]
I am going to run a submersible pump in a well 600 feet from our cabin. It is going up hill probably 20 feet in slow rise. Would you have a low pressure by only going with 1" instead of 1 1/4" sch 40. Also another question - the existing line is one made of ~2" - ~2 1/2" plastic pipe which they...
Water hammering, water arresters, big pipe flowing into small pipe
[ 2 Answers ]
Hi,
I have a water hammer (I'm guessing) problem in our house. All the pipes are under the house and it is a timber house so each time there is a water hammer noise it is extremely noisy. Basically any tap in the house is making the noise when turning on or off quickly with loud bangs. Cold...
Gas pipe size
[ 4 Answers ]
I live in a home in Birmingham, AL that was built in the mid-fifties. I am working on correcting some problems due to improper work done by the previous owners and am starting to completely re-pipe my natural gas system that feeds a furnace, water heater, stove, gas dryer, and fireplace log. I...
Pipe size?
[ 2 Answers ]
I live in san francisco and am adding a lavitory sink I plan to connect to current shower drain with a wye and loop vent through same what size pipe do I need and what is the best way to support it ? Sink will be 4 1/2 feet from shower drain thank you tallgrass:o
View more questions
Search
|