The NM-B #6-3 With GROUND already has a ground. A separate ground wire from panel to panel is not needed nor allowed.

This cable may have a maximum of 60 amp breaker.

Keep the neutral isolated from the equipment ground at the subpanel, by using the insulated neutral bar for the white, and a separate equipment grounding bar bolted to the panel metal box for all green and bare grounds.