    Where to install a Grounding Rod
    My house is about 20 years old and I do not have a grounding rod installed. Although all the wiring is grounded to the water pipes, I would still like to install one. My question is how close or far from the main electrical box should the grounding rod be installed?

    On on the other side of the wall of my electrical panel is a water facuet, my AC Compressor and also my Gas meter. So I have two questions.

    I'm pretty sure the gas line is about 4 feet down underground, but how far away from the house do they run the line before it goes parallel to the backyard? I know my gas line runs to the backyard cause when I had sprinklers installed, the guy found the gas line with a metal detector and showed me the location. Would a surge running to the grounding rod trigger anything near the gas line? Like and explosion?

    Also does it matter if the grounding rod is placed near the AC Compressor? Would having it too close to the compressor cause problems if there was a surge? Like short out my brand new compressor?

    Also, does anyone know the best way to get the grounding rod in to the ground other than pounding it with a 5 pound hammer? Its 8 feet long and 5/8" in diameter

    I can provide a picture of the area if anyone is confused.

    Thanks a bunch

    David
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Oct 13, 2005, 07:08 AM
    In the past it was common for all that stuff to be grouped in a small area. Wise and legal now? Hope tkrussel replies soon. Thinking about the gas line was wise. You should be able to find a number in your phone book to call for locator service. They might even find something you forgot such as a phone line.
    harleyds's Avatar
    harleyds Posts: 56, Reputation: 2
    Junior Member
     
    #3

    Oct 13, 2005, 07:50 AM
    Both Phone and Sprinkler lines area already mapped out in my yard. I drew up blueprints of where everything was as it was being installed when the Phone company came out cause the sprinkler guys snapped the phone line!

    Thanks for the reply

    EDIT...

    My cable TV line is above ground so that is not an issue!
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Oct 13, 2005, 07:53 AM
    Phone lines and cable tend to be more hidden in the dirt than buried. I got both once with a tiller.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Oct 15, 2005, 05:44 AM
    I have pounded many a ground rod in with a 5 pound sledge, using a pair of channelocks to hold the rod to prevent hitting my hand and keep the rod still wihle swinging the hammer.

    You may be able to rent an electric jack hammer, most have an attachment that takes the place of a drill bit, it is a deep narrow cup that slips over the rod and will drive the rod in effortlessly.

    Depends on the soil conditions, if sandy or clay the hammer will work fine, just takes a little longer, the rental will help if the conditions are rocky.

    You can look in the phone book for a free " Call Before You Dig" utility locator service.

    Your system is currently grounded via the connection to the city water system, assuming this is what you have, and assuming that the city water line to your house is metal.A ground rod is now required as supplemental by code, to be in addition to the main ground, the connection to your water.

    The rod can be anywhere in relation to the "Main Box". The connection is the important issue. Most likely the water ground wire connects to the main box, on the neutral bar. This is where the ground rod wire needs to connect to. The wire to the rod must be no smaller than #6 AWG copper,and can be bare or insulated.

    The rod can be near anything, I would keep it as far away as practical, but the distance to anything such as a air conditioner is not an issue, and will not cause any problems. The AC unit is, or should be, grounded back to the main ground in the panel, so the rod and the unit is all at the same zero potential.

    Hope this helps, but grounding is a very confusing and complicated matter, and hard to anticipate all the conditions that may be encountered. Some photos may be helpful just to be sure something is not being missed.
    harleyds's Avatar
    harleyds Posts: 56, Reputation: 2
    Junior Member
     
    #6

    Oct 16, 2005, 04:58 PM
    Picture
    The Red line at the bottom is my first choice since there are less things in my way when I have to pound this bar in to the ground.

    The Blue line is where I would like to put it since it is closer to the water line where an existing ground is attached to my water line, but the electrical meter is right there and I don't want to risk hitting and breaking the glass.

    I will be calling the Utility company to tell me where all my lines are. Now that I think about it, the water line leads to the front yard so If I put the grounding rod where the red line is, I may hit it.

    Does anyone know how far away from the house I should put it? My house doesn't have a basement so the foundation stretches out a bit. If I want to keep the grounding rod close to the house, then I may need to chip away some of the concrete that stretches out underground. I guess it really doesn't matter, but I guess the closer to the house, the better so that there is less chance of someone tripping over it or the mower hitting it.
    Attached Images
     
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #7

    Oct 16, 2005, 07:09 PM
    I just measured, mine is about a foot out from the block foundation, crawl space. I am surprised that 20 years ago, they didn't put in a ground rod. Where does the conduit just to the left of the gas meter coming down from the box go? I would check it out before adding a ground rod.

    Otherwise, either the red or blue looks OK to me.
    harleyds's Avatar
    harleyds Posts: 56, Reputation: 2
    Junior Member
     
    #8

    Oct 17, 2005, 07:05 AM
    Conduit
    The conduit on the left of the gas meter is electrical. The box it is conneceted to is a secondary breaker box someone installed because the house was running on fuses before and there was no room to add a 220 connection. I know for a fact that it leads away from the house about 3 feet and then heads to the right.

    Seems I will go with the blue line location about a foot away from the house. Chances are I will dig down a foot or two first to make sure I don't hit anything. I still have to call the Utility company to do a metal detector check.

    David
    fredg's Avatar
    fredg Posts: 4,926, Reputation: 674
    Ultra Member
     
    #9

    Oct 17, 2005, 07:14 AM
    Grounding Rod
    Hi,
    When all else fails, or to have a "peace of mind", you might consider calling an Electrician, asking for a quote, and having that person install it for you.
    Best of luck,
    fredg
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #10

    Oct 18, 2005, 05:01 PM
    The top of the rod and the wire connector all need to be installed below grade, so no fear of tripping. The wire clamp must be direct buried rated.Most available are already rated for this purpose.

    Bury the wire also, only a few inches deep if only for a short distance is fine.

    I am interested in the wire that comes out from the right side of the meter, runs sloppy on an angle heading directly to the water line. What is this? If this is your "water Ground" I question it's integrity.

    The wire to the ground rod must connect to either the main switch or the meter socket. This may be dictated by the local utility, many do not want the main grounding electrode conductor, (the technical name for the wire you want to install) connected in their meter. This leaves the main box, which has 240 volts and nearly unlimited amperage available.

    Heading the advice to hire a pro is highly recommended, Working in this area requires only qualified personnel with the OSHA approved protective gear if worked live.

    Although ground rods are now required to supplement utility water systems as a ground, rods were not required back twenty years ago. Installation of the new rod and wire is only for a pro, I suggest the existing ground wire and system be checked also. Even if is to clean and tighten the existing connections.

    Good solid, grounding is so important, explaining all the details here is difficult and really not for a novice.
    Borewyrm's Avatar
    Borewyrm Posts: 65, Reputation: 2
    Junior Member
     
    #11

    Nov 29, 2005, 08:10 PM
    One other thing as great advice has already been given. If you do have multiple ground rods from different utilities (tv, phone, electric etc.) they should be all bonded together with at least #4 bare copper to equalize the ground potential. The other pitfall people make is that even those expensive UPS systems, surge protectors, and panel surge arrestors aren't going to be worth squat without a soldid ground. I actually heard the home depot electrical ace tell a woman who was concerned about the corroded groundwire on her equally corroded water service that a nice 300 dollar UPS would be an easy fix.
    Monahans4@msn.com's Avatar
    [email protected] Posts: 1, Reputation: 1
    New Member
     
    #12

    Dec 5, 2005, 03:09 PM
    Grounding rod inside the basement
    We are finishing off a basement and have the grounding rod in the floor where we plan to place a couch. What should we do? It's low enough that the couch can sit over it. Is that dangerous?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #13

    Dec 5, 2005, 03:17 PM
    Large bare, electrical connectors do deserve respect, but the ground rod is just that, ground. It shouldn't be a problem.
    Borewyrm's Avatar
    Borewyrm Posts: 65, Reputation: 2
    Junior Member
     
    #14

    Dec 8, 2005, 06:15 AM
    I have a question. Has anyone here (peeks over at tk) used hammerlock type clamps as opposed to acorns? I was wondering if they work well with stranded copper ground wire. The photos I have seen all have solid.
    nubbin248's Avatar
    nubbin248 Posts: 1, Reputation: 1
    New Member
     
    #15

    Aug 18, 2009, 12:00 PM
    I sink ground rods in Dallas clay soil with water. Water wets soil, push into mud, pullout and repeat, and repeat...
    The last few inches, I hit it with a 5 pounder.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Grounding Bar vs. Neutral Bar? [ 14 Answers ]

Hello all. I have extended the wires from an unused 240 outlet to the backyard for a spa via a sub-panel. I also hooked up a new grounding electrode near it to avoid having to run a fourth wire all the way back to the main panel. This fourth wire goes to the small grounding bar in the sub-panel...

Generator grounding [ 5 Answers ]

I just bought a 4400/3500 watt generator for a building project. The directions say that I need to ground the generator with a suitable grounding rod and stranded No. 12 AWG wire. I have never heard of contractors grounding their generators. Are they being careless, or are my generator...

Grounding an Outlet [ 22 Answers ]

I am moving into an older house that has only 2-prong outlets. Some are 3-prong, but they are not grounded (I have a power strip that tells you if it is gounded or not). I found this at Ace Hardware....

Detached garage grounding rod or not [ 1 Answers ]

Hi, I just ran across another problem. I will be running 40 amps 240 volts out to my garage via underground 8-3 plus ground. Do I need a grounding rod at the garage or is the ground via the service cable to the garage enough? I have seen both and am not sure why. Is the 240 volt service to the...

Help - What to do with the Grounding Wires [ 5 Answers ]