    Wire size for 70 Amp furnace
    I've installed a heat pump with an auxiliary heating coil. It requires a 70 amp 2 pole breaker. I was informed I need a #3 wire, yet the connections on the heat pump will only fit a #6. The dealer has told me, he has never seen anything more than a #6 on any installation. What do you think?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 6, 2010, 07:15 AM
    First I would like to know how the 70 amp breaker is determined.

    Assuming that is correct, next we need to detemined the wiring method.

    I suspect NM-B cable, AKA Romex.

    #6 NM-B cable is only rated to carry 55 amps. #6 NM-B cable cannot be connected to a 70 amp breaker, period. However, I am sure this has been done many times. Does not matter, it is wrong.


    If #6 THHn is pulled through conduit or MC cable is used, then the #6 is rated 65 Amps.

    If this is the case, #6 THHN or MC cable can be connected to a 70 Amp breaker, as we are allowed to go to the next standard size breaker. 65Amp Cb does not exist, 70 Amp CB does exist.

    If you need to use Romex, then #4 NM-B cable will be needed.

    Even if the buidling has all Romex as the wiring method, there is no reason not to use MC cable so the # 6 could be used.
    nuttup's Avatar
    nuttup Posts: 3, Reputation: 1
    New Member
     
    #3

    Aug 7, 2010, 03:04 PM

    Thanks for your reply.
    The Heat pump specifies a breaker size of 70 amp.
    I'm using a NMD 90 cable. (#3)
    Is a THHn cable a metal shielded cable? I'm thinking of running the NMD90 3.3 to a sub panel and then run an MC #6 from the panel to the furnace. Do you think this would meet code?
    Thanks again.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Aug 7, 2010, 03:38 PM
    Quote Originally Posted by nuttup View Post
    I'm thinking of running the NMD90 3.3 to a sub panel and then run an MC #6 from the panel to the furnace. Do you think this would meet code?
    Code where? We have no idea where you are from.
    nuttup's Avatar
    nuttup Posts: 3, Reputation: 1
    New Member
     
    #5

    Aug 8, 2010, 07:55 AM
    Quote Originally Posted by stanfortyman View Post
    Code where? We have no idea where you are from.
    This installation is in British Columbian, Canada.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Aug 9, 2010, 05:48 AM
    We can only quote the National Electric Code, enforced in the USA.

    Sounds like your plan will meet CEC code, but you really should checked with your local Code Enforcement Office.

    THHN is a type of insulation that is pulled through conduit.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire size & conduit size for 60 am subpanel 150 from source [ 9 Answers ]

Indiana question: I want to install a 60amp subpanel 150 feet from the main panel. This is all exposed runs both inside and out in a commercial envirenement. What gauge and type of copper wire and what size conduit whould I use. How often should insert a junction box in the run. John

Can I run a 50 amp subpanel if a 100 amp main if so what size wire [ 1 Answers ]

Can I run a 50 amp subpanel from a 100 amp main and if so what size wire

Wire size for 80 amp breaker [ 1 Answers ]

I am installing a 80 amp sub panel and need to know the size of the wire from the main to sub

Wire size wire & circuit breaker do I need for a 15.8 range [ 2 Answers ]

What size circuit breaker & wire size do I need rfor a 15.8 raqnge ?

Sub Panel AMP Size and Supply Wire Size [ 1 Answers ]

I would like to install a sub panel in my garage I was told to run 6/3 Romex to supply the sub panel and have done so. The run is about 65 feet and I am now wondering after reading this site what is the max I can get for this size wire? I plan to supply a compressor (20 amp) and the garden...


View more questions Search