    Transformer wiring
    I am trying to wire a tranformer into a lennox furnace, unfortunately , though she would not admit to it, the girl where I bought the transformer , pulled off at least 2 of the wires on the primary side of the old transformer, of course I wrote down which color wire came off from where , not where they were on the transformer. I need to know what connects to the following on the primary side. COM - This is Wht 120 This is blk 208 this is red, and 340, this is orange. These are the markings on the primary side. I am comfortable I know where the wires on the secondary (24 v side go) Thanks
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Apr 23, 2007, 09:53 AM
    If it is a standard gas/oil furnace you will use the white and black for 110 volt operation. If it is a electric furnace setup you will need to use th wires for 220 volts.
    bikerguy's Avatar
    bikerguy Posts: 87, Reputation: 13
    Junior Member
     
    #3

    Apr 23, 2007, 10:12 AM
    Is there A COM? Or is that your signoff. Com normally refers to the common wire that you use with any of the other tap points from 120 up. I would say com and 120 if that's what voltage you are using.. An ohm meter would prove this out as you would see the most resitance on the highest voltage tap and you could confirm the COM
    JackT's Avatar
    JackT Posts: 260, Reputation: 19
    Full Member
     
    #4

    Apr 23, 2007, 01:46 PM
    Most multi tap transformers use Black as common, with the white wire for 120 volt, red for 208, orange for 240, and black/red for 480.
    tdenison's Avatar
    tdenison Posts: 2, Reputation: 1
    New Member
     
    #5

    Apr 25, 2007, 04:24 PM
    Thank You for your help. Here is the latest. I realized the lady actually gave me back a completely different transformer. I went back and she did find the right one. Now she gave me a replacement. The old one had Red and Black for the primary side, one went to one side of the power in, the other to the other side. On the secondary side , it was blue and yellow. On the new one, the secondary side was the same, no problem, on the primary side , in addition to the red and black, there was also a white and orange. I figured I would follow color code so connected the red where the old red had went and black to where the old black went. Flipped on the breaker and pow, it blew the transformer. I am assuming this means the red and black on the new one are different then the red and black on the old one. What I need to know is which of the 4 wires on the primary side should go to primary power, and Is it OK to just cap off the two wires not being used? Thanks fyi , this is strickly an electric unit, heat inside, air outside. Wiring on new primary : wht=com, Blk=120 red=208 org=240. Sorry I am a novice so I am not sure which should go where, as stated the old one only had black and red and both went to input power from the breaker box, one on one 120 side and the other on the other 120 side.
    JackT's Avatar
    JackT Posts: 260, Reputation: 19
    Full Member
     
    #6

    Apr 25, 2007, 04:47 PM
    You most likely have a 230 volt unit. If so, you need to use the black & orange lines. Are you sure you don't have a short on your secondary (24 Volt ) side? Is there a fuse in the secondary line? If not you should install one, this could be what's taking out the transformer.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Installation of Transformer wiring [ 1 Answers ]

I have central heating and my Transformer has burned out. I have a new Transfomer and I'm having trouble installing it with the different types of wires. Can you please assist me with installing the correct wires into the Transformer.

Low voltage wiring/transformer [ 5 Answers ]

Hello, I have low voltage wiring run for undercabinet lighting in a newly remodeled kitchen the end of that low voltage wire run is in an unfinished basement. Along with that I have a 120v that line that is powered or will be from a wall switch upstairs in the kitchen and also ends in the...

Wiring 12 volt transformer [ 1 Answers ]

I have recently installed some 12 volt miniature lights in home. I have them working now but began wondering about how I have the 12 volt transformer wired. The lights are on a switch and I have the transformer in the line before the switch. Thus I have power at the transformer all the time. Is...

Transformer wiring of tempstar furnace [ 2 Answers ]

Hi Labman, I had a bad relay (LY2 24 VAC), so I marked the wires on piece of paper to take it off and install the new one. The problem that I lost the paper somehow and I don't have a clue how to install the new one. I know that the I/p is 120 VAC and the o/P 24 VAC. How ever I have 6-wires...

Transformer wiring [ 18 Answers ]

I have a Payne furnace that had a Intermatic wall timer connected to it. The timer was causing the furnace to come on at various times and sometimes just the blower (it'll run all night). If I hit the on/off button on the timer, it'll disable it for 24 hours. I attempted to disable the timer...


View more questions Search