    220v lines in garage question
    My son wants to put two 220v lines in his garage.
    There is a 100 amp panel inside the garage. ( 100 amp panel outside also )


    In the 100 amp panel inside the garage... we plan to put a 60 amp breaker that will feed a subpanel approx 2' away... that will have two 30 amp breakers.


    We plan to run #6 from 60 amp breaker to subpanel.( approx 2' )

    We plan to use #10/2 for the 30 amp breakers with runs of approx 10' and 18'.


    Can the white of the #10/2 be used as a hot ?


    Can a stranded wire be used as a ground ?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Jan 29, 2018, 06:29 PM
    Yes to both. Mark the white as black or red at both ends. I use a big magic marker. THHN is approved as a ground and much easier to pull, make sure it is green. BTW, it is now 240 VAC.
    draftd's Avatar
    draftd Posts: 23, Reputation: 1
    New Member
     
    #3

    Jan 30, 2018, 03:55 AM
    Thank you ma0641.
    draftd's Avatar
    draftd Posts: 23, Reputation: 1
    New Member
     
    #4

    Jan 30, 2018, 09:48 AM
    Addon to my prior 220v question
    Here's the subpanel purchased.

    Would our wiring be correct locations ?
    Attached Images
     
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #5

    Jan 30, 2018, 02:08 PM
    Not sure what that is, the holes on the right are for a neutral bar if you needed 120VAC
    draftd's Avatar
    draftd Posts: 23, Reputation: 1
    New Member
     
    #6

    Jan 30, 2018, 03:11 PM
    Thanks ma0641

    Assuming our wire locations will be correct beings you did not mention anything wrong.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #7

    Jan 31, 2018, 01:27 PM
    Looks OK. As long as you stay in the same building, you do not need a separate ground. The ground bar should not be bonded to the subpanel box, it is grounded through the main panel. In the picture, it looks like it is isolated, which is what you want. I see a screw through the plastic, that is OK.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #8

    Feb 2, 2018, 10:34 AM
    Referring to "what is this?" - this is used to bond the neutral to the ground. This is required by the code to happen in only one location and that location is at the first overcurrent device or main circuit breaker.
    Being that this is a sub-panel, the neutral and ground must remain electrically separate from each other.
    The "what is this" bonding strap should be removed as you will not need it. What you need to do is get another ground bar and attached it directly to the box. The two holes on the right side of the box are for this ground bar. All ground wires will need to go to this bar.
    All neutral conductors are required to go to the isolated bar already shown.
    The white (neutral conductor terminates at the lug you marked as "#6 grnd". The bare or ground conductor goes to the new ground bar.

    By the way you need to use #6/3 which has (2) black wires, (1) white wire and (1) bare ground wire.
    Hope this is helpful
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #9

    Feb 2, 2018, 05:17 PM
    Please don't forget the Ground Rod and the ECG if this is a remote building.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #10

    Feb 3, 2018, 07:57 AM
    This is 240 only and 2 ft. away from main panel. No neutral.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #11

    Feb 3, 2018, 08:57 AM
    OK, so you don't need the neutral, then take the "what's this" bonding strap and connect it to the ground bar to effectively bond the panel enclosure to the equipment ground...
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #12

    Feb 4, 2018, 01:01 PM
    Lot of great answers above, could do this, a Quad 30/30 Breaker:

    https://www.ebay.com/i/272886286753?chn=ps
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #13

    Feb 5, 2018, 10:01 AM
    Oh Yeah, The Ground in Your Electrical Boxes Need a Solid wire for a Ground, No Stranded

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I need Circuit diagram to make 220v power point by using two 110v lines [ 9 Answers ]

I need Circuit diagram to make 220v power point by using two 110v lines. Can any one do this for me. Thanks

220V Svc to garage/ [ 1 Answers ]

Can anyone tell me hot to run a 220V breaker box to an out bldg 75' from the house. Do I use 10-2 w/grnd to the outbldg? And how do I attach the wires in the new smaller svc box ? Thanks

Connecting 220v garage heater [ 2 Answers ]

Good Day, I have a 220v outlet in the garage (wires are red, black, white) the red and black are connected to the 30 amp breaker in the house. Now the heater has (red, black and copper), the copper I've grounded and I figure red goes to red and black to black but what about the white.

New wiring to my garage for a small 220v welder. [ 3 Answers ]

Greetings all, I have a small dual voltage welder 150 amp output @ 220v, 90 amp @ 110v, that I have used as a portable for a number of years. It is a great welder. When I got it, I had it converted to a 110v plug by my partner(who is long gone), as it is used from regular 110 outlets all the...


View more questions Search