    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #1

    Nov 28, 2017, 10:23 AM
    Tiki Hut electrical failure
    Okay, my sister-in-law has a wired dedicated branch circuit (120V / 20 A) Tiki Hut in the back yard.

    The feed is on dedicated breaker feeds a GFCI receptacle (which protects all of the downstream outlets in the Tiki Hut) and then underground in PVC conduit over to the hut. The conductors are 12 AWG wires, not cables.

    Problem: The GFCI receptacle kept tripping as soon as it was energized.

    A feed wire from the overhead outlet supplies two post mounted switches - SW1 to the light on the fan. - - SW2 Rotary light switch for fan.

    Problem: The feed from the outlet box to SW1 was stripped and horseshoed bent to the SW2 screw post and then to feed SW2. However it came loose and arched, blowing the switch (SW blew to an open condition) and the rotary switch and taking the GFCI with it every time power is reset.

    I replaced both the SW1 and SW2 (now a 3 speed fan switch)

    New problem: The SW1 now operates properly, but the light does not come on, nor does the rotary switch activate the fan. Also there are several receptacle outlets arranged under the Tiki Hut's canopy that are also dead and have been all along.

    What could the SW1 to the light take out that killed everything else?

    There is a nasty looking hive near the fan base overhead outlet box and I have no real desire to see if it is active just to get into that outlet box. Any creative ideas?
    talaniman's Avatar
    talaniman Posts: 54,327, Reputation: 10855
    Expert
     
    #2

    Nov 28, 2017, 11:02 AM
    Wasp and hornet spray foam from home depot. Works GREAT!
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Nov 29, 2017, 05:59 AM
    Unfortunately the answer is correct but wrong. :) The creative ideas I'm looking for are with the wiring, not the hive.

    I guess it's "Up the ladder I go." I just don't understand how a switch failure can take out the whole circuit yet not continue to trip the GFCI or the breaker. Oh, well, dirty words. I guess I'll hope for warm, pleasant weather.
    talaniman's Avatar
    talaniman Posts: 54,327, Reputation: 10855
    Expert
     
    #4

    Nov 29, 2017, 06:52 AM
    I know, tracing wires looking for fault conditions is NO fun. Hard to be creative about tedious work you cannot see.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Nov 30, 2017, 10:43 AM
    Lightning!! I suspect a lightning flash killed the circuit. I'll know for sure tomorrow when I can get into the canopy.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #6

    Dec 1, 2017, 10:53 AM
    If the NEUTRAL Or Hot Touches Ground it will trip, Are the Light/Fan On Line or Load side of GFI? Some will trip when first applying power, if it doesn't reset, remove load wires, If it still doesn't reset, it is a bad GFI.(Verify Hot and neutral are on Line Side) I am repeating a lot of what you know, you seem knowledgeable, Don't mean to repeat what I know you already know.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #7

    Dec 1, 2017, 12:08 PM
    Name:  j-box.jpg
Views: 191
Size:  321.7 KBName:  Feed & Switches.jpg
Views: 130
Size:  485.6 KBStrat - Unbelievable!

    At the post J-Box, the feed from the GFCI is cut and pig-tailed to supply both switches and then continues up to the overhead. Each switch has a red wire as a return which goes to the overhead.

    At the overhead, the red wires go to receptacles up under the eves instead of to the fan as I first thought. (SW1 snap switch for light / SW2 rotary for fan) NOPE. The fan and light kit are connected to a black which also feeds a receptacle.

    Here are some pics.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #8

    Dec 1, 2017, 03:22 PM
    I wonder if the previous owner had the rheostat to control some receptacles for "mood" lighting and the switch to turn other receptacles off. Still makes no sense to me.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #9

    Dec 5, 2017, 08:51 AM
    Any Luck?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #10

    Dec 5, 2017, 11:49 AM
    Bingo!! As of today. The original owner (may he rot and have limbs fall off) set it up with the toggle switch for 4 separate duplex receptacle outlet boxes up under the eves and two receptacle boxes vertically behind a counter top.

    The rotary switch controlled one duplex receptacle at the top of a shelf. Neither switch had anything to do with the fan or the fan's light, yet both pull chains on the fan were cut off at the fan.

    Anyway, I rewired the toggle switch for the fan's light kit and marked the wire from the switch with blue tape. The new fan rotary switch is marked with black tape. Then I connected all of the receptacles so they stay hot.

    The failure was the blown toggle switch and I found a nicked insulation on a conductor behind the switch.

    Following behind someone can be such a PIA!
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #11

    Dec 7, 2017, 07:58 AM
    Good Deal, I run into a Lot of bad wiring techniques about every day it seems.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electrical circuit failure [ 3 Answers ]

I have a group of wall receptacles (approx 10) that are not working. The circuit breaker is not tripped. The circuit breaker has not failed. In fact, all the CBs on the main panel test out OK. None of the receptacles has a GFCI. What can I do next to determine the problem?

Sears riding lawn mower electrical failure [ 6 Answers ]

I was driving my lawn tractor up a ramp into a truck. It shut down suddenly. No lights. It won't turn over at all. The fuse is OK and the battery isn't dead. Any ideas what would cause the electrical system to shut off?

Can substandard electrical wiring installation at home produce electrical arching [ 6 Answers ]

Can substandard electrical wiring installation at home produce electrical arching? Then fire?

Electrical outlet failure [ 1 Answers ]

My outlet was working yesterday now it is not working. All the breakers are working just that one outlet is not working. Maybe it is the outlet that isn't working please help


View more questions Search