    Low voltage fuse blowing on ac controlboard
    My thermostat went blank so I replaced it. Turned on the heat and nothing, checked the 5 amp fuse and it was blown. The fan turns on until I try to turn on the heat. I disconnected the low voltage going outside and the problem remains. I can turn on the heater by jumping the wires on the control board. Help please!!
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Jan 9, 2017, 12:42 PM
    Not sure where you are jumping? Since it doesn't do it on cool, wiring to compressor appears OK. The Heat relay may be shorted. Remove heat wire in air handler, try again, if it blows, it is more likely in thermostat wiring. Good Luck, keep us updated
    lucian22's Avatar
    lucian22 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 15, 2017, 09:15 AM
    I found a blown 1k ohm resistor. The heater works when I disconnect the blue wire, not trusting that though since it is the neutral.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Jan 15, 2017, 11:06 AM
    Where are you located? Neutral for what? If for the main 120 VAC power, would not work with neutral disconnected and most likely not blue since
    NEC code requires white or gray. In UK and most of Europe, blue is neutral.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Low voltage fuse in a\c [ 2 Answers ]

The 3A fuse in my Air Handler blows

CHALLENGING QUESTION: Low-voltage switch in a high-voltage circuit? [ 6 Answers ]

A project I'm working on has an air pump and a water pump that run during operation. When the water tank that the water pump draws from becomes empty, a liquid level switch will be used to shut off both pumps. The original plan was to just place the switch in series with the power supply for...

Why hrc fuse not used for low voltage circuits ? [ 1 Answers ]

HRC fuse is generally used for medium voltage circuits,what are the reasons for not using it in low voltage circuit.

Bryant Secondary Voltage Fuse keeps blowing [ 7 Answers ]

I have a Bryant 373LAV horizontal furnace and the 3 amp secondary voltage fuse keeps blowing. I swapped the thermostat with the same problem.

Track lights: low voltage vs line voltage.comsume the same electricity in the end? [ 11 Answers ]

Hi! I just installed a section of track light in my living room just to see what it would look like and so far I'm not convinced... you see, I had a regular celing lamp with a 75w incandescent bulb and the room was very well lit... now with the track light I find that I need 3 fixtures with halogen...


View more questions Search