    Conductor sizing
    I have a
    600v three phase gen, 60hz, 40kw, 50kva, 8pf
    Class h insulation
    And a
    Three phase transformer
    45kva, 600v primary
    208vy/120v secondary
    4.8 impedance
    Conductor temp at 170 deg.
    Out of the secondary on the transformer I will go to a three phase panel.
    I need to know the conductor size between the gen and the primary of the transformer and between the secondary of the transformer and the panel.
    Also any tips tricks or hints would be greatly appreciated
    All runs are less than 5 feet.
    Thanks in advance
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jan 2, 2017, 06:42 PM
    Are you seriously asking this question on a Home & Garden message board?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Jan 3, 2017, 05:01 AM
    There is a whole section in the NEC that will tell you how to size transformer conductors.

    Read the Book!!
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Jan 3, 2017, 11:59 AM
    This is hardly a DIY question! Look online at NEC Section 450 and 455.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electrons are emitted from a conductor when the conductor is? [ 3 Answers ]

Multi. Choose... A. exposed to weak light. B. cooled rapidly C. Bombarded by high-speed electrons D. subjected to a small voltage

Wire sizing and conduit sizing [ 8 Answers ]

I am looking for confirmation on some of the info I have found and answers to a few missing pieces. This is regarding wire size and conduit size for service conductors from the meter to the breaker panel (about 30 ft away). Wire Size: 125A service needs #2 copper or 1/0 aluminum -- #6 copper...

Convert 3 conductor range to 4 conductor plug ? [ 4 Answers ]

I'm attaching a photo of the connections on an old range with a 3 conductor plug that I want to convert to a 4 conductor plug. What looks like a strap under the center of the connection block is actually not -it doesn't hook to anything nor is there a screw hole for it to attach to....

Parallel conductor sizing [ 2 Answers ]

I have to run power to a building 1200 amps service, the building is located 1500ft from FPL transformer the voltage will be 277/480, what size wire should I use.

Conductor sizing? [ 5 Answers ]

TK, Cobraguy, Labman, KISS Okay, I now have a nine volume set of current books ranging from simple wiring to the NEC. I also sound some U.S. Navy BPARS manuals and theoretical engineering books from when I went to Internal Corporate electrical schools. Not to mmention product specific...


View more questions Search