    100 amp subpanel
    Hi I am installing a 100 amp 24 slot subpanel in an unattached garage 50 ft away and plan on running 4 wires from the main 200 amp panel in the house, do I use a 100 amp double pole breaker in the feed panel from the house or do I use a double 50 amp breaker?

    Thanks
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Oct 15, 2016, 07:35 AM
    That depends on the size wire your will be using. The breaker protects the wire not the panel.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Oct 15, 2016, 02:50 PM
    A couple of other things:

    1) Will the main panel accept a 100 amp breaker. You need to verify that.
    2) Did you size the load you need to service. 100 amp can support an small home.
    do_hall1's Avatar
    do_hall1 Posts: 2, Reputation: 1
    New Member
     
    #4

    Oct 15, 2016, 05:08 PM
    Thanks, yes I already put a 100 amp breaker in the main panel, and using 2/0 wire. It's actually like a small home 28 x 40 1 1/2 story with small kitchen a full bathroom and heated floors so there will be two hot water heaters and two garage door openers and of course receipts and lights
    Artie62's Avatar
    Artie62 Posts: 8, Reputation: 3
    New Member
     
    #5

    Oct 15, 2016, 09:18 PM
    Depends on the wiring and load. Water heaters pull a lot of amps. Either way you get the same protection since the 50's are bridged. Just use the best quality breakers and a good ground source.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #6

    Oct 15, 2016, 09:50 PM
    Assuming 2/O UF aluminum cable a double 115 breaker is maximum, using conduit and 2/O THHN aluminum wire, 145 double breaker is maximum.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #7

    Oct 17, 2016, 01:15 PM
    You are aware that the secondary panelboard in the garage needs to have its own grounding system. The Neutral bus cannot be bounded to the secondary panelboard.

    That means you need to install a primary and secondary ground rods to ground the panelboard to. Because the garage is a remote structure it has to have its own grounding and bonding system.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #8

    Oct 29, 2016, 08:49 PM
    Quote Originally Posted by Artie62 View Post
    Depends on the wiring and load. Water heaters pull a lot of amps. Either way you get the same protection since the 50's are bridged. Just use the best quality breakers and a good ground source.
    That is completely incorrect.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Overhead from a 100 amp service panel to a 100 amp subpanel in a garage. [ 6 Answers ]

An Electrician friend said I could use #4 copper for the (2)120 volt legs and a conventional Suspension wire as the nuetral. The overhead span is about 35 feet and the overall run From panel to panel is about 70 feet.The supply outlet said to use #2 copper. Also, what type wire for sunlight...

Can I run a 50 amp subpanel if a 100 amp main if so what size wire [ 1 Answers ]

Can I run a 50 amp subpanel from a 100 amp main and if so what size wire

100 amp subpanel [ 1 Answers ]

I see I need to supply moe info, underground from house to pole barn, with mostly 120 volt circuits. Possible 240 volt for air compressor. That why 100 amp panel will do the job. As what to use conduit or direct burial cable not sure yet, depends on price.