|
|
|
|
New Member
|
|
Apr 28, 2016, 04:45 PM
|
|
40 gallon electric water heater wiring question
Hello, my current hot water setup is through a summer winter hookup in the boiler. The boiler is leaking. I need to save the money to replace the boiler, so I was going to install an electric water heater in the meantime. I have a propane stove in place of an electric range that we replaced. My question is can I use the circuit and wiring for the range for the water heater if I change the breakers in the panel from 40 amp to 30 amp? I would also have to add a workbox in place of the old stove outlet and run 10-2 from the box to the water heater. The wiring from the panel to the box is 6 gauge, so I am also not sure if it is OK to connect it to a different gauge.
Thanks in advance for any advice!
|
|
|
Home Improvement & Construction Expert
|
|
Apr 28, 2016, 05:37 PM
|
|
If I understand correctly you have 6-2 from the circuit panel to a box with a 40 amp breaker. You want to run 10-2 from the box to the water heater and change the breaker to 30 amps.
Yes, you can do that, it is the way I would do it.
|
|
|
Uber Member
|
|
Apr 28, 2016, 05:42 PM
|
|
That is OK. You can connect different gauges as long as the lower amperage is the protected source. Was the range, 120/240 or straight 240? The WH is 240. You can use the range wiring but if it is a 4 wire 120/240 setup, you would cap off the neutral.
|
|
|
New Member
|
|
Apr 29, 2016, 03:20 AM
|
|
Thank you very much for the quick responses! Yes, the range was 120/240. I was thinking eventually the range plug can be put back in the future if need be and what I wanted to do will avoid tearing out the entire basement ceiling to run a new wire to the panel. Just wanted to make sure I was not making a problem for myself. This will save me a lot of aggravation until I have the boiler replaced. Thanks again!
|
|
|
Uber Member
|
|
Apr 29, 2016, 07:21 AM
|
|
The only thing you might need to be careful with is wire nutting the #6 strand to the #10 solid. Make sure you get good contact with a big wire nut. You may not need a new workbox if you pull the old receptacle, add an extension ring to the wall box and then add a cover. I believe the extension ring has a knockout for the Romex.
|
|
|
New Member
|
|
Apr 29, 2016, 09:14 AM
|
|
Just out of curiosity, I happen to have some 8-2 that would reach from the connection to where the water heater would be. If I were to use that, could I just leave the 40 amp breakers as is? Or is that a potential problem? I realize it is overkill for what the heater needs.
|
|
|
Uber Member
|
|
Apr 29, 2016, 12:46 PM
|
|
I don't know if the HW heater wiring would handle 40 Amps, most are 4500 watts. If a short were to occur, it might fry the heater before the breaker tripped. You can run 8, but I would change the breaker to 30. Breakers are cheap and that is your protection, not the wire size. You could run a 15 Amp breaker on a #6 but couldn't run a 30 Amp on a #12, the breaker might not trip until the HOUSE FIRE consumes everything!!
|
|
|
Ultra Member
|
|
Apr 30, 2016, 05:35 PM
|
|
I am not going to condone or recommend this... BUT...
I have seen dryer / range pigtails wired to an electric water heater to utilize the existing plug. The breaker was changed to suit the 30amp requirements.
Now this is the Ozarks and I have seen many other unusual methods of wiring, plumbing and construction. I'm just sayin'...
|
|
|
Home Improvement & Construction Expert
|
|
May 1, 2016, 07:49 AM
|
|
I happen to have some 8-2
I wouldn't mess with the 8-2. 10-2 is not that expensive, Electrically you can use it but its not worth the savings for extra difficulty pulling it and making your wiring connections.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
20 gallon vs 30/38 gallon electric hot water heater?
[ 12 Answers ]
I am faced with the same hot water heater question as others. I am building a small utility building on property on Texas Gulf Coast. Within this building I want to put a small shower stall with a hot water heater to supply this shower and occasionally use a washer. It will be for...
Is a 60 amp breaker too much for a 40 gallon electric water heater?
[ 2 Answers ]
I had a tankless water heater installed and after a lot of trouble with it, it died. So, I want to go back to a regular tank water heater. Can I hook it up to the existing electric service to the tankless, which is really big: two pole 60 amp breaker with a 6 or 8 wire?
I have the feeling that...
View more questions
Search
|