    A 20 amperes circuit breaker safety carry a load of ?
    What is the safety carrying load of a 20 amperes circuit breaker?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Feb 22, 2016, 12:18 AM
    A 20 amp circuit breaker can carry 20 amps. However a 20 amp circuit breaker requires 12 gauge wire or larger. A 12 gauge wire can carry 20 amps. However, there is an additional restriction, "a dedicated branch circuit rating shall be not less than 125% of the non-continious load." What that effectively means is that a dedicated branch circuit can carry 80% of its rating.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #3

    Feb 22, 2016, 05:39 AM
    May I ask why the question?
    Is this for a specific application or just a general question?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Feb 22, 2016, 11:48 AM
    A breaker primarily protects in an overcurrent situation. People think a 20 Amp breaker will automatically shut off at 20 Amps. That is not the case, I have measured more than 20 Amps flowing through a 20 Amp breaker. The bigger issue is the wiring insulation on a continuous feed at 20 Amps, it can thermally deteriorate and burn off, possibly causing a short, at least in a grounded metal box, at which point the breaker will(should) trip. I have replaced quite a bit burned wire in a plastic box and raceway where the breaker never tripped, the wire melted and broke the circuit. See HKStroud comment regarding circuit loading.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #5

    Feb 23, 2016, 07:38 AM
    If you exceed 80% of the breaker capacity it starts to heat up. Breakers can safely carry their rated capacity, but that should be avoided. Overheating and premature failure is what you can expect at near capacity.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Maximum load on 20 amp circuit breaker [ 14 Answers ]

I am aware of certain normal maximums. I guess I'm looking for somebody to tell me that I'm pushing things too far, or not. I want to hook up a portable air conditioner (Sunpentown WA-1220E) which is rated at 950 watts (and, mysteriously, at 9.0 amps) along with an HP 4Si printer, which is rated...

Circuit breaker load [ 3 Answers ]

I have 70 amp. Breaker, and has 2 unit /motors to be hooked up Combined load of motors 49 amps.?

Main circuit breaker size and load? [ 2 Answers ]

My panel box and breakers are Bryant, with about 20 positions for breakers. My question is, my main breaker is 2, 60 Amp breakers doubled, What is my service? 60, 120 ? And what are the total amount of 15 and 20 amp breakers I should have in this panel?

Calculating load per circuit breaker [ 3 Answers ]

How do I calculate how much load I can place on a nn amp circuit breaker? My knowns would be voltage and watts per hour. How to I allow for (amp draw) when a shop motor or freezer compressor spins up at initial start?

Circuit breaker load [ 2 Answers ]

I'm remodeling my basement, & putting in a lot of elec'l outlets. Wondering how many outlets, or how do I figure how many, I can put on one ckt brkr. I'm using no. 14 Romex & 15 amp brkr. Tom :confused: