    Yeah, that shouldn't keep the ignitor from getting hot, only shut it off quick.
    Riles530's Avatar
    Riles530 Posts: 15, Reputation: 1
    New Member
     
    #22

    Dec 15, 2015, 12:57 AM
    I'm stumped, had to call a specialist, I'm betting on the (hot surface igniter module) being the issue, I'll find out in the morning, I'll pass it along, thanks for the assistance, with your help, I have a little better understanding of the proper operation of this unit
    parttime's Avatar
    parttime Posts: 1,440, Reputation: 113
    Ultra Member
     
    #23

    Dec 15, 2015, 04:39 AM
    Thanks Riles, update will surely help someone else down the line.
    Riles530's Avatar
    Riles530 Posts: 15, Reputation: 1
    New Member
     
    #24

    Dec 15, 2015, 08:32 PM
    the hose from the induction blower to pressure switch had a split in it at the end that I had shortened and re applied after testing the pressure switch and there was a loose/broken power wire on the side of the NEMA box that contains the module and circuit boards, thanks again for your assistance
    parttime's Avatar
    parttime Posts: 1,440, Reputation: 113
    Ultra Member
     
    #25

    Dec 16, 2015, 09:16 AM
    Thanks for the update, I'm glad you're warm again.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Have a rheem criterion 2 gas furnace (1X2000), our gas was out for three days (Tucson [ 0 Answers ]

Have a rheem criterion 2 gas furnace (1X2000), our gas was out for three days (Tucson Az ) Now it’s back on, and both furnaces start and stop about ever 4 to 10 minutes

Rheem criterion furnace fan will not work in the fan on position [ 1 Answers ]

I have a Rheem criterion gas furnace which works great ac/heat but I want to use the fan only without the ac/heat and the fan will not run in the on position but does run with the ac or heat on, any suggestion's... I put in a new thermostat and it is installed properly ( honeywell) I called the...

Fan limit settings for a RHEEM Gas Furnace Model 3214-100FB [ 1 Answers ]

I have a RHEEM Gas Furnace Model 3214-100FB. My problem is that when the heat shuts off the fan keeps moving until all the hot air is removed from the vents. The fan then continues to blow until the house becomes cool again, which then causes the heat to have to come back on. What are the proper...

Rheem Gas Furnace Fan limit switch settings Model # 3214-100fb [ 1 Answers ]

What are the proper settings for this particular model. The fan stays on way to long after the heat/fire shut down, which then causes the house to cool down quickly.


View more questions Search