    #1

    Feb 16, 2015, 06:49 PM
    Heil 7000 Gas Furnace
    Heil
    Model # NUGK075DG08

    I am stumped. Furnace was short cycling at first. Call for heat, Inducer motor comes on, Ignitor ignites pilot, Safteties all NC, Gas valve opens , burners lit, heat ing begins Blower fan comes on then roughly 1 minutes latrer kicks out on high limit. Found Dirty coil ,Dirty blower wheel, dirty secondary heat exchanger. Cleaned all look like brand new now. Drain clogged after cleaning flooding back into inducer motor wheel. Cleared the clogged line everything drained perfectly. Now cannot get unit to ignite . Does the Honeywell control box have to be mounted to ground it properly ?
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #2

    Feb 16, 2015, 07:51 PM
    All boards I am aware of need a good ground. Some controls have one or more of the mounting holes sleeved with brass. This is supposedly a source of grounding.
    bollingcs's Avatar
    bollingcs Posts: 3, Reputation: 1
    New Member
     
    #3

    Feb 16, 2015, 08:09 PM
    Ok the only thing I haven't done is mount the control box back to the unit. So this has to be my problem
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #4

    Feb 16, 2015, 10:13 PM
    Give it a try & let me know.
    bollingcs's Avatar
    bollingcs Posts: 3, Reputation: 1
    New Member
     
    #5

    Feb 17, 2015, 04:49 PM
    Ok so I mounted the ignition control box. Got ignition, pilot proved gas valve opened. When fan started gas shut off. Tested fan limit control and limit. Limit was faulty, so changed the limit and it worked perfectly.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

1992 Heil 7000 furnace [ 2 Answers ]

Last night I touch two red wires and a part fell of my furnace. I was able to put the part back on but it must be broken to come off that easy. I think it is called a flame rollout switch or sensor. Should this fall away from its location?

HEIL 7000 furnace [ 0 Answers ]

Furnace won't stay lit iv'e tried jumping limits and roll over switches volt meter reads 24 volts what should I do could it be the gas control valve?

HEIL 7000 gas furnace with 2 questions [ 0 Answers ]

Gas ignites stay lit till blower fan turn on then gas flames shut off. Then when calling for more heat same thing happens. Also, noticed some water/moisture in my draft inducer fan housing. Is the moisture normal since it does have hoses connected to it? Many thanks for the help. Rich

7000 Heil Furnace [ 1 Answers ]

My Heil 7000 furnace, installed new in 1993, is leaving a wet spot on the floor just below the lower right panel edge. When I slide my finger along this lower right edge, there is accumulated water, which is dripping ever so slowly, causing the wet spot. What might be the cause of this never before...

Troubleshooting heil 7000 gas furnace [ 1 Answers ]

On initial start up on my Heil 7000 furnace it is making one heck of a noise until the blower comes on at which time everything is normal. Heater is working perfectly at that point. Do you have any ideas?


View more questions Search