    I keep having to replace the thermocouple
    The valve worked great for 5 or maybe 10 years and then toward the last couple months of last years heating season I had to replace the thermocouple 4 times.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #2

    Sep 5, 2013, 06:21 PM
    The pilot may be burning too hot or the thermocouple may be positioned wrong. Does the pilot sound like a miniature propane torch with a blowing sound? The pilot flame should be a soft flame not one with a sharp point.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to replace thermocouple [ 1 Answers ]

I would like instructions on how to install a new bfg conversion kit I am replacing the old one

How do you remove shroud to replace thermocouple [ 3 Answers ]

There is approx 1" square shroud or shield surrounding thermocouple making the thermocouple connector innaccessable. I would like to know how to remove this shield. Furnace is Coleman LP gas model 7680A Series 856. 80,000 BTU Serial 127564502

How to replace Thermocouple in Gas Water Heater [ 2 Answers ]

Hello - I need help in removing the thermocouple in the gas water heater made by State Industries. It seems very difficult to reach inside.

How risky is my plan to replace thermocouple? [ 3 Answers ]

I believe I have located the problem with my old Luxaire Forced Air, Natural Gas Furnace. The furnace fails to light, very randomly, when the temp drops below the thermostat setting. I noticed that the colder it gets, the more common the problem. I discovered that if I use my hair dryer, and...


View more questions Search