    How do I test for bad contacts on condenser
    Hi hvac guys; this is my problem. I have a new t-stat installed there is 240v power at contact l1 -l2 single pole) . There is 24v across contacts. So when all the power is turned on , I turn the t-stat down below the room temp. (room-85--t-stat down to 60) wait 5- min or so . Nothing starts. Air-h nothing . Cond unit nothing. The contacts do not pull in. But : If I push them in manually the comp and comp fan at the cond unit runs. Let go and cond stops. Also the air handler blower will not start at all. Even when the cond. Is started manually. Im hoping you may have an answer to this trouble shoot . Thank you. Chag.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Aug 24, 2013, 03:56 PM
    If you can manually close the contactor and everything works the contactor points are good. The question is whether the coil is good.

    Disconnect the low voltage wiring and do a continuity check of the low voltage leads to the coil of the contactor. You should have voltage between the low voltage wiring and ground. With low voltage wiring disconnected you should also have voltage between wires. With low voltage wires connected to contactor your meter should show no voltage or almost no voltage between terminals. That would be because the voltage is going through the coil and should be equal. If coil is good the terminals should show no voltage between terminals but each should show voltage to ground. If coil is faulty there would be no current going through coil so terminals would show difference in voltage.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #3

    Aug 24, 2013, 06:50 PM
    I suspect you've wired something wrong. If you are getting 24 volts at the contactor, you haven't blown a fuse or transformer. Double check the wiring on the stat & configuration of the stat if it is one which can be configured for different applications.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #4

    Aug 25, 2013, 10:15 AM
    24v across contacts? Do you mean you get a 240v reading when checking from one side of contact to the other? Or you are getting 24v to the coil of the contactor? If the air handler is not coming on, I do think you may have blown a low voltage fuse, or transformer on the airhandler when wiring the new stat. This would cause the air handler to not come on and the outdoor unit to not come on. Check for power to the indoor air handler. Check for 24v between R and C at the air handler control where the t-stat wires hook. If you don't get 24v there, you have a fuse or transformer issue in the air handler.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Will a bad Capacator cause a Condenser Fan Motor To get hot? [ 9 Answers ]

My Central A/C is starting to blow fuses. The fuses are located in the A/C unit. The fuses blew and when I replaced mthem it took about 9 hours and the fuses both blew again. I replaced them and they blew after about 20 minutes. They are 30 amp time delay fuses. I checked and the fan motor was very...

Why a condenser will melts the contacts of a contactor [ 2 Answers ]

Why a condenser melts the contact of a contactor

Condenser fan not spining, contacts pull in and there is a humming, [ 1 Answers ]

Condenser fan motor not spining, fan blades move easily, contacts pull in and there is a humming, compressor starts heating up, is it the capacitor? Rheem residential unit

How to import contacts from my Outlook 2007 contacts to BT Yahoo contacts? [ 2 Answers ]

I'm hoping that if I can import my list of Outlook contacts into BT Yahoo webmail it might stopping blocking emails from known friends. There appear to be no instructions for importing Outlook 2007 contacts into BT Yahoo/Talk21. I am following the instructions for earlier versions of Outlook, have...

Old Luxaire condenser fan has gone bad [ 3 Answers ]

'76 Luxaire res unit, model EEC048FAB, sercial 195103002440, with condenser fan motor from Electric Motors and Specialties. Motor mmodel 9-131HU416-01, 1/4/hp, 230V, 1 ph, 60hs, 2.8 amps, 800 rpt, rot ccw, serial p76. Fan motor bearings bad - have been super-lubeing it for yers to keep it going but...


View more questions Search