Inside and outside unit won't shut off outside unit new
Compressor was bad got new outside unit now the inside won't shut off or shut off outside unit
|
|
|
Ultra Member
|
|
Jul 29, 2013, 01:37 PM
|
|
If neither unit will shut off inless you turn of breakers then the probem is in the t-stat or t-stat wiring. Or do you mean the unit will not get to temp thus not shut down. In that case could be a number of things including freon problem or unit does not match or lines was not properly vacumed
|
|
|
New Member
|
|
Jul 30, 2013, 07:11 AM
|
|
We removed the thermostat from the wall and they still both run I really think the outside unit is wired wrong and the guy says it isn't and wants to charge me to come c so for 3 ays I been pulling the breaker to let it stop for awhile before it blows
Originally Posted by Joshdta
if neither unit will shut off inless you turn of breakers then the probem is in the t-stat or t-stat wiring. Or do you mean the unit will not get to temp thus not shut down. in that case could be a number of things including freon problem or unit does not match or lines was not properly vacumed
|
|
|
Ultra Member
|
|
Jul 30, 2013, 01:48 PM
|
|
Are any wires touching each other at the t-stat. it your system a gas furnace and ac or a heatpump?
|
|
|
New Member
|
|
Jul 30, 2013, 02:35 PM
|
|
No thermostat isn't hooked up at all right now and it is a ac/heatpump
Originally Posted by Joshdta
are any wires touching each other at the t-stat. it your system a gas furnace and ac or a heatpump?
|
|
|
Ultra Member
|
|
Jul 31, 2013, 01:44 AM
|
|
Yellow and red t-stat wires are touching somewhere. This is the only way both units would run
|
|
|
Uber Member
|
|
Jul 31, 2013, 06:00 AM
|
|
Identify thermostat wires at Air Handler, remove, and test for open between each of the wires, then twist all together at one end, go to the other and verify you have continuity, with all the wires disconnected at the Air Handler, It should not run, If it doesn't, it was a short in the wiring.
If it still keeps running with the wires disconnected, the Thermostat is not the problem, Problem is in Air Handler.
|
|
|
New Member
|
|
Jul 31, 2013, 07:24 AM
|
|
A friend is coming today to check because the
Thermostat isn't even wired and either unit will shut off I really think he didn't wire outside correctly thanks will post results
Originally Posted by Joshdta
if neither unit will shut off inless you turn of breakers then the probem is in the t-stat or t-stat wiring. Or do you mean the unit will not get to temp thus not shut down. in that case could be a number of things including freon problem or unit does not match or lines was not properly vacumed
|
|
|
Uber Member
|
|
Aug 1, 2013, 06:09 AM
|
|
I Understand thermostat is not hooked up, did you read the above post, especially the part about disconnecting the wires in air handler, to be sure a short on the thermostat wires is NOT the cause.
|
|
|
New Member
|
|
Aug 1, 2013, 06:22 AM
|
|
Has to be outside I think cause that was the only wires he messed with my friend couldn't come last night so they both still on and I. Afraid to mess with it
Originally Posted by Joshdta
yellow and red t-stat wires are touching somewhere. this is the only way both units would run
|
|
|
New Member
|
|
Aug 1, 2013, 06:24 AM
|
|
I just saw you post I don't know what the air handler is lol
Originally Posted by Stratmando
I Understand thermostat is not hooked up, did you read the above post, especially the part about disconnecting the wires in air handler, to be sure a short on the thermostat wires is NOT the cause.
|
|
|
Uber Member
|
|
Aug 2, 2013, 07:20 AM
|
|
The Inside Unit is commonly called an "Air Handler", and the unit outside, the "Compressor Unit",
The Air Handler has a 24 volt transformer, and supplies power to the thermostat, the thermostat will make connections to trigger relays in the Air Handler, to turn on the Fan and compressor for cooling, or the fan and heat strip for heating.
If thermostat wires are disconnected at the Air handler, and it still runs, problem is at the air handler with a relay stuck, or support electronics energizing relay.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
A/C unit. Inside rotating fan won't come on
[ 2 Answers ]
I noticed how hot it was and the inside temp has higher than what the thermostat was on. The outside unit runs fine. When I turn unit on seems like inside wants to come on ( I hear air through coils) but fan won't turn. I tried to manually turn it and it turns freely. Any suggestions