    8-4 romex amp rating @ 130 ft.
    What is the amp rating for a 130 foot run of 8-4 romex?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    May 8, 2013, 11:59 AM
    Amp rating doesn't change regardless of length. Voltage drop is the issue and it affects motors, compressors etc. What are you planning on this circuit?
    stevestoy's Avatar
    stevestoy Posts: 3, Reputation: 1
    New Member
     
    #3

    May 9, 2013, 08:51 AM
    Installing a 7 ft. square spa with 220v motor and heater. Label on spa connecting box is stating 50A service.
    Dr_Spa's Avatar
    Dr_Spa Posts: 101, Reputation: 13
    Junior Member
     
    #4

    May 10, 2013, 06:31 AM
    Romex? Code for wiring pools and spas requires that the supply circuit includes a ground wire that's insulated and of equal size to the other wires. Romex does not meet this requirement.
    stevestoy's Avatar
    stevestoy Posts: 3, Reputation: 1
    New Member
     
    #5

    May 10, 2013, 08:47 AM
    Wow, OK, thanks. I'll check codes and a local supply house for what's needed. Thanks again.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What is the amp rating for a 75' run of 10-3 romex wire [ 15 Answers ]

What is the amp rating for a 75' run of 10-3 romex wire?

Romex wire/amp issue [ 3 Answers ]

I am replacing a 30" kitchen range with a new 48". The existing wiring is approximately 30' of romex NM-B 8/3 on a 40 amp breaker. The new range requires as follows: Maximum connected load: 10.2 kW for 48". Required power supply: 240V/208V/50A/60Hz for 48". Minimum supply wire size: L1 and...

Romex 12-2 temp rating? [ 2 Answers ]

Hello. My first visit to this very informative site. I have a question about wiring in a pole building. I'm using 12-2 Romex simpull on a 20 amp outlet circuit along the walls. My question is, will heat in the summer months on the metal siding be hot enough to damage the wire if it is stapled on...

SEU & Romex [ 1 Answers ]

Can SEU and NMB cable be uses interchangely for a 60 amp, 240 volt circuit.


View more questions Search