    Need Technical Specs for Service Panel
    I need technical specs to prove that I am allowed to have tandem breakers in a QO6-12L100S Series G3 Square D service panel. Also need specs for the maximum number of circuits I can put in this panel.

    I asked about this panel before here:

    https://www.askmehelpdesk.com/electr...wed-51950.html

    TK said that the panel can support tandems and I have no doubt he is correct. However, the electrical inspector came out and he wants me to provide the technical specs to prove that tandem breakers are allowed. The inspector also wants proof that this service panel can support 6 circuits plus a 100-amp main.

    If someone could point me to where I can find the technical specs I would appreciate it.

    I've got the electrician installing retaining kits for the main breakers. Thanks, TK, for bringing that up.

    My electrician mentioned that a grounding bar was needed for this service panel. Is this true? Upstream of the service panels will be a Cutler Hammer 6 Gang Meter Pack.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 22, 2007, 03:09 AM
    Here are the specs found at www. Squared.com:

    Square D Online Catalog : Product Detail : QO612L100S

    Yes an equipment ground bar is now needed for each panel, if I remember correctly, all the main disconnects will be located in the meter pack, so these panels must have the neutrals insulated from the equipment grounds.

    I came back to add this after re-reading your post, why a 100 amp main in this panel? The main breakers are out in the meter pack?
    Ohio_Remodeler's Avatar
    Ohio_Remodeler Posts: 85, Reputation: 1
    Junior Member
     
    #3

    Mar 22, 2007, 06:38 AM
    Is there a way to have one main disconnect in the meter pack that covers the entire building - instead of having 6 breakers in the meter pack?

    Then each service panel could have it's own main. The reason I ask is because it will cost an additional $720 to get a 200 amp breaker and 5 100-amp breakers for the meter pack and all the main breakers in the service panel are already there.

    If this is not an option, I'll have the electrician remove the mains in the service panels and install breakers in the meter pack.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Mar 22, 2007, 11:27 AM
    Sure you can have one main before all the meters and have a breaker in each panel, ONLY if the lines from each meter to each panel does not run to long inside usually no more than 10 feet of cable is allowed.
    Ohio_Remodeler's Avatar
    Ohio_Remodeler Posts: 85, Reputation: 1
    Junior Member
     
    #5

    Mar 25, 2007, 08:44 AM
    Is there a main disconnect in the meter pack? Or is a separate box installed before the meter pack? I am envisioning a setup like the one pictured.

    I got this picture out of Illustrated NEC 2005, and in the caution box next to the picture it states, "On long runs it may be necessary to increase the feeder conductors' size to compensate for voltage drop 215.2(A)(3). I couldn't find anything stating the feeder conductor could only be 10' long. I'm estimating the run on this building will be somewhere between 15'-30' from meter pack to service panel.

    Do you have the code that says the run can only be 10' from the meter pack to the service panel? And is there any exception to it I can take advantage of without relocating the service panels?

    Thanks for all the help, very informative as always.
    Ohio_Remodeler's Avatar
    Ohio_Remodeler Posts: 85, Reputation: 1
    Junior Member
     
    #6

    Mar 25, 2007, 08:47 AM
    Forgot the picture.
    Attached Images
     
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    Mar 25, 2007, 02:04 PM
    There is no written 10 foot rule, NEC wants the main disconnect for each unit immediately as the feeder enters the building. You better check with local code and utility before you run unprotected feeders 15-30 feet.

    Voltage drop is not an issue here.
    nmwirez's Avatar
    nmwirez Posts: 453, Reputation: 20
    Full Member
     
    #8

    Mar 26, 2007, 04:16 PM
    Quote Originally Posted by Ohio_Remodeler
    I need technical specs to prove that I am allowed to have tandem breakers in a QO6-12L100S Series G3 Square D service panel. Also need specs for the maximum number of circuits I can put in this panel.

    I asked about this panel before here:

    https://www.askmehelpdesk.com/electr...wed-51950.html

    TK said that the panel can support tandems and I have no doubt he is correct. However, the electrical inspector came out and he wants me to provide the technical specs to prove that tandem breakers are allowed. The inspector also wants proof that this service panel can support 6 circuits plus a 100-amp main.

    If someone could point me to where I can find the technical specs I would appreciate it.

    I've got the electrician installing retaining kits for the main breakers. Thanks, TK, for bringing that up.

    My electrician mentioned that a grounding bar was needed for this service panel. Is this true? Upstream of the service panels will be a Cutler Hammer 6 Gang Meter Pack.
    A 6 Meter Pak still requires a 4 wire cabling to each "sub", that is why you need an EGC. (equipment ground conductor terminal bar bonded to the each enclosure.)
    nmwirez's Avatar
    nmwirez Posts: 453, Reputation: 20
    Full Member
     
    #9

    Mar 26, 2007, 04:25 PM
    Quote Originally Posted by Ohio_Remodeler
    Forgot the picture.
    Also note that a master disconnect is only needed if the AHJ requires it. Six handles (tennant disconnects) are allowed on one structure as NEC compliant.[230.2]
    Also note, the meter center needs one ground electrode conductor to at least two earthing ground electrodes.
    The sub panels only require bonding to each respective unit separate water pipes if existing.
    Nm
    nmwirez's Avatar
    nmwirez Posts: 453, Reputation: 20
    Full Member
     
    #10

    Mar 26, 2007, 04:42 PM
    Quote Originally Posted by Ohio_Remodeler
    I need technical specs to prove that I am allowed to have tandem breakers in a QO6-12L100S Series G3 Square D service panel. Also need specs for the maximum number of circuits I can put in this panel.

    However, the electrical inspector came out and he wants me to provide the technical specs to prove that tandem breakers are allowed. The inspector also wants proof that this service panel can support 6 circuits plus a 100-amp main.


    My electrician mentioned that a grounding bar was needed for this service panel. Is this true? Upstream of the service panels will be a Cutler Hammer 6 Gang Meter Pack.
    Each subpanel (with ground bar) can be an MLO if the Panel and breaker temp ratings qualifies for use of 'Twin or Tandem' breakers. Note the 6 Pak meter center tenant 100's qualify MLO sub-panels. Google Square D.com nm

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service Panel - Access [ 7 Answers ]

Is there any way to install finish trim around the basement service panel? I'm refinishing a basement bedroom with wallboard. Along one wall are two closets with that gray service panel between them. What kind of access to the service panel is required and does anyone have any suggestions for...

Wire at the service panel [ 1 Answers ]

I am installing a GEŽ 30" Free-Standing Electric Range(JBS55WK/CK/BK). It can use a 3 or 4-WIRE CONDUIT INSTALLATION plug from the range to the outlet. I have a double braker space available at the service panel. I have installed brakers into the panel for outlets and lights and then had them...

Main Service Panel needs [ 9 Answers ]

I ran across this site accidentally today and found someone who had many of the same issues I need help with. Most of my questions were answered reading the forum however I have one more, using the following information I am hoping someone can help. The existing house is apx. 2300 sq ft w/a 200...

Service panel in bathroom OK? [ 1 Answers ]

We are going to finish our basement and our electrical service panel in the corner of a room where we would like to build a new bathroom. Can we have the service panel in a closet in the new bathroom or would that be a hazard?


View more questions Search