    Heil Furnace flame burns inside burner
    Occasionally, when my furnace lights off the flame burns inside one of the burners instead of on top like the others. Is there a fix for this? I have tried to adjust the venturi but it doesn't help.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #2

    Feb 16, 2013, 04:56 PM
    Remove & clean the burner.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Feb 16, 2013, 04:57 PM
    Make sure gas pressure is adjusted to spec. on furnace tag or label.
    Clean burner orifice because a restriction will cause this problem.
    Post back with results.
    maggiesdad's Avatar
    maggiesdad Posts: 11, Reputation: 1
    New Member
     
    #4

    Feb 16, 2013, 05:51 PM
    Quote Originally Posted by hvac1000 View Post
    Make sure gas pressure is adjusted to spec. on furnace tag or label.
    Clean burner orifice because a restriction will cause this problem.
    Post back with results.
    I should have mentioned; I did have the furnace serviced. Burners were cleaned and gas pressure at the burner header was checked to be in spec. Service man did not clean orifices so I can try that.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Feb 16, 2013, 05:58 PM
    Quote Originally Posted by maggiesdad View Post
    I should have mentioned; I did have the furnace serviced. Burners were cleaned and gas pressure at the burner header was checked to be in spec. Service man did not clean orifices so I can try that.
    The orifice has a very small hole and if you use LP gas the hole is even smaller. DO NOT increase the hole size whatever you do. Use a bobby pin or hat pin or small wire and run it around the hole to make sure there is no obstruction. While you are at it you might as well do all the orifices.
    maggiesdad's Avatar
    maggiesdad Posts: 11, Reputation: 1
    New Member
     
    #6

    Feb 16, 2013, 07:24 PM
    Quote Originally Posted by hvac1000 View Post
    The orifice has a very small hole and if you use LP gas the hole is even smaller. DO NOT increase the hole size whatever you do. Use a bobby pin or hat pin or small wire and run it around the hole to make sure there is no obstruction. While you are at it you might as well do all the orifices.
    OK, Thanks. I'll give it a try and report back.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #7

    Feb 17, 2013, 09:02 AM
    For cleaning orifice, I use a piece of copper wire since it won't enlarge the hole & nearly all restrictions are soft or easily removed.
    maggiesdad's Avatar
    maggiesdad Posts: 11, Reputation: 1
    New Member
     
    #8

    Feb 17, 2013, 10:02 AM
    Quote Originally Posted by Grady White View Post
    For cleaning orifice, I use a piece of copper wire since it won't enlarge the hole & nearly all restrictions are soft or easily removed.
    Thanks Grady. I know how to fish; although, the last couple of years I'm not sure I know how to catch fish.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #9

    Feb 17, 2013, 07:11 PM
    I know what you mean. With the lack of fish in the bay, I haven't fished in 3 years. Want to buy a 25' Parker? ;)
    maggiesdad's Avatar
    maggiesdad Posts: 11, Reputation: 1
    New Member
     
    #10

    Feb 18, 2013, 05:06 PM
    Quote Originally Posted by Grady White View Post
    I know what you mean. With the lack of fish in the bay, I haven't fished in 3 years. Want to buy a 25' Parker? ;)
    I'm afraid your Parker wouldn't fit well in the strip mines I usually fish. Maybe in the Illinois River? I'm more of a bass fisherman. Good luck.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #11

    Feb 18, 2013, 08:04 PM
    Any luck with the burner?
    maggiesdad's Avatar
    maggiesdad Posts: 11, Reputation: 1
    New Member
     
    #12

    Feb 19, 2013, 07:25 AM
    Quote Originally Posted by Grady White View Post
    Any luck with the burner?
    Had a funeral to attend. Have left the cover off the furnace for two days and haven't heard any burning in the tubes. Got to believe it's related to air flow.
    maggiesdad's Avatar
    maggiesdad Posts: 11, Reputation: 1
    New Member
     
    #13

    Feb 22, 2013, 01:55 PM
    I finally had the chance to clean out the orrifices on my furnace. I didn't find anything in them but I haven't had any burning in the tubes since I cleaned them.

    Now all I have to do is replace my condensate trap that I split the threads on after cleaning it. Just some 2" PVC and a little time. Tried epoxy and it worked but I still feel a little seepage.

    Thanks for all your help.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #14

    Feb 22, 2013, 03:18 PM
    There was probably a spider web in the orifice. They are very hard to see. I had a hard time years ago believing that a spider could be so small to fit in that hole but it is true. Hopefully you got it fixed.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heil furnace vg 1905aer pilot burner location [ 0 Answers ]

Wher is the pilot burner located for a heil vg105aer

Heil furnace burner starts then shuts itself off [ 1 Answers ]

The burner ignites then it shuts itself off in like ten seconds

My heil gas furnace with electronic ignition won't get a flame [ 4 Answers ]

My Heil Furnace with electronic ignition will spark but the burners won't ignite. I have a 80% 2 stage furnace. It is only 3years old.

Heil furnace burner igintes then goes out [ 3 Answers ]

I have a Heil furnace model number NUGK075AG02 (75,000 btu's) and the burner ignites for about 15 seconds then goes out and the fan continues to run. What might be the problem? Deka

Heil furnace short cycling of burner [ 1 Answers ]

My 1983 heil model NUGK075DG01, natural gas, forced air furnace is running but only heats the house to 67 degrees no matter how high I set the temp, the fan continuously runs (in auto on thermostat) and the burner will cycle for 3-4 min. then shut-off for 10 min.. I have powered down and back-on,...


View more questions Search