    Basements/ejector pumps/washers
    A twist on a familiar question posted here... I am attempting to move my washer/dryer into my basement. It is rough plumbed for a bath, with a 4 inch waste line dumping into a sewage ejector pit. Can I cut a tee into that 4 inch waste line and route my 2 inch washer drain line into it? I am guessing I will have a P trap in the wall, with the washer drain line emptying into that which will flow into the 4 inch line. The 4 inch waste line shares a vent with the bathroom lines -- am I overloading that vent? Can I vent the pipe that my washer drains into somewhere after the P trap but before it tees into the 4 inch waste line?

    Additionally -- does anyone have a recommendation for a "good" ejector pump to service a basement bathroom and washer for a family of five?

    Thank you very much for your help.

    Rich
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Jan 6, 2005, 10:38 AM
    Basements/ejector pumps/washers
    Hey Rich,

    If you're asking if you can discharge a major fixture, (your toilet) past a unvented minor one,(your washer) the answer is no.
    How many fixtures in your bathroom group? What does the vent take off from. I need more details about this basement bath room before I can be more specific. Let me know the entire layout. Especially about the vent configuration. I think you're going to be able to tie your washer in to the drainage system. Just not the way you describe. Cheers, Tom
    rstallard's Avatar
    rstallard Posts: 9, Reputation: 1
    New Member
     
    #3

    Jan 6, 2005, 11:07 AM
    Re: Basements/ejector pumps/washers
    OK, from memory... (I took pictures of the rough in before the slab was poured... ). I have a "classic" bathroom rough in (for Virginia). A 2 inch drain stubbed out of the concrete for a shower, a 2 inch vented drain against the wall (sink drain), both of those connect to my 4 inch toilet drain, which in turn runs into my ejector tub. The vent on the sink drain has a pipe protruding in the direction of my shower, so I assume that's the shower drain vent (?). Is that descriptive enough, or should I scan a pic tonight and post it tomorrow?

    Thanks again!
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    Jan 6, 2005, 11:31 AM
    : Basements/ejector pumps/washers
    Are the walls open? The floor has been poured, right? Does the lavatory vent extend through the roof? Where would you want the washer to set in relation to the lavatory? I think I need a photo of the roughin. Also some dimensions on where the fixtures will set. Exactly what fixtures do you have installed at the present time? Is the holding tank vented? I'll wait on the photos but I need more information before I can get specific. Cheers, Tom
    rstallard's Avatar
    rstallard Posts: 9, Reputation: 1
    New Member
     
    #5

    Jan 6, 2005, 01:29 PM
    I tried to draw it so we could continue... check out the attached jpeg -- it's a top view and side view of the situation. The basement in rough framed at the present, I have started to break out the concrete to move the shower drain (6 inches, of course). Let me know if this helps and you can visualize the situation -- I labeled the laundry room and bathroom, which are in different rooms.

    Rich
    Attached Images
     
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #6

    Jan 6, 2005, 03:16 PM
    Can you give me a side view of the laundry room? I am particularly interested in where the vent from the holding tank is placed. My thought would be to tee off the vent with a 2" "P" trap with a 36" raiser and pick up your washer with that. Since there's nothing above the vent it's a natural to tie to. Sound like a plan? Nice drawing! Cheers Tom
    rstallard's Avatar
    rstallard Posts: 9, Reputation: 1
    New Member
     
    #7

    Jan 7, 2005, 11:05 AM
    Interesting, I guess I'll call the city and see if that's OK. That would be wonderful if I can do that. Let me see if I got this straight... Add a P trap to the vent that services the sewage pit, and have at least 36" of vertical pipe above that P trap that my washer will dump into, and bob's your uncle? Now...did you imply the vent can not used for anything else? Try this pic on for size -- i added the P trap and a 36" pipe to the sewage vent... And, as the saying goes (and I mean it) -- if you're ever in Virginia, stop by for a hot chocolate and some cookies. Your help is very appreciated and I would look forward to helping in return.
    Attached Images
     
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #8

    Jan 7, 2005, 12:20 PM
    Bob's my uncle?? There should be no problem using the vent to discharge the washer into. Instead of discharging into the side of the tank through the 4" your discharging into the top through the vent. Same difference. BTW what size is the vent anyhow? Minimum size allowed for the washer discharge will be 1 1/2" . 2" is the normal size but my house has used a 1 1/2" trap and stand pipe for the washer discharge since the house was built 50 years ago. You asked. "Now...did you imply the vent can not used for anything else?"
    What else would you want to use it for? Regards, Tom
    rstallard's Avatar
    rstallard Posts: 9, Reputation: 1
    New Member
     
    #9

    Jan 11, 2005, 12:52 PM
    I just talked to our county inspector -- he says I can't use the pit's vent to drain my laundry into. He advocates using the washer's pump to get the output up into my joists and run it to my main sewer line. I have 9 feet celings in my basement... do washer have specs on their pump published? Thoughts on the county guy's thoughts?
    tommytman's Avatar
    tommytman Posts: 153, Reputation: 2
    Junior Member
     
    #10

    Jan 11, 2005, 07:44 PM
    I'm not sure if this will help but check

    http://www.saniflo.com/products/sanivite.html

    This thing can pump water 10 feet up but can olny accept water from a laundry basin... If it has to be vented you could tie it into your vent line... Good luck.
    rstallard's Avatar
    rstallard Posts: 9, Reputation: 1
    New Member
     
    #11

    Feb 4, 2005, 11:29 AM
    I DID IT! Here's the pic. The groundwork was approved. THANK YOU for your help!
    rstallard's Avatar
    rstallard Posts: 9, Reputation: 1
    New Member
     
    #12

    Feb 4, 2005, 11:36 AM
    I DID IT! Here's the picture. THANK YOU!
    Attached Images
     

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Why do some fish not need air pumps [ 14 Answers ]

My sister has a goldfish and it doesn't have an air pump in it, but my tank has to have one or all the guppies, tetra, whatever I buy or they will die. Why is that

Air Pumps for Goldfish [ 9 Answers ]

Odd, but I won 2 goldfish at the carnival 3 days ago. I went to Petsmart and bought a proper fish tank (2.5 gallons), bedding gravel, and plants for them. Since my father is the ultimate money saver, he insisted that we didn't need an air pump or filter. I saw the fish gulping for air on the...

Vac pumps [ 5 Answers ]

Just wondering how long do you leave the pump on the condencer? For 1.5 and 2 T I usually leave the pump on for about 20 to 30 min. Yesterday and today I installed 3 - 5 tonns and 3-4 tonnes at a new building . Tomorrow I'll vac them out for about 30 min each. If you don't mind me asking, what's...

Wood Basements [ 1 Answers ]

How do I stop the noise from my well pump where the plastic pipe enters through the wall ? It a vibrating noise

Pressure Washers [ 1 Answers ]

I am looking for assistance in determing what size pressure washer is needed for 'general' household use (i.e. cleaning siding, decks, sidewalks) Thanks


View more questions Search