    Hooking up a hot tub
    Hot tub 120 havc 20 amp what size wire and breaker do I need to hook it up
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Nov 20, 2011, 05:02 PM
    Is it going to be direct wire or will it have a plug with an integral GFCI?
    smokejumper's Avatar
    smokejumper Posts: 6, Reputation: 1
    New Member
     
    #3

    Nov 20, 2011, 05:26 PM
    I was going to hook it to a gfi breaker.. so it will be direct plug, but should I use a 20 amp breaker
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Nov 21, 2011, 02:21 PM
    Since you no doubt have a motor in the pump, you need, by code, to rerate the load at 125%. Therefore, your load is 25Amps. I would use a #10 Cu wire and a 30Amp breaker.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Nov 22, 2011, 03:49 AM
    What do the instructions require for electric service?
    Dr_Spa's Avatar
    Dr_Spa Posts: 101, Reputation: 13
    Junior Member
     
    #6

    Nov 29, 2011, 09:59 AM
    Spas are typically rated by the size of the circuit they require. As such, you needs a 20a GFCI and 12 gauge wire.

    MA0641 is correct about the 125% rule, HOWEVER, your pump motor probably is rated at a MAXIMUM of 12 amps (and more likely 8 to 10 amps). As such, a 30a circuit isn't necessary (125% of 12a is only 15 amps).
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #7

    Nov 29, 2011, 02:10 PM
    Unfortunately, he never answered as to what the plate says. I interpreted "hot tub 120 havc 20 amp" to mean it was rated at 20 Amps. Why ask what size breaker if he has a 20? It could also have a heater.
    Dr_Spa's Avatar
    Dr_Spa Posts: 101, Reputation: 13
    Junior Member
     
    #8

    Nov 29, 2011, 02:42 PM
    It almost certainly does have a heater... but the way these things are designed, only the low speed of the pump (generally around 2 to 3 amps) runs when it's heating. When you turn on the high speed of the pump, the heater shuts off... The is the industry standard for how they operate.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Advice for hooking up a hot tub on a 100amp subpanel, 200amp service. [ 4 Answers ]

Hi- Hopefully I explain my situation well enough. I recently bought a inexpensive used hot tub to help with my always increasing 40 yr old pain. Lol. The hot tub is a Hydro Spa by all of my Google research, 5-6 seater, 220v, but I do not know a model number or style name, and it cannot be found...

I am hooking up a Hot tub with a max fuse size of 50 amps. [ 3 Answers ]

I am hooking up a hot tub rated for a 50 amps max fuse size. I already have the #8 thhn and 1/2 liquid tight flex conduit. Will the #8 wire be enough for 50 amps.

Hooking Up a Hot Tub [ 11 Answers ]

All right, I'd like to thank you guys ahead of time for the help. As you can tell from the title, I'm trying to figure out a way to hook up our new hot tub (this tub can be either 110 or 220, 220 will obviously be more powerful). I don't have any room left on the service so I was going to hook...

Hooking up hot-tub.why would there be no ground? [ 11 Answers ]

Hello, I was recently given a dimension one hot tub from a friend, and have started wiring it up. When I disconnected it from his house, the electric job seemed very nice. There was 8 gauge THHN going to the disconnect/GFCI box, and 6 gauge from there to the main panel. What was weird,...


View more questions Search