    York 80 furnace intermittent loss of burners
    Service tech replaced rollout switch, broke the bracket while doing it, and cleaned flame sensor. Charged $300, told me to replace thermostat, and problem still persists. They want another $100 for "call out."
    Here is what happened today when I observed its' operation; ( I cleaned the flame sensor, as many on this site suggested)
    Blower shuts off. After 30 secs, Igniter comes on, gas valve clicks, burners light up. 15 secs later blower comes on. Furnace runs for 14 minutes. Burners and blower stop, inducer keeps running.
    1 min later, igniter comes on, gas valve clicks but no re-light.
    2 min later,(repeats) igniter on, gas valve clicks, no fire. Blower runs, cold. LED flashes #1, lockout.
    Cycle power off, repower in 30 secs.Furnace goes through re-light cycle, 1 min later blower starts and furnace runs normally; for only 8 minutes. Fire goes out, blower and inducer remain running.
    1 min later, igniter comes on, gas valve clicks, but no burners light.. 30 secs later blower shuts off.
    1 min later, igniter on, gas valve clicks, no fire.
    2 minutes later, igniter on, gas valve clicks, burners light, 30 secs later blower runs.
    Furnace runs for 4 minutes, then shuts off, 3 degrees below set point temp.
    5 minutes later, blower and inducer start, led flashes code 1 lockout.
    Cycle power and furnace relights as it should and contiinues running for over 30 minutes, shutting off at the set point temp. blower and inducer run on for a minute, then shut off too.
    I could sure use some help with this, I have had three different techs, from two local York dealers, charge me a bundle of dough but they cannot diagnose it either. I have some diagnostic skills, mostly with big diesel engines, transmissions.
    Thank you
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    May 20, 2011, 03:41 AM

    If I were you, I would protest the charges you have already paid since you have not received satisfactory results.
    twinlakes01's Avatar
    twinlakes01 Posts: 4, Reputation: 1
    New Member
     
    #3

    May 22, 2011, 12:02 PM
    Quote Originally Posted by KC13 View Post
    If I were you, I would protest the charges you have already paid since you have not received satisfactory results.
    This is the fourth "factory trained, dealer tech' I have had work on this darned thing. Same result every time. Runs OK for a week or so, then back to square one. How York qualifies its dealers is a mystery to me.

    I cleaned out the inducer housing. Checked the vacuum, ewith a manometer. It holds about 1.5 in H2O constant. The pressure switch activates and completes the circuit.

    When it is operating I have 24V at the limit switch, so it is closed, as it should be. It maintains 24V at the yellow lead to the gas valve.
    Also have 24V at the rollout switch.

    The flame sensor has 1.3 M ohms resistance, and provides 0.000,007 Amps vs a specification of 0.001 Amp. If I disconnect the sensor, the unit runs through the pre start sequence, fires up, then shuts off after 5 seconds; which seems about right. So it seems like it is reading the flame presence, but maybe loww on ampereage?

    This morning it was blowing cold again. I cycled the power and it lit up after the second attempt.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

York Furnace: Only one of four burners light [ 1 Answers ]

York (Model: P4HUA1ZN06401B) vertical natural gas furnace. Observed that the burner on right, by the glowing starter, starts properly but the other three burners do not light and since the thermocouple on the left does not start, the gas is stopped in about 5 tyo 10 seconds. I cleaned all four...

I have a Rheem Corsair 90%, burners intermittent, replaced about everything... [ 0 Answers ]

5 yr old corsair 90%er burners flash on, then burp, and run then burp, then kicks out and goes to lock out... I've replaced about everything... control panel, pressure switches, gas valve (twice), heat sensor rod, hot wired around thermastat...

York diamond 80 furnace last two burners won't light [ 1 Answers ]

I have a York Diamond 80 furnace. The first two burners light up but the others won't. After about 4-5 seconds the burners turn off but the fan is till running and blowing out cool air.. What do I need to do other than calling someone.. Please help.. Thanks

York burners won't ignite mod P3HU 9 yrs. Old [ 3 Answers ]

When t-stat calls for heat the combustion blower starts, the glow plug glows but gas valve doesn't open and burn doesn't ignite. The combustion blower continues to run. Is this a problem with the pressure switch? Does it need to be replaced? :confused:

Intermittent loss of Hot Water [ 1 Answers ]

I have a water heater problem. It's a standard gas water heater, Rheem. The water in the moring was not as hot as normal, like the water heater stopped working overnight. I checked and the pilot light was out. I relit the pilot and the burner fired up and was working fine. The next morning the...


View more questions Search