    Honeywell Thermostat Furnace heat not on
    Hi,
    We installed a new Honeywell Deluxe 5-2 Programmable Thermostat (RTH6300B) last week. We have a Carrier Furnace that is 15 years old, I believe.

    We've noticed that the temperature of our house doesn't seem to be reaching the temperature it's set for but have been so busy and out so much that we haven't had time to look into it.

    It is set to be at 17 degrees Celsius during the night and then to go to 21 degrees at 6:30 AM. At 9:30 this morning, we noticed the temperature in our house was 16 degrees. When we turned up the manual temperature, the furnace heat did not come on. We're starting to wonder if the electric baseboard heat in our addition is the only thing heating the whole house.

    We installed the thermostat ourselves. The previous thermostat was probably original to the house (built in the 50s). There are only two wires: for heat and for the fan. They are called G and W. The G is white and the heat is black. We think fan is G and W is heat. We have the G attached to G and W attached to W. We even tried switching them around this morning but it didn't make a difference.

    It's cold in Manitoba in January so I'm hoping we can get some advice! If we have to call a furnace installer, the $100 service call will make our new thermostat much more costly than we'd planned.

    Thanks,
    Pam
    Peter Kwan's Avatar
    Peter Kwan Posts: 26, Reputation: 1
    New Member
     
    #2

    Jan 3, 2007, 12:07 PM
    I think your old thermostat act just like a switch, when the temperature in the house fall below the setting, it will turn on to give a short circuit, and will turn off (disconnect) when the temperature is above the set point.

    To test your system, if you have a volt meter, if you measure the voltage across the two wires, you should have 24-27 VAC. If that is the case, shorting the 2 wire, your furnace should turn on.

    If the above test is correct, to solve your problem, one of your wire should connect to R terminal and the other to W terminal on your thermostat.

    Let me know if this help.
    PamG's Avatar
    PamG Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 3, 2007, 12:14 PM
    Thanks Peter,

    My husband solved the problem by tracing the wires from the thermostat back into the furnace and finding where they were connected. It turns out the white was connected to W and the black was connected to R. I think the main confusion about the whole situation was the fact that when disconnecting the original thermostat, the white was connected to a screw labelled G.

    Everything seems to be working fine now.

    Cheers.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring a furnace thermostat to manually operate the furnace fan [ 2 Answers ]

I have two wires connected to my furnace thermostat. There is a place labeled G on the thermostat. Can I simply run a wire from the G terminal on my thermostat to the terminal labeled G on my furnace fan relay to operate the fan separately?

NO HEAT! Janitrol heat pump and AC system. Changing to Lux Thermostat. Wiring issue. [ 11 Answers ]

I have a Janitrol A/C and heat pump system. I replaced the thermostat with a Lux T9000LC The A/C works fine, but the heater does not. I have it wired as follows: G - Green Y - Yellow W - White RH - Pink B -

Honeywell RTH 7400 Thermostat wiring for Heat Pump (Rheem) [ 2 Answers ]

I am trying to hook up a Honeywell RTH 7400 Tstat to the existing Rheem HVAC in my house. Currently using Rheem thermostat that came with the house (non-programmeable, using mercury tubes). Heating is provided by a heat pump as well as Natural gas furnace for aux heating (besides the air...

Honeywell - Heat OK, A/C not [ 1 Answers ]

Hello all, I replaced my original digital thermostat with a Honeywell CT3200 programmable thermostat today. The heat settings work great and the unit turns on and off when it should; but when testing the air conditioning no luck. The thermostat says the system is on when cooling but the...

Honeywell thermostat heat/cool in Rheem 2 stage furnace? [ 1 Answers ]

I have a Honeywell 1 Heat/1Cool thermostat (TH6110D1013) that I would like to use with a Rheem 2 stage gas heat furnace. I think it is possible but would I get the same benefits as having a thermostat with 2 heat/1 cool? Would I just connect the W terminal on the Thermostat to the W2 on the...


View more questions Search