    What size wire do I need for a 60 amp breaker running 50' to power a plasma cutter?
    I am running a cable wire with no conduit 50 feet from the panel box. I have heard some say 6 gauge is OK where I want to buy the cable they are telling me 4 gauge.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 23, 2010, 06:18 PM
    Need #4 copper if a cable, such as Romex ,or SE.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Oct 23, 2010, 07:05 PM

    Just curious, TK is rarely incorrect on things, so I am wondering about the thinking behind #4cu.

    #6cu in NM or SE cable must use the 60 deg C column in 310.16.
    In this column #6 is rated for 55A. Since there is no 55A breaker we can round up to 60A.
    Unless the actual full load is 56-60A I would say #6cu is fine.
    creahands's Avatar
    creahands Posts: 2,854, Reputation: 195
    Ultra Member
     
    #4

    Oct 23, 2010, 09:16 PM

    If manufacturer is recommending a 60 amp breaker, I would assume unit takes more then 50 amps to start and run.

    I am not an electrician, but agree with TK. Use #4 copper.

    Chuck
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Oct 24, 2010, 05:12 AM
    Sorry. I hit the agree button instead of the quote button. No big deal.


    Quote Originally Posted by creahands View Post
    If manufacturer is recommending a 60 amp breaker, I would assume unit takes more then 50 amps to start and run.

    I am not an electrician, but agree with TK. Use #4 copper.

    Chuck
    This is fine, but what do you base it on?
    Even if it takes 90A to start, this is figured into the equation. Like I said, if the running amps are under 56 than #6 will be fine. At only 50' the distance is not at a consideration.

    Knowing that TK certainly knows what he is talking about I was just curious as to why he suggests #4.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What size wire and what breaker for a 100 amp sub panel 275 ft [ 2 Answers ]

"I have a 200 amp panel in my house with 7 avalible slots. I want to run from it to a 100 amp sub panel 275 ft away. What size wire and what size breakers should I run to the sub panel? Then from the panel I was going to run in the barn 3 shop lights and 4 plugs. Then go about 75 ft to a pavilion...

Wire size for 80 amp breaker [ 1 Answers ]

I am installing a 80 amp sub panel and need to know the size of the wire from the main to sub

Wire size wire & circuit breaker do I need for a 15.8 range [ 2 Answers ]

What size circuit breaker & wire size do I need rfor a 15.8 raqnge ?

100 amp breaker wire size [ 5 Answers ]

Will #2 aluminum wire fit a 100 amp cutler - hammer circuit breaker

Wire size in a 100 amp breaker [ 1 Answers ]

I was wondering if a 2/0 wire will fit in a siemens 100 breaker? Thanks for your help


View more questions Search