    What is causing my condenser to have ice
    My carrier AC condenser is not cooling and has ice on the compressor and line. What is causing this?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    May 6, 2010, 09:11 PM

    Low on freon, cloged filter, or problem with indoor blower
    gilbertbjr's Avatar
    gilbertbjr Posts: 6, Reputation: 1
    New Member
     
    #3

    May 7, 2010, 06:03 PM

    Thanks for the info.

    I've replaced the air return filters, can you tell me if there are other filters and their locations. Is it between the air handler and evaporator? Or in the copper line somewhere? I really don't know, any help is appreciated.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #4

    May 7, 2010, 06:05 PM

    If you have changed your return air filters then then next thing is probably a freon leak. Are you air filters in the duct work at the airhandler or in filter grills upstairs?
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #5

    May 8, 2010, 11:09 AM

    Change the filter,shut the system down and allow pleanty of time to thaw. Start it back up, be sure the indoor blower is running. If it starts freezing again, it's time to place a service call, it may be low on refrigerant.
    gilbertbjr's Avatar
    gilbertbjr Posts: 6, Reputation: 1
    New Member
     
    #6

    May 10, 2010, 11:01 AM

    Thanks Joshdta and hvaservicetech_07, I'll get a tech to check the freon.

    I appreciate the help.
    gilbertbjr's Avatar
    gilbertbjr Posts: 6, Reputation: 1
    New Member
     
    #7

    Jun 30, 2010, 08:59 AM

    I checked the evaporator coil and both sides are clean it looks new.

    I hooked up the gauges and I got the following:

    Blue/low line = 80 PSI
    Red/high line = 175 PSI

    There are not high or low pressure switches outside on the condenser unit

    I checked the blower in the attic and its working okay

    The air filters in the returns are new and there are not filters in the attic blower system

    Last the condenser's compressor is cycling on and off approx. every 7 - 10 minutes.

    I'm guessing that it's low on freon?

    Any ideas?
    gilbertbjr's Avatar
    gilbertbjr Posts: 6, Reputation: 1
    New Member
     
    #8

    Jun 30, 2010, 09:05 AM
    What is causing my AC system's high line
    What is causing my AC system's high line "small copper line" to be low it's 175 PSI, and the condenser and lines had ice?

    The original problem was that the condenser and lines were iced over and the system wasn't cooling.

    I've replaced the condensor's capacitor and contactor.

    I checked the evaporator coil and both sides are clean it looks new.

    I hooked up the gauges and I got the following:

    Blue/low line = 80 PSI
    Red/high line = 175 PSI

    There are no high or low pressure switches outside on the condenser unit

    I checked the blower in the attic and its working okay

    The air filters in the returns are new and there are no filters in the attic blower system

    Last the condenser's compressor is cycling on and off approx. every 7 - 10 minutes.

    I'm guessing that it's low on freon?

    Any ideas?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #9

    Jun 30, 2010, 06:34 PM

    Is this a 410 unit? Puron? If so the blue in should have been about 130 to 145
    gilbertbjr's Avatar
    gilbertbjr Posts: 6, Reputation: 1
    New Member
     
    #10

    Jul 8, 2010, 06:24 AM
    Comment on Joshdta's post
    No it's a R22 unit, and sorry for the late response

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Ice maker not making cubes my ge profile ice cube maker has stopped making ice [ 1 Answers ]

Ice maker not making cubes my ge profile ice cube maker has stopped making ice

Sub zero ice maker continues to make ice now ice drawer is stuck [ 0 Answers ]

The ice maker in my sub zero model 561 has continued to make ice even though the switch has been turned off. Now the ice drawer is jammed and the ice maker is jammed with ice cubes stuck together. How can I open the drawer and what can I do to fix this issue?

Ice dispenser door is not shutting good and causing frost [ 2 Answers ]

How do I get the door to stay closed securely? I have a kenmore side by side, with the ice maker and dispenser in the door. Frost is building up around the opening of the ice maker. I cleaned all this ice off and the door is still not shutting.

Scotsman Ice maker Model # CSE60, not giving solid ice cubes [ 2 Answers ]

Our Scotsman Model # CSE60, has stopped giving solid ice cubes, and it is now sporadically giving shelled ice.:confused: Any suggestions on how to correct this problem? :D We have tried all of the owners manual suggestions, such as cleaning and preventative techniques. :p Thanks Onisno60

Replacing A/C - condenser or heat pump/condenser [ 1 Answers ]

I live in a condo. All of the units in the building need to new air conditioners because they are all old and will not survive a scheduled reroofing of the building. The association got a bid for a company that will put in a new condenser unit for anyone who wants one - it is about $1500 installed....


View more questions Search