    Changing from metered service on my shop to service from my house.
    I’ve had the meter and 3 wire service cable removed from my shop. I’ve purchased 90 feet of 100 amp direct burial cable to run from the lower section of my home meter to my shop. Not being an electrician, I’m still trying to install this changeover. The direct burial cable has 4 wires. 2 larger black wires, 1 larger black with white striping, and 1 smaller green wire. My assumption is that the 2 larger black wires connect to the connections going into the breaker panel. Now my problem arises. Where do the other 2 wires connect? Now to my 2nd problem. I know the 2 black wires connect to the lower side of my home meter. There are only 3 wires going to the top side of my home meter. Where do the black wire with stripe connect and where does the green wire connect? Both my home and my shop have ground rods driven into the ground. I hope I haven’t confused anyone as much as I am confused. Thanks for your help. Eddie6789
    Fr_Chuck's Avatar
    Fr_Chuck Posts: 81,301, Reputation: 7692
    Expert
     
    #2

    Dec 1, 2006, 06:48 PM
    1. This could and should not be done without a building permit and inspected by the building inspector

    2. If you don't know what you are doing, don't do it, you will end up burning your house or shop or both down

    3. If the other service was for a business, and you were deducting the electric as a business expense, when it is hooked to your home, it would no longer be deductable,
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Dec 2, 2006, 06:39 AM
    The four wire direct burial cable you have should be called URD, or Underground Residential Distribution cable. The two black wires, note one may have a red tracer to be able to tell the difference between both, are the hot wires, the large wire with a white tracer is the neutral, these three should be all #2 or larger for 100 amp.

    The green wire is the equipment ground, and is the most important wire.

    At the house panel the two hots will connect to a 2 pole 100 amp breaker to feed the shop. Now, if the house panel has the Main Breaker in that panel, both the Neutral and the green will connect to the Main Neutral bar in the Main Panel.

    If the Main Panel does not have a Main Breaker in it, then the Neutral connects to the Main Neutral, and the green wire will connect to a separate equipment ground bar that should be in the Main Panel.

    At the shop, connect the hots to the shop panel Main Breaker or lugs.

    Here is where it will get tricky, so pay attention.

    The Neutral wire of the URD cable will connect to the Main Neutral bar.

    If the shop panel had a Main Breaker in it, look closely at the Main Neutral bar for a jumper or a green screw that connects the neutral bar to the metal can of the panel, find this and REMOVE the jumper and/or screw. THIS MUST BE DONE to isolate the Neutral from the metal panel box AND the equipment grounding. Purchase and install an equipment ground bar, mount directly to the metal panel box with machine screws, no sheetmetal screws allowed.

    The green wire of the URD cable will now connect to this new equipment bar.

    Disconnect any wire connected to the Neutral bar that goes out to any ground rod or water line. Move any bare or green wires FROM the main Neutral bar and connect to the new equipment bar.

    If the shop panel did not have a Main Breaker in it, then this separation of Neutral and equipment grounds should already been done for you.

    The newly connected shop panel is now a subpanel and the Neutrals and grounds MUST BE separated.

    If your home is a single family dwelling, then you may be allowed to do your own electrical work, providing you obtain an electrical permit from your local Code Enforcement or Building office.

    And have all your work inspected, including having the direct buried cable inspected BEFORE the cable is covered.

    There are specific details on how to bury cable also, depending on your local codes, soil conditions, type of cable, and if installed in conduit.

    What Fr Chuck is trying to tell you if you don't have the installation permitted and inspected, and if your electrical work causes any loss of life or property, your insurance carrier will not cover any losses, and you may be criminally responsible for any injury or loss of life.

    Consult with your accountant on the tax issue.

    I am not confused at all. Any confusion on your part can be disastrous.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Over service of Alcohol [ 4 Answers ]

I know that a bartender and the premises is liable for service of an alcoholic beverage to an obviously intoxicated person. (Califonia) But what about if a bartender serves someone 10 shots of tequila and 5 beers in the time span of 1 hour. And, duing that hour, the patron did not show symptoms...

Community Service [ 3 Answers ]

This may sound stupid and all but, a few months ago I came across a dog that was being badly abused and starved... so I notified the animal cops. It has been a few months now and the dog is still left to die, they did nothing about it. Well... I now find myself wanting to do something, like...

Best dsl service [ 2 Answers ]

I presently have Direct TV DSL. They are ceasing operations soon and I need to decide on another service. I would like to go with another DSL service, if possilbel, but I would consider going with a cable-broadband system. I am in the Atlanta area. My questions are how good is Bellsouth DSL. ...

Service entrance [ 5 Answers ]

Can someone tell me how to find out what the amp rating of a service to a house is . The fuse box is old with edison base fuses, but the weather head and pipe to the meter cradel looks newer want to change to beaker panel Not sure what size

Xp service pack2 [ 1 Answers ]

I have now down loaded sp2 shoud I use the sp2 firewall and virus protection or disable it and continue to use Norton internet secruity which is up and ruuning ? Only all this I find a bit confusing


View more questions Search