    Old Carrier electric heat relay
    I'm a hvac certified tech and am working on Carrier 40gc900220, around 30 to 40 years old, been told even the model number is obsolete. My top 5 kilowatt heat strip is getting no power but has continuity and 14 omhs resistance. My bottom strip has power and has a loop the goes up and connects to the top burner on the right side. The left terminal on the top burner connects to the NO side of a relay switch. The relay switch is a spst . When I test this relay when there is a call for heat, I get 24 volts across the contacts. Doesn't that mean that the switch is bad and won't let current pass through? Or just that when it's energized that it opens to allow NO to close? Also, the NO open contacts are 240 volts for heat strip and second relay, when I test across these terminals on a call for heat there is no power, doesn't this mean the switch is open and functioning properly? Also there is a control switch of some sort that feeds the 2 switch relays... is has a post marked COM and one marked NO and 2 marked HEATER. They are not inline, parallel, etc. Would you test this switch for continuity with one lead on COM and one on NO, or one on COM and one to the heater leads in turn? Another words, which is the load and which is the switch?
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #2

    Nov 21, 2006, 08:48 PM
    To many questions, I lost track. So the #1 heat bank tests good on continuity and has not got 240 V across it? This relay uses 24 V to switch a 24 V circuit for heat? Can you hear the relay close? Do you get continuity across it with 1 wire removed and it is energized?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Nov 22, 2006, 04:21 AM
    Have an expert in HVAC rewire the unit to use a Sequencer. Just did one the other day. Any HVAC tech that has been around can do that for you an eliminate the old Carrier relays.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electric Heat-Pump-No heat [ 2 Answers ]

I had a wall-mounted unit installed in a room in may of this summer. In the middle of the night the heat shut off and has not come back on since. It is an Amana, electric heat with heat pump unit. The cooling works, the heating setting does not blow air at all. When I remove the cover it says...

Changing from gas heat to electric heat [ 3 Answers ]

How do you change from Apollo gas heating system to electric heating system?

No heat, blower runs constantly, carrier gas furnace [ 7 Answers ]

This am we I got up the blower on my carrier series 100 gas furnace (approx 10 years old)was running and blowing out cold air. Even with the thermostat turned to off the blower runs constantly. The only way to stop the blower from running is to turn the switch on the side of the furnace to off or...

Electric heat [ 6 Answers ]

I recently moved to a home with electric heat. I am not familiar with it. Is the air from the registers suppose to be more cool than warm, it is not cold but cool Debbi

Carrier split - heat burners cycle on and off [ 7 Answers ]

Carrier split unit in heat mode appears to basically operate OK. Once the pilot is lit and the burners come on, the pilot remains lit but the burners will intermittently cycle on and off. This appears to sometimes delay the blower from turning on. Once the blower turns on, it heats to the set temp...


View more questions Search