    Beckett burner starts has flame for about 15 seconds off for 12 then flame on & runs
    I have replaced the following with the problem still happening: replaced the primary control(R8184G 4009), cad cell--the oil unit was service at the beginning of the heating season. Ran like a champ.

    Now for the past two weeks with new parts the problem is: Oil burner starts with a flame for about 15 seconds, then flame out for about 12 seconds---then unit flames on until heat temp is reached. Happens exactly the same all the time with new parts. I have a two pipe system, oil lines have flare fittings---everything is tight. I checked the filter still like new from the service. I also primed the oil pump--even though I have a two pipe system. Why is this happening. Now when there is the 12 second no flame and when it comes back on it is a normal ignition --no roar or big explosion just a normal ignition. I have a Beckett AFG unit, Weil-McLain Gold, Honeywell Primary Control/cad cell, High Limit, Suntec two stage oil pump (3450 RPMs), and an Emerson motor that matches.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Feb 1, 2010, 05:12 PM
    Do you have an electric oil valve installed as shown on the below link drawings? The problem has to be in oil delivery since if it was ignition you would hear about it like in Boom. LOL

    http://customer.honeywell.com/techli...it/69-0618.pdf
    john102653's Avatar
    john102653 Posts: 5, Reputation: 1
    New Member
     
    #3

    Feb 1, 2010, 07:18 PM

    No electric oil valve
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Feb 1, 2010, 07:31 PM
    It has to be fuel delivery but why the perfect timing I have no idea. The 15 second/12 second thing is very strange. What kind of tank do you have/ Above or below ground? Have you checked the vent on the tank or any anti spill device in the vent?
    john102653's Avatar
    john102653 Posts: 5, Reputation: 1
    New Member
     
    #5

    Feb 2, 2010, 01:48 AM

    Tank is in the ground (1000 gallon tank), vent is unobstructed and clear--I measured the oil and I have 510 gallons in the tank. There is no leaking ---I monitor the oil burned by measuring and from Dec 9 to Jan 11(in which the burner was fine) ---from Jan 11 to Feb 01 >>burning about the same amount of oil.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Feb 2, 2010, 04:46 AM
    If it is an in ground tank then it is drawing from the top so the old floating object at the bottom of the tank deal is not involved.

    My last thought on this is the oil pump and king coupling. I am sure when you set up the burner you tested and set the oil pressure properly just as any service person would do but to confirm the issue put your gauge back on the units oil pump and fire it over. Watch the gauge as it runs and see where the pressure goes during the 12 seconds of flame out. This will confirm at least that the pump is good but it could also tell of a possible bad check valve in the pump or a slipping kin coupling.

    Many years ago there was a delay style coupling that would wind up before exerting pressure on the pump to produce oil. Those items caused much trouble when they got old and really produced some strange effects. The possibility of you having one of those left on your burner is slim to none but I just thought I would mention that fact.

    Post back with your oil system operating pressure during normal running and also during flame failure.
    john102653's Avatar
    john102653 Posts: 5, Reputation: 1
    New Member
     
    #7

    Feb 2, 2010, 07:02 AM

    I am at work---will check later -- the entire system was installed new in 1997. Suntec two stage pump(model B2VA-8216) 3 GPH (100 - 150 psi, R.H. Rotation, #2 Fuel). Pressure was fine at the beginniung of the heating season but things due happen. Will get back to you... thanks.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Feb 2, 2010, 07:58 AM
    Ok

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Beckett model AFG burner flame-out [ 14 Answers ]

This season is the first time ever that this has happened. The furnace starts, gets a flame, runs for a while, then it flames-out. It sounds like the oil pump is still running (I hear like a spraying sound). Nothing shuts off. Then the flame will come on again, but may continue flaming-out...

Flame comes on for only 9 seconds then turns off. [ 3 Answers ]

I have a Bryant 376CAV model. The heater will try to come on, it lights for about 9 seconds then goes out. The fans will then run for 90 secs and will shut down. After a while it may do this for a few times and then it will stay off until I turn off the breaker and turn it back on.

The flame on the water heater only burns for a few seconds and then shuts down. [ 0 Answers ]

I am not currently getting any hot water out of my water heater. The flame comes on and burns for a few seconds and then shuts off. This same patterns then continues to repeat.

Beckett AFG model Oil Boiler NO FLAME [ 3 Answers ]

I have no contract for yearly cleaning I have changed the filters and oil strainers, I am getting oil in the line, but NO Flame. Is it possible to cean the ignition nozzle? Can anyone recommend a fix to this problem... Snow is in the forcast. Please help.

Soon as fan starts up the flame goes out [ 8 Answers ]

When I start my furnace the flame starts and than the fan will come on and the flame will go out and it will continue doing this until I shut it off. And some times the fan will be stuck on until I shut it off directly from the power switch, also there is a blinking red light on the furnace . Any...


View more questions Search