    Pulling wire through conduit
    I currently have 100' of 10/2 UF cable running underground through 3/4" PVC conduit. I need to pull the 10/2 out, and pull in 10/3 UF (or its code equivalent) to replace it. I have 3 questions: 1) Is 10/3 UF cable always produced in a flat configuration, or does some company manufacture a round 10/3 UF option? 2) Does NY code require UF if the wire is running inside of conduit? 3) If not, what would be the best alternative to 10/3 for pulling thru 100' of 3/4" conduit? Thanks!
    omzig's Avatar
    omzig Posts: 119, Reputation: 19
    Junior Member
     
    #2

    Nov 11, 2006, 11:13 PM
    I don't know what the specifics are in NY, but I don't know why you would want to run UF in conduit.

    I usually bury PVC (sched 80) with individual THWN wire. I have always heard that even if it's in conduit, if it's buried it's still considered a wet location. THWN is suitable for wet locations (whereas THHN is only for damp). Actually most of the wire I buy these days is marked THHN/THWN.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Nov 12, 2006, 09:02 AM
    Not being sure if your in NYC or NY State, best to check with the appropriate code office.

    I do know that NYC does not allow ANY direct bury cable, without special permission, see Section 300.5A of the NYC code amendment

    And since NYC has several amendments and seems to be updating their code amendments, I am not sure exactly which code is in effect. I know NYC code is very strict, and has several amendments to exceed the NEC. Not sure if the state is as strict.

    You will not find any electrician considering to pull any UF cable through any conduit of any great length, only, maybe 10 or 20 feet at the most, when a sleeve is needed, and then the conduit would be oversized. UF cable is just not built for pulling through conduit.

    And, no, never have seen any UF cable not made round. Even if it was, you would damage the conduit and/or the cable no matter if it is round or flat.

    Best to do as omzig suggests, install conduit and pull through individual wires.

    XHHW insulation copper and aluminum wire is also available, and becoming more popular, actually is a bit smaller in OD, and takes less conduit fill. XHHW does not have the thermoplastic covering that THHN/THWN has, that usually gets wrinkled and adds to the pulling friction.

    Omzig is absolutely correct, any buried conduit is to be considered as a wet location.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Pulling hair [ 3 Answers ]

I find myself,well, my friends and family always tell "stop pulling yor hair" and I try so many times and I can't. If I'm sad I pull my hair, if I'm mad, hungry anything that disturbing to me. My excuse is people bite their nails and I pull my hair!! Now my sister who I went to visit in Florida I...

3-wire home, 3-wire fan, 2-wire remote [ 9 Answers ]

Greetings, My home is 3-wire. I bought a Hunter ceiling fan (model 23811). The fan came with a remote assy. That I do NOT want to use... The fan has standard 3-wire connections (black, white, blk&white strip, ground). The remote receiver home-side wiring looks to be for 2-wire (blk and white)....

Do I need conduit? [ 4 Answers ]

I have a panel in my garage for my garage based workshop. I want to run a 220 volt circuit (have have the capacity in the panel to do so). My question is whether I need to run the wire inside conduit or can I run romex without conduit. The wire will be behind drywall the entire way so it will...

Pulling Credit For mortgage Shopping [ 1 Answers ]

I Am Shopping For A Mortgage, My Credit Is Being Check Every Time. Is This Going To Affect My Credit Rating. Do I Have Any Grace Period Before It Does Hurt My Rating.:confused: :confused:

Conduit sizing? [ 4 Answers ]

Hi all! I am relocating my breaker box approx 30 feet from its original location. Installing splice box in the old location for connections. My question is : I have 14 12-2 and 3 12-3 to pull from new box to splice box what size conduit do I need so not to worry about heat build up or de-rating...


View more questions Search