    200 amp panel feeding a 100 amp panel roughly 130' away
    Hi all,
    We are building a apartment above the garage,my question is what size wire do I need to run from the 200 amp panel to the 100 amp panel roughly 130' away?
    I want to use aluminum wire as I think copper would be to costly.

    Thanks for your help in advance,
    Dude


    :eek:
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 6, 2006, 03:43 AM
    The smallest aluminum wire to supply 120/240 volts, 80 amps, at 130 feet is #1/0 XHHW Aluminum. This will result is a 2.9% voltage drop, the maximum recommended is 3% for a feeder.

    Are you sure the 200 amp panel at the main house can handle the added load of the apartment? Is it practical to have the apartment fed by it's own service from the utility?
    tdude12181's Avatar
    tdude12181 Posts: 5, Reputation: 1
    New Member
     
    #3

    Nov 6, 2006, 08:18 AM
    There is a 400 amp meter panel with 2 200 amp breakers ,1 of them goes to the house,the other goes to the pole barn across the yard.
    There is a 200 amp panel in the in the pole barn ,I was going to put a 100 amp breaker there and run to the apartment.

    Thanks again for your help

    Dude
    contractor's Avatar
    contractor Posts: 10, Reputation: 1
    New Member
     
    #4

    Mar 23, 2008, 07:14 AM
    Make sure that you use a 3 wires and a ground and keep the neutrals (whites) and grounds (bare) separate on their own terminal bars. Do not screw the green screw through the neutral bar into the new 100 AMP panel throw it away or use it for the new grounding bar that you have to add to the panel. Find an electrician to go over it before you install it.
    Handyman2007's Avatar
    Handyman2007 Posts: 988, Reputation: 73
    Senior Member
     
    #5

    Jun 14, 2012, 07:20 PM
    Is the apartment going to be in the pole barn?? If so, the 200 amp box should have enough service for an apartment unless it will be all electric.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Jun 15, 2012, 02:37 AM
    Question started back in 2006, I would think the project is done by now.
    Handyman2007's Avatar
    Handyman2007 Posts: 988, Reputation: 73
    Senior Member
     
    #7

    Jun 15, 2012, 06:13 AM
    Wow, I didn't even look at the date. I wish they would come up with a way to purge questions that are over, let's say, 6 months.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Jun 15, 2012, 10:01 AM
    That is not going to happen. Been discussed, and too many threads to deal with. Those that chose to answer questions need to note the dates of threads. Often answering an old thread may be helpful to others.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

200 amp or 100 amp [ 6 Answers ]

Which is better, a 100 amp circuit box or a 200 amp circuit box?

Sub panel 40 amp wiring [ 1 Answers ]

I have a 70 amp sub panel. I'm trying to figure out how to wire in a 40amp breaker in the sub from the panel in my house. I have two hot wires coming in to separate lugs, one neutral, but the breaker itself has one trip/reset lever yet has two screws on the bottom of the breaker;one on each side....

100 amp panel voltage [ 3 Answers ]

When looking for a problem with a double 15 amp circuit breaker, I measure the voltage at the 2 main feeds. One measured 115 volts and the other only 80 volts. Then disconnecting the main feeds from the 100 amp panel they both were 115 volts. My question is if this is caused by a loose neutral wire...

125 amp sub panel [ 5 Answers ]

What size wire do I need to pull for a 125 amp sub panel. Thank you

Question on 100 amp service/panel [ 1 Answers ]

HI, glad to have found this place, I have an electricl question hopefully Ic an find the answer to here... Is there any way to have 150 amp service added to my 100 amp box? (Giving me total capacity of 150 amps) I just replaced my old fed pacific main panel and sub panel w/ cutler hammer...


View more questions Search