    It took me a while to get back to this subject.
    My t-stat has a battery and it has Rh and Rc which are connected together.

    At the t-stat
    Black - RC
    Red - RH
    - RC and RH are connected together
    Green - G
    Orange - Y
    White - W

    At the furnace
    Black and Red - R
    White - W
    Orange - Y
    Green - G

    It's a really hot day today so I'm hoping to somehow just get the fan going manually with the AC on.
    BTW, thank you for all your help
    98accord's Avatar
    98accord Posts: 9, Reputation: 1
    New Member
     
    #22

    May 30, 2013, 05:56 PM
    Quote Originally Posted by KISS View Post
    I can't really say that.

    Your tests could be to connect R to G at the thermostat and then R to G at the furnace and see if the fan comes on. A loose or broken wire at a connection is a usual cause. So is rubbing by vibration.
    I should say that when I first tried to turn the AC this year, the fan stopped working and a technician replaced the transformer. This happened a couple of weeks ago.

    I made sure the connections were tight and replaced G with R at the t-stat and replaced the G with R at the furnace as you suggested, I also removed the black wire from both sides as it seemed redundant

    Turned AC on, fan on.
    Fan is on, but AC is not on right away,
    Two minutes later AC outside turns on and fan goes off.
    I'm back at square one.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #23

    May 30, 2013, 07:03 PM
    The transformer died probably because a wire is rubbing against ground someplace. Just a thought anyway.

    Quote
    1. Turned AC on, fan on.
    2. fan is on, but AC is not on right away,
    3. two minutes later AC outside turns on and fan goes off.
    Unquote

    Somehow, you may be talking about two different fans.
    The inside fan (furnace/evaporator fan) and the outside fan (condenser fan)

    If #1 Fan is the inside fan, that's OK.
    #2 is OK
    #3 A is OK, the fact that the outside unit turns on 2 minutes later.

    The fact that it turns OFF is likely due to the AC unit kicking out because of "something"
    Suggestions are
    1. High pressure
    2. Low pressure
    3. Outside fan isn't running

    The "2 minute" delay is usually built into the thermostat to prevent the compressor from coming on under load.

    I can't quite figure out the pieces, because "fan" can mean multiple things. Outside or Inside.

    The fact that the transformer died suggests another problem such as an intermittent short in the tstat wires heading to the outside unit.

    Now, you could cut the AC power to the outside unit at the disconnect and watch/listen for the contactor to click after the 2 min wait. If the contactor stays in, you probably have an AC related issue. If it does not, then you may have a t-stat/wiring issue.

    In most cases the outside AC contactor gets power from the furnace.



    I'm back at square one.
    98accord's Avatar
    98accord Posts: 9, Reputation: 1
    New Member
     
    #24

    May 30, 2013, 07:18 PM
    Quote Originally Posted by KISS View Post
    The transformer died probably because a wire is rubbing against ground someplace. Just a thought anyway.
    That is probably the case because I did notice the black wire that connects to the Rc or Rh was loose at the furnace

    Quote Originally Posted by KISS View Post
    Somehow, you may be talking about two different fans.
    The inside fan (furnace/evaporator fan) and the outside fan (condenser fan)
    When referred to the fan, I've been referring to the Furnace fan circulating the air in the house. (inside fan)
    When I referred to the AC turning on, it's the outside AC fan and compressor as I can hear them both.

    I will try your other suggestion tomorrow.
    Again thanks for your help.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #25

    May 30, 2013, 09:44 PM
    This post got misplaced:

    Do this also:

    With the t-stat turned OFF which means
    FAN --> Auto
    Mode; Cool-OFF-Heat (turn to OFF)

    At the furnace connect R to Y to G. Before you make the connections, turn the power to the furnace off.

    If all goes to plan, the AC would turn on, but never turn off. The inside fan will run too.

    ---

    Aside:

    Something to consider, since you have the right number of wires: Make the Rc/Rh connection at the Stat and also bring Common to the thermostat.

    Depending on the age of the furnace, Common may not be labeled, but if your tstat supports common, I would use it.

    Common is simply the other wire of the 24 V secondary that isn't connected to R.

    ---
    98accord's Avatar
    98accord Posts: 9, Reputation: 1
    New Member
     
    #26

    May 31, 2013, 05:31 AM
    Quote Originally Posted by KISS View Post
    Do this also:

    With the t-stat turned OFF which means
    FAN --> Auto
    Mode; Cool-OFF-Heat (turn to OFF)

    At the furnace connect R to Y to G. Before you make the connections, turn the power to the furnace off.

    If all goes to plan, the AC would turn on, but never turn off. The inside fan will run too.
    Do I use another wire to connect R to Y to G? Or do I connect the R to the Y and the Y to the G and R remains unconnected?


    Quote Originally Posted by KISS View Post
    Something to consider, since you have the right number of wires: Make the Rc/Rh connection at the Stat and also bring Common to the thermostat.

    Depending on the age of the furnace, Common may not be labeled, but if your tstat supports common, I would use it.

    Common is simply the other wire of the 24 V secondary that isn't connected to R.

    ---
    So right now the R from the furnace is connected to Rc and Rh. The Black wire is available for use.
    I do see an un labeled spot at the furnace which is probably the Common, and I can connect the black wire to it.

    At the Stat, I don't believe I have the option for Common.
    These are my options.
    H2, H1, B, O, RC, RH, G, Y, W.

    What would I be connecting the Black (Common) on my Stat?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #27

    May 31, 2013, 09:30 AM
    OK, you don't have common on the stat. On the surface, you have a heat pump thermostat with humindity control. See: http://www.epatest.com/store/resourc...t-operates.pdf

    The giveaways are the B and O terminals. One of these goes to a reversing valve, that changes the system from heat to cool. B and O are complements of each other. Which one is used depends on whether the reversing valve is unpowered in heat or powered in heat.

    H1 and H2 are humidistat contacts.

    Rc and Rh we discussed.

    G is the Fan

    Y is the compressor. In a heat pump, the Y connection is used ALL of the time. It turns the outside unit on.

    What confuses me "a little" is that I would normally expect W to be labeled W2. For aux heat.
    Aux heat is usually a resistance heater in the furnace.

    The stat could still have configuration options for conventional or heat pump. We need to nail what type of system you have? 1) Conventional or 2) Heat pump

    With a heat pump, the outside unit comes on when your heating or cooling unless the outside temperature is too low. In a heat pump, there is a valve that reverses the pluming connections to the compressor.

    SO, there is a CHANCE that the thermostat can do conventional or heat pump by configuration.

    ==

    So, let's ignore the R to Y and R to G for now although I will try to describe what I meant. Leave the wires as they are connected at the furnace and have the thermostat off. It doesn't matter if you use two wires or one, just as long as R,G and Y are connected together and you do the connections with the furnace disconnect off.

    If this is a heat pump, you may end up with heat or cooling. Usually heat. The idea is if a reversing valve fails, you want the system to be stuck in heat, not cool mode, but that is dependent on the heat pump operation.

    So,
    1. is outside unit a heat pump?
    2. Is the thermostat the correct type or can it be configured?
    98accord's Avatar
    98accord Posts: 9, Reputation: 1
    New Member
     
    #28

    Jun 4, 2013, 11:18 AM
    So I bypassed the stat and ran the tests you suggested.

    I can get the inside fan to go on, the heater to go on, I can get the AC outside fan and compressor to go on, But when I connect the AC with the instide Fan, the fan just does not want to turn on..

    This in my opinion eliminates the possibility that the stat is at fault. I took a picture of the motherboard and it looks burned out.

    I am now looking for a "ST9160B 1050" motherboard, but all the parts I've seen online don't match the one that I have. Any suggestions on where I can purchase the correct one? If I were to purchase a "ST9160B 1050" with a green board and a different layout, would it still work? Are there different versions?
    Attached Images
     
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #29

    Jun 4, 2013, 01:28 PM
    You did good.

    I tend to agree with about 95% certainty. We have not eliminated a short within the t-stat wiring or the wiring to the AC unit.

    I am trying to think of other scenereos that may cause your issue. Fresh batteries in the stat? I would not expect this to be the case, but if the AC system had it's own transformer and it was connected like you have it, it MAY be possible for the 24 VAC to drop to zero. Two transformers in parallel.

    We never did determine if the stat was a heat pump/regular stat. The furnace definitely looks conventional.

    So, I would suggest to remove and label all of the wiring going to the thermostat at the furnace (that will leave two wires going to the AC outside) and repeat the R to Y and R to G test.

    Another odd ball suggestion is if there are any EXTRA wires in the AC unit, change briefly to another two running outside. Really doubt a problem exists here.

    I'm trying to 100% eliminate everything else. I don't know if you own a multimeter?

    Aside:

    Note the automotive type fuse in the upper left hand corner. This is the fuse to the thermostat 24 VAC secondary.

    Note the yellow an the Blue wire. Blue "probably" connects to one end of the fuse and then to R. Verify!

    That would make the Yellow fat wire, the Common terminal on the stat. For future reference a Piggyback spade connector would be a way to add a common terminal should you decide to replace the stat.

    The furnace boards DO NOT have to look the same. Some actually come with various harnesses to allow them to work with other models. This is just one example listing: Honeywell Fan Control Board ST9160B1050 ST9160B 1050 | eBay

    TIP:
    If you do not have a hole house surge suppressor, I would consider investing in a wired in suppressor just for the furnace. Most furnaces have nothing in there for protection against spikes and RFI.

    If you can't afford that, I would add a TVS on the 24 V secondary side. For about $5.00.

    I HAD to add a $80.00 RFI filter on a carrier furnace because it was interfering with my power line automation controls.

    I do live in an area where power problems are very rare including outages. The two important things, the computer network and the phone/answering machine and a PERS alarm are on a UPS. One repeater on my network is not. That power supply got knocked out at the same time a neighbor's oven controller was knocked out.

    The importance of a commercial product is not the cost, but the warranty, Some have a $50,000 to $100,000 insurance policy on connected equipment and offer a lifetime warranty.

    I am not 100% convinced. Maybe 95%, but not 100. Why, one side of the 24 VAC is usually grounded.

    One commercial AC guy actually ordered a ceiling heat pump because he thought it was bad. When all of the effort to install the HP including overtime, it still would not work.
    He asked me for some help. In about 10 minutes, working together, I said you have a bad t-stat wire and left him. Turned out the wire had shorted at a metal stud during a remodel.

    In another instance, the installer didn't pay attention to the way the outside unit was wired. Two wires were paralleled and he paralleled the wrong ones. To make matters even worse for trouble shooting, the installed spliced the wires about 2 feet from the AC unit and then used different colors. The splice was crappy too without a drip leg. Using the wrong colors was definitely bad. It was a really tough problem to find.
    98accord's Avatar
    98accord Posts: 9, Reputation: 1
    New Member
     
    #30

    Jun 26, 2013, 06:10 AM
    So here is my solution to my furnace problem.
    I ordered a universal replacement Control Board (ST912ou1011) from HVAC Parts Outlet which is meant to replace my OEM board.
    I connected it according to the diagrams but it would not work, the blower fan would turn on even if the stat is unplugged. When I would turn the AC on from the stat, it would not turn on. I had my brother come in and test all the connections and follow the diagram to make sure I'm not missing anything and I wasn't.
    On the diagram for the board, it showed that M1 and M2 were not being used and that I should have a cable for Data and Cont.
    When I saw that the forecast for this week was going to be in the high 30s and low 40s I decided to call a professional. I called the same company that replaced my transformer over a month ago and the same person showed up.
    When he came in, he spent about 30 minutes diagnosing the connections I've made, then proceeded to tell me that these universal boards don't always work and that I need an OEM board.
    It took him over an hour to go pick up the new board which to my surprise was an identical board, same universal model. He told me that this is the only one as a replacement. When he plugged it in the same way as I had it, everything worked fine.

    I'm happy that I finally have the AC working but I'm quite upset that I had to spend $340 on the technician when I could have resolved my own issue if the board just worked. I also have my doubts that I'll be getting my money back on the defective board.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Blower in furnace works in heating mode, not in cooling mode [ 5 Answers ]

The furnace is an older model Carrier. I do not know at this time the exact model. It is at this time about 20 years old. The central air is a newer Carrier Performance series model. It is two years old. I have checked to make certain the blower moves freely; it does. The blower in the...

Carrier A/C Blower will not come on in A/C mode but works when in heat mode [ 3 Answers ]

I need some guidance. I have a Carrier A/C unit that has been working fine. Last night the fan stopped working for some reason in the A/C mode. But when I put the heat on, it works fine. The compressor and condenser work fine but the A/C fan just will not kick on. I thought it might be the...

Blower turns on and off / flame works fine [ 1 Answers ]

I have a Luxaire Delux High Efficiency Furnace (PBNU-LD12N1000)that probably isn't to efficient since it's about 15 years old. I recently bought a new home and have had trouble with the blower in the furnace turning off before the house is heated to the correct temp. It will then turn itself back...

Furnace turns off at 'ON' mode and will not operate at 'AUTO' mode [ 6 Answers ]

The furnace will not turns on at "ON' mode. After some reading, I thought it would be the pilot light that has gone out. I re-lighted the pilot light to see blue-red flame, but the furnace will turn off AGAIN after 3-4 hrs. Replaced a new Honeywell non-programmable thermostat today with the...

Furnace turns off at 'ON' mode and will not operate at 'AUTO' mode [ 2 Answers ]

The furnace will not turns on at "ON' mode. After some reading, I thought it would be the pilot light that has gone out. I re-lighted the pilot light to see blue-red flame, but the furnace will turn off AGAIN after 3-4 hrs. Replaced a new Honeywell non-programmable thermostat today with the...


View more questions Search