    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #41

    Sep 6, 2009, 09:29 AM
    Should I put a cardboard sleeve around the PVC coming up so the concrete doesn't touch the PVC?
    We use Armoflex (see image) to insulate our pipes coming through the slab. Good luck, Tom
    adkhkr's Avatar
    adkhkr Posts: 64, Reputation: 1
    Junior Member
     
    #42

    Sep 6, 2009, 09:37 AM

    So do you piece it together so it covers around the whole pipe?

    Just so you understand what I am talking about, I want to wrap the 4" and 2" pipes.

    I am moving along with the plumbing. The pitch was fine, after I connected the length of 4" pipe it turned out to be 3/8" per foot. Below is a picture of the rest of the job. How does it look?

    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #43

    Sep 8, 2009, 02:21 PM
    I'd make a few changes to this... have you installed this yet? Let me know... if not, I'll post a new drawing up and show how I would do it... O.K.? Let me know...


    PS: Cardboard will be fine around the PVC coming out of the ground... ;)

    MARK
    adkhkr's Avatar
    adkhkr Posts: 64, Reputation: 1
    Junior Member
     
    #44

    Sep 8, 2009, 03:40 PM

    Mark -

    I have only installed one 10' piece of 4" PVC just past the 2-Street 45s. I haven't done anything in the bathroom or kitchen. Any help would be great.
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #45

    Sep 8, 2009, 05:21 PM
    Hey hey...

    Need to end the run in a 4" elbow into a 4" cleanout... run a 4"x2" wye to pick up the kitchen sink.

    In terms of the bathroom you want end on the toilet with a 4" elbow and use a 4" elbow and use a 4" wye (rolled above center line) to wet vent both the toilet and the shower using the vent for the sink. You will need to increase the vent to 2" as directed in the drawing below.

    A 2" wye (rolled above center line) to wet vent both the toilet and the shower using the vent for the sink. You will need to increase the vent to 2" dandy clenaout are required as below, etc.

    Let me know if all this makes sense...

    MARK
    Attached Images
     
    adkhkr's Avatar
    adkhkr Posts: 64, Reputation: 1
    Junior Member
     
    #46

    Sep 12, 2009, 11:15 AM
    Mark... the layout I had isn't going to work because my measurements were incorrect. Measure twice, cut once right. Sorry you made the layout for nothing, my apologies.

    Anyway... unfortunately my measurements were on the long side so I had to rearrange the bathroom. Do you think this layout is acceptable? I realize its tight, but I can't change the dimensions. And I really didn't want to go with a smaller shower than a 40" corner unit. Also, I will be using a pocket door.

    Here is a revised pic of the bathroom.

    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #47

    Sep 12, 2009, 04:30 PM
    No problem on the measure error... I've gotten pretty quick at drawing these up... ;)

    I don't blame you on the 40" minimum shower....you won't regret that, but it is a tight space, for sure! The toilet is tight, but it fits within the 30" minimum toilet space required by code.

    I've attached a new layout... let me know if it makes sense. Review post #45 to be clear on additional information.

    MARK

    PS: You are installing a properly ventilated fan at bathroom... yes?


    .
    Attached Images
     
    adkhkr's Avatar
    adkhkr Posts: 64, Reputation: 1
    Junior Member
     
    #48

    Sep 13, 2009, 06:31 PM

    When you say to roll the 4x2 wye above center, is this what you mean?




    I have to say, I can't wait until I don't have to break up anymore concrete:)
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #49

    Sep 14, 2009, 04:36 AM
    Exactly what I mean...
    adkhkr's Avatar
    adkhkr Posts: 64, Reputation: 1
    Junior Member
     
    #50

    Sep 19, 2009, 01:10 PM
    I have all the concrete trenches done, but now I am confused about how to get the 2" shower pipe to come up in the exact spot where the shower drain is. I bought the shower pan, an americh 38x38 corner neo angle. I know where it should be... but I am just worried that when I concrete over the trenches/pipes, and something shifts I am screwed. Is there a trick to this. I read in another post about a DAPOUT box, should I do this?. This morning I made a template out of plywood with the hole in the correct spot. I think that is going to take any error out of the final location.

    This is the drain that came with it... if you click on the link it is in the shower base manual section.

    Downloads | Manuals

    Should I get another drain that is easier to work with, if there is such a thing? This utilizes a neoprene ring that expand against the pvc pipe as a seal.

    Where the toilet comes up... do I use a regular 4" 90 degree elbow with the 4" PVC coming up through the concrete? Then I would flush cut the PVC with the top of the concrete when its cured.
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #51

    Sep 20, 2009, 08:07 AM
    The link didn't work Adkhkr... but the neoprene sleeve type is the easist to work with.

    In terms of the dapout box... yup! That's the trick with showers... ;)

    A plumber would rough in the ptrap and stub up a riser about 6 inches above the floor, and then install the dapout box, cover with dirt, pin it tight with stakes and then add concrete to the surrounding floor. When the concrete dried, the stakes and dapout box are removed and the dirt is cleared away to about 4 inches below the floor. Then the shower pan is DRY FIT (just placed over the stubbed up pipe) and lkeveled in all directions to see how the rough in went. If all is OK, the plumber proceeds to install the strainer assembly, install a structolite (or mortar) base and then sets the shower pan and levels from side to side and from front to back (use shims as needed to keeep pan where it is wanted).

    You can try to do it as a plumber... OR, you may want to DRY FIT the ptrap and riser, making sure you like the rough in and then remove it all back to the horizontal pipe and just cap it for now. Place the dapout where it will work nicely for the drain and then fill the dapout with dirt and stake it off and then add concrete to trench and let all dry, etc.

    Then, pull the dapout box, remove all the dirt, and start cementing the ptrap and riser up and into place. Check the fit with the pan leveled as mentioned above as you go and you should be able to get a good rough in without too much trouble.

    After the drain is roughed in correctly, you will fill the dapout hole to within 2 inches of the concrete floor and you will install the shower strainer and once again, DRY FIT the base and level to be sure all is good! Once all is confirmed good you will want to install a base or structolite or mortar and set the shower pan level from front to back and from side to side.. again, shimming overnight or so to be sure the base doesn't move even a little bit!

    Be clear that an 1/8" off on the base will translate to 3/4" off on the shower doors (6ft vertical x 1/8" off horizontal = 3/4" out of plumb on door). There is some adjustability in neo angle doors, but not a full 3/4"... usually! My point is simply that you need to be sure the shower base gets set perfectly... ;)

    Let me know if you need more...

    MARK
    adkhkr's Avatar
    adkhkr Posts: 64, Reputation: 1
    Junior Member
     
    #52

    Sep 20, 2009, 09:48 AM

    Thanks. Two additional questions:

    1) Coming up for the toilet, should I use a standard 4" 90 degree elbow and glue a piece of 4" PVC so it sticks out of what will be the top of the slab?

    2) On the 4"x2" Wye that is turned up, does the 2" section that comes out have to be completely vertical as in the previous picture? The problem is that I will be getting too close to the slab. I can really only turn the WYE slightly. How much turn do you have to have?
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #53

    Sep 20, 2009, 11:47 AM
    1) Use a regular 4" 90 and DRY FIT the stub up for now. Later, when all is tiled you can put the flange on the tile and measure the piece you need to join the flange to the elbow. Then you can prime/cement the flange/pipe into the elbow easily! When tiling, be sure to leave enough room around the dry fit stubbed up pipe so that it acommodates the new closet flange, but not so much room that you can't screw the flange down through the tile.

    2) As long as the wye rolls above the centerline of the drain pipe it will work for me at any angle.

    MARK
    adkhkr's Avatar
    adkhkr Posts: 64, Reputation: 1
    Junior Member
     
    #54

    Sep 21, 2009, 05:59 AM

    For the length of 4" pipe that connects to the toilet, I had to stake it into position because the natural position was shifted a bit from where I wanted it.

    I didn't force it to the point where it was going to snap at the joint, but I did need push it a bit and stake it in to prevent it going back.

    Obviously you aren't here, but can PVC, such as in this case be pushed into place and not have to worry about having a joint fail in the future?
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #55

    Sep 21, 2009, 06:03 AM
    PVC joints are welded and not glued. If you primed and cemented the joint correctly and didn't put too much strain on the fittings you should be just fine Good luck, Tom
    adkhkr's Avatar
    adkhkr Posts: 64, Reputation: 1
    Junior Member
     
    #56

    Sep 21, 2009, 06:19 PM

    Down to my last couple of fittings under the slab and I ran into a bit of a problem. One of the fittings doesn't want to weld. After I weld it, with a little bit of force it pulls apart. I tried cleaning it with primer and glueing it again but it doesn't want to take like a normal piece. If I twist it, its strong but any vertical force and it pulled out.

    I thought I would be done tonight and I run into this. I really don't want to have to put a new piece in because it's the wye going to the shower and I would have to dismantle the pieces going to the sink. Any ideas or am I just losing it?
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #57

    Sep 21, 2009, 07:39 PM
    Hey hey...

    When this pops up you want to do exactly what you did... reprime and recement, but then you need to hold it tight... and I mean tight!

    Takes a few minutes longer and you may need to strain a bit beyond normal, but on occasion you run into that certain fit/joint that just wants to pull apart. You need to stop it from doing so, up to a minute or more. Then it will weld to the point that you can let go. It could slide out again, so want to check it for first 4-5 minutes... and be sure you are NOT the first person this has happened too... ;)

    If you reprime, recement and hold, the joint will take.

    Any more questions, let us know...

    MARK
    adkhkr's Avatar
    adkhkr Posts: 64, Reputation: 1
    Junior Member
     
    #58

    Jul 13, 2010, 12:15 PM
    Its been awhile, but I am finally looking to finish this project up. I am going to run the vent pipe to an existing vent... see attached. My question is... is it OK to run an existing vent pipe with 3 90s and a horizontal length of approximately 30'.

    Can the vents be connected the way I have shown?

    Thanks.
    Attached Images
     
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #59

    Jul 13, 2010, 01:38 PM

    Hi Adkhkr... been awhile... ;)

    You can use the 90s, but most codes allow only 1/3 of a vents overall developed length to be run horizontal.

    For example, on a vent with an overall developed length of 60 feet, only 20 feet of that run would be allowed to be horizontal. Here, if the horizontal run exceeds 1/3 of the developed length, say 45 feet in our example, then you must increase the pipe size of the entire vent by one pipe size.

    What is the overall developed length of the vent from the basement floor to the roof? Let me know... OK?

    Mark
    adkhkr's Avatar
    adkhkr Posts: 64, Reputation: 1
    Junior Member
     
    #60

    Jul 14, 2010, 03:16 AM

    Looks like I might have a problem with this... the overall developed length would be approximately 50', with 30' being horizontal.

    Could I get away with installing an air admittance valve as the vent?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can you Install a house trap yourself? [ 4 Answers ]

I just had a plumber come out and they told me that my house trap is rusted/clogged and has tree roots in it. Their recommendation is to replace it (I totally agree) I'm pretty sure that the code in Allegheny county, PA says that you have to keep the trap. Unfortunately, the Roto-Rooter guy said...

Installing House Trap [ 14 Answers ]

Hi there. I found this site after researching house traps I live in Allegheny County, Pittsburgh PA We have a septic tank, and the water and sewage authority is requiring us to disconnect from our present (working) septic, And connecting to their sewage line, About 60 feet down a steep hill....

New house, no p trap in shower, buried in concrete. [ 3 Answers ]

So, we built a new house, had a plumber do the rough in and run the water lines. Had another contractor build the shower base's for custom showers. I tiled one shower and it turned out gorgous. Then after using the shower a couple of times a horrible gas smell arouse, I thought it might be the...

Sewer P-trap for house main line [ 1 Answers ]

Bought a 40 year old single story home in San Diego and we love it, except we get a sewer smell periodically outside (depending on weather, I guess). The smell is really bad. Had a plumbing come out and unclog a clog, and he mentioned maybe putting a P-trap on the our main line between the house &...

House Trap Odor [ 3 Answers ]

I have a horrible odor coming from the house trap. What could be the cause and what Can I do to correct it? Thank you for any suggestions.