    David Pollard's Avatar
    David Pollard Posts: 2, Reputation: 1
    New Member
     
    #1

    Oct 15, 2006, 12:49 PM
    Carrier Gas Furnace
    My Carrier 58SS gas furnace starts up and lights up the burners and operates normally for 2 minutes, then the burners shut down but the igniter and pilot light continue indicating the thermostat is requesting the furnace to heat up the house. I changed thermostats to see if that was the problem and it isn't. When I shut off the furnace and retry it the same thing happens in the same amount of time every time. For some reason the gas is being shut down to the burners after 2 minutes. I replaced the air filter and checked the reset button used for a blocked air intake. Why is the gas shutting down to the furnace burners after 2 minutes? Thanks.
    The WB's Avatar
    The WB Posts: 78, Reputation: 6
    Junior Member
     
    #2

    Oct 15, 2006, 02:29 PM
    Your limit switch may be malfunctioning. Do you have a pilot light or an electronic ignition? I don't think that you can have both.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #3

    Oct 15, 2006, 03:36 PM
    Does the blower come on? Gas furnaces have a start up sequence with sensors checking each step. If something doesn't work, it starts over again a few times before giving up. Some furnaces use an electric ignitor to light a pilot, and then open the gas valve once the pilot is burning. Then a sensor must detect a flame. The next step is for the blower to come on. If either it doesn't detect the flame, or the blower doesn't come on, it shuts the gas off and tries again. The problem could be either one of the switches, or on the control board. The relay for the blower on the board often fails.

    Many newer furnaces have a light that flashes a trouble code. Could help you narrow the problem down.
    David Pollard's Avatar
    David Pollard Posts: 2, Reputation: 1
    New Member
     
    #4

    Oct 15, 2006, 08:35 PM
    Quote Originally Posted by David Pollard
    My Carrier 58SS gas furnace starts up and lights up the burners and operates normally for 2 minutes, then the burners shut down but the igniter and pilot light continue indicating the thermostat is requesting the furnace to heat up the house. I changed thermostats to see if that was the problem and it isn't. When I shut off the furnace and retry it the same thing happens in the same amount of time every time. For some reason the gas is being shut down to the burners after 2 minutes. I replaced the air filter and checked the reset button used for a blocked air intake. Why is the gas shutting down to the furnace burners after 2 minutes? Thanks.
    Yes the blower comes on and a check of the heat vents shows normal heat being distributed to the rooms in the house. There is a pilot light and I can hear the ignitor until the burners light off. 2 minutes later the burners shut down and the ignitor can be heard again.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #5

    Oct 15, 2006, 08:59 PM
    The circuit board is shutting down the furnace because it thinks the blower isn't running. Either the limit switch that signals the blower is running is bad, or the board is bad. The limit switch will be a thingamabob somewhere on the heat exchanger and have 2 wires running back to the board
    The WB's Avatar
    The WB Posts: 78, Reputation: 6
    Junior Member
     
    #6

    Oct 17, 2006, 09:47 AM
    Are your thermostats level?
    Tarik's Avatar
    Tarik Posts: 3, Reputation: 1
    New Member
     
    #7

    Feb 24, 2007, 10:56 AM
    Quote Originally Posted by David Pollard
    Yes the blower comes on and a check of the heat vents shows normal heat being distributed to the rooms in the house. There is a pilot light and I can hear the ignitor until the burners light off. 2 minutes later the burners shut down and the ignitor can be heard again.
    I have the same problem though our furnace run for more than 2 min at a time. I
    Did you figure out the problem David?
    BrianM's Avatar
    BrianM Posts: 1, Reputation: 1
    New Member
     
    #8

    Apr 26, 2007, 08:23 PM
    I have a very similar problem but not as severe. A tech guy came to replace the blower motor and the problem got worse. He thinks it could be the spark sensor or gas value. He also recommends replacing the whole thing. What was your solution? I see the spark sensor costs is about $25 and I may go with that. The heating season is now gone here so I could wait till fall.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #9

    Apr 27, 2007, 10:18 AM
    BrianM, I would suggest cleaning the flame sensor before you call someone back
    mirzas's Avatar
    mirzas Posts: 1, Reputation: 1
    New Member
     
    #10

    Oct 16, 2010, 08:13 AM
    May be your chimeny needs cleaning.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Carrier furnace [ 2 Answers ]

Blower runs, furnace won't ignite. ( pilot light IS WORKING) 1. filter was cleaned 2. thermostat reprogrammed . Is there anything we can do beafore calling service?

Carrier Furnace [ 4 Answers ]

I am looking at furnace for a friend. The furnace will come on with that small fan and the pilot will light. However, the burner will not catch. This unit has a igniter I suspect that the igniter is bad. Is there any way to test it?

Carrier Natural Gas [ 4 Answers ]

I have a carrier central natural gas heater model 28rds030000 we have heat, but it won't shut off, I replaced the thermostat and it still does the same thing. Can anyone help me locate this problem? Marc (DELAWARE)