    #21

    Mar 15, 2009, 03:43 PM
    Quote Originally Posted by hvac1000 View Post
    Very strange indeed. Since the service man already replaced the circuit board which did not help and then replaces the gas valve which then allowed the furnace to operate normally for two weeks before the problem started again I have just about exhausted what I can tell you to do from here since the only part you can check next is the pressure switch mentioned by KC13 in his post above.

    I did not mention the pressure switch before since I figured you did not have a electric meter to measure resistance across the contacts when the small furnace draft fan is in operation. If you have a meter or can borrow/buy one you can test the pressure switch which is part number 41 on page 4 of this link.

    http://igate.northernplumbing.com/pa...anMfg/GMS8.pdf

    The pressure switch is attached to the furnace and has a plastic tube attached to it.
    I do own a digital multimeter (Christmas present from a friend who always looked out for me with tools.. ). So here goes the questions... :D

    Have AC/DC switch: presume AC
    Dial has the following areas: F, V, A, O(with feet): presume the later (O with feet)
    Settings in ohm; 20M, 2M, 200K, 20K, 2K, 200: Not sure here, or does it matter. I presume any number is not good.

    When you indicate to measure when the small draft fan is on. I presume this is the first fan I hear when the unit begins the heating process?
    Mikie D's Avatar
    Mikie D Posts: 45, Reputation: 1
    Junior Member
     
    #22

    Mar 15, 2009, 03:51 PM

    20 ohm fine, test all limit switches firsy when you touch leads together meter should read 0 that's continuity take wires off limits and test all should read zero. Now the pressure switch should read open not zero,Then start furnace and 5 sec after first draft motor starts ,test press switch and should close or zero meaning made then let us know
    coreyclark's Avatar
    coreyclark Posts: 15, Reputation: 1
    New Member
     
    #23

    Mar 15, 2009, 04:21 PM
    Quote Originally Posted by Mikie D View Post
    20 ohm fine, test all limit switches firsy when you touch leads together meter should read 0 thats continuity take wires off limits and test all should read zero. now the pressure switch should read open not zero,Then start furnace and 5 sec after first draft motor starts ,test press switch and should close or zero meaning made then let us know
    Pardon the rookie question, 20 ohm meaning 20m? If so, results:

    Test with Leads on Switch = 0
    Test wires attached to switch = 0
    Test switch with no wires = no change in digital reading

    Test switch after power on of furnace (no wires attached, correct?) returns to zero after approximately 2 seconds.

    Standard operation?
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #24

    Mar 16, 2009, 03:35 AM
    It seems as though you are not reading anything beyond the most recent post. Good luck.
    coreyclark's Avatar
    coreyclark Posts: 15, Reputation: 1
    New Member
     
    #25

    Mar 16, 2009, 06:24 AM

    Don't mean to be rude, but I have read all the posts. Your second post concerning the timing of jumpering the pressure switch came as were were discussing the aux limit control jumpering. Since that time, I the discussion has migrated to the pressure switch. Specifically, checking for resistance on the pressure switch. Does the last test satisfy the question about the functioning of the switch? If not, then I presume the draft inducer is the first initiated process after the t-stat calls for heat?

    Sorry for all the rookie questions but it is frustrating to have this when our service is stumped about the issue.

    Again, thank you all for your generous assistance.
    coreyclark's Avatar
    coreyclark Posts: 15, Reputation: 1
    New Member
     
    #26

    Mar 16, 2009, 03:47 PM

    Finally got a call from the service man. He contacted the Goodman company and they want to have the pressure checked from the gas line into the furnace. Goodman indicated that the newer models of gas valves need less pressure than their older counter parts. The service man is coming out tomorrow. I'll post back with the results.

    Thanks again for all the responses.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #27

    Mar 16, 2009, 03:59 PM
    Are you on Natural gas or propane?
    coreyclark's Avatar
    coreyclark Posts: 15, Reputation: 1
    New Member
     
    #28

    Mar 16, 2009, 04:34 PM

    Natural gas.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #29

    Mar 16, 2009, 10:35 PM
    Your quote (The igniter will not stay lit long enough to ignite the gas. The process starts blower comes on, click, igniter lights, igniter goes out, you hear the gas released but obviously does not ignite the burners.)

    It will be interesting to see how this works out.
    coreyclark's Avatar
    coreyclark Posts: 15, Reputation: 1
    New Member
     
    #30

    Mar 17, 2009, 04:22 PM

    Well what do you know. The service guy came back today and the Goodman contact was correct. The gas pressure was set to high. He throttled it back to the appropriate pressure and it worked. He tried it multiple times just to make sure. So, it is working... for now.

    Now the interesting question... Did we really need to replace the board and gas valve? Guess we'll never know.

    Thank you all for your information and assistance.
    Mikie D's Avatar
    Mikie D Posts: 45, Reputation: 1
    Junior Member
     
    #31

    Mar 17, 2009, 05:08 PM

    I highly Doubt it I can tell you how many time techs set up new and old furnaces and never put there manometers on them. Mikie D
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #32

    Mar 17, 2009, 05:54 PM

    Glad you got it fixed. Sorry I wasn't there to check pressures. This is common. High pressure on newer vavles will not let valve open(sometimes letting them open a few seconds too late, after igniter has shut down).
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #33

    Mar 17, 2009, 08:42 PM
    I have had a service person out and after he checked all the switches and bypassed all parts, indicted it was a faulty circuit board. His return trip to install the circuit board was not successful. The furnace fired once and then back to the cycling. He then replaced the gas valve. At the time this appeared to resolve the issue.


    When he replaced the gas valve he did not do what servicemen are supposed to do and adjust the gas pressure as part of the service. You always check and adjust the gas pressure as part of the service and check out or when replacing the gas valve.

    BTW It does not make a difference if it is a old or new gas valve as far as the pressure goes. The correct operating pressure is listed on the furnace information tag along with the model numbers and you always adjust to that pressure since that is what determines the firing rate/BTU's per hour heat capacity.

    When standard routine's are not followed this is what happens and you had to pay the piper for his mistakes. At least you got it going.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman pilot light on but furnace burners will not come on? [ 4 Answers ]

We have a Goodman furance that will not produce heat. The pilot light is on, the gas is released, but the burners will not kick in. Do you have any idea what is causing this problem.:confused: Scott's Chicago

Goodman furnace burners [ 1 Answers ]

How do I ignite the burners on a goodman furnace?

Goodman gas furnace not igniting [ 1 Answers ]

Suddenly the furnace is not igniting, we can light it manually and the furnace kicks on, but once it reached the desired temp, it will not ignite itself when the temp goes back down. Where do we start troubleshooting?

2002 Goodman furnace not igniting [ 3 Answers ]

For several days - have been manually powering down then restarting sometimes catching on the first second or third ignite, trying to fix the furnace and save the kids some money... today it died... will not ignite.. have sanded the flame sensor... cleaned every connection possible... Today...

Goodman furnace not igniting [ 25 Answers ]

I have a Goodman furnace (I think, that's what the guy who came to give me an estimate for having central air installed said) and it won't ignite. I had a vent blocked to one room in the house because I was scraping paint and didn't want the dust in the ducts. It was blocked for about 20 hours. ...


View more questions Search