    Are zone valves or zone thermostats possible with a steam boiler?
    I have an old 4 story building with one thermostat controlling the steam heat to all floors. There is a commercial space on the ground floor and they are complaining that they don't get enough heat sometimes (and on occasion get too much!) They have suggested that there is some way to place a thermostat or valve on the radiators in each space in the building to control the heat in that space. Is this possible? They are the only inhabitants of the building who are having issues with the heat. This space also has a lot of glass windows in the front. Any suggestions would be helpful.
    21boat's Avatar
    21boat Posts: 2,441, Reputation: 212
    Ultra Member
     
    #2

    Jan 6, 2009, 06:11 PM

    If your steam radiators have one pipe system you can take of the original air steam bleeders and replace it with a steam radiator thermostat valve. This controls weather the steam comes into the radiator buy controlling how much steam in temp somes into the radiator.
    Just remove the steam bledder vavle that ssshhh part and replace with adjustable tem valve and these can be adjusted for a good temp range

    Signed 21 Boat

    If I Helped To Answer Your Question Please Rate My Answer

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

2 zone oil heat, 2nd zone runs 1st zone [ 1 Answers ]

Hi, We have a 2 zone oil burner. The 1st zone (upstairs) runs separately and works no problem. The 2nd zone(basment), when we try to run 2nd zone separately , it seems to run zone 1(upstairs) and the baseboard heating upstairs gets hot and heats zone 1 even thought we have the t-stat set low...

3 wire old steam with zone vals [ 1 Answers ]

:confused: I have 2 zone steam boiler with honeywell mechinal zone valves controlled by a three wire thermostat zone valves need power to open on call from thermostat as well as power to close from thermostat... valve is definitely working but I can't figur how to wire 3 wire t stat properly......

Wire zone valves [ 3 Answers ]

I have a oil fired boiler with taco 562 zone valves.My wires are from transformer red&green.Wire from thermostat are red& green.On my zone valves the wires are red,green&yellow.Aperson who said he could fix zone valves had taken all wires off the zone valves.The zone valves have numbers 1,2,3,which...

Zone valves [ 2 Answers ]

Looking for a wiring diagram for a new dunkirk boiler . Just the diagram for the 3 zone valves. Company says that the boiler transformer is enough to run three zones ( 24v) . Or do I need to add transformer. Just can't figure out the wiring from one zone valve to another. Contacts on each zone are...


View more questions Search