    Placement of AAV
    Long story short our kitchen sink in our house needs an AAV as a result of a renovation. My question is to the exact location of the AAV downstream from the p-trap. Thank you in advance for any advice.

    RMH

    Option 1. Place it ontop of the "T"

    AAV
    L
    l--------------------P-Trap
    l
    l
    l

    Or...

    Option 2. Downstream of Ptrap but before elbow

    AAV
    L
    ------------l---------P-Trap
    l
    l
    L
    L
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #2

    Jan 5, 2009, 05:10 AM
    Hi RMH:

    The AAV should be located within a few feet of the p-trap. It can be piped on the horizontal at least 6-12" above the pipe (picture 1 on left), or it can be on top of the vertical pipe above the ptrap (picture 2 on right). The AAV must remain accessible in case it needs to be changed in the future.

    Let me know if need more...

    MARK
    Attached Images
     
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #3

    Jan 5, 2009, 08:57 AM
    Quote Originally Posted by RockyMtnHigh View Post
    Long story short our kitchen sink in our house needs an AAV as a result of a renovation. My question is to the exact location of the AAV downstream from the p-trap. Thankyou in advance for any advice.

    RMH

    Option 1. Place it ontop of the "T"

    AAV
    l
    l--------------------P-Trap
    l
    l
    l

    or....

    Option 2. Downstream of Ptrap but before elbow

    AAV
    l
    ------------l---------P-Trap
    l
    l
    l
    l
    How's this grab you? (see image) Good luck, Tom
    dclynch's Avatar
    dclynch Posts: 202, Reputation: 19
    Full Member
     
    #4

    Jan 5, 2009, 12:04 PM
    Are AAVs allowed in Mass residential codes?
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #5

    Jan 5, 2009, 04:05 PM
    Hi Dennis...


    NO... AAVs are NOT allowed in Massachusetts residentially or commercially.

    You can appeal to the local plumbing inspector for a variance, but I have only seen 1 approved in 26 years!

    Let us know if need more here...

    MARK

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Stem Placement [ 7 Answers ]

We are replacing the stems on the hot/cold faucets of our 3 handle tub/shower. We have tried placing the stems facing many different directions, but still we can not get the faucets to turn on and off properly. What are we doing wrong? No directions came with the Danco 3S-9H/C stems. Any help...

Wye Placement [ 4 Answers ]

Hello All, I have a question as to the correct placement of a wye fitting. This is a 3" wye from a toilet that is draining into the main line. After installing this I realized that the wye may need to be placed more on its side, rather than almost upright. I'm imagining the water just flowing...

Panel Placement [ 4 Answers ]

Per NEC can an electrical panel be located inside a employees "coat room?" LA county requires a coat room, and I'm out of space to locate the panels. Any help is appreciated. Also, if you can point me to the NEC section I would greatly appreciate it.

Toolbar placement [ 3 Answers ]

I feel ridiculous. Somehow I managed to move the toolbar (clock, LAN settings, virus protection on the right; short cuts like IE, FOXfire, etc. on the left) from the bottom of my computer screen, around to the right, and then to the top of my screen and I can't seem to move it back. There must be...


View more questions Search