    Older gas furnace is short cycling
    I have an older Sears "Fifteen" horizontal gas furnace (#867767840) located in the crawl space. Recently it has been short cycling, meaning it starts a normal cycle, runs for approximately 1 minute, stops for several minutes, then starts another 1 minute cycle. This repeats until the set temperature is achieved. Also, the pilot light has gone out twice in the past two weeks.

    Filters are new, all vents are open, returns are unobstructed.

    So, I first replaced the thermocouple. And the pilot hasn't gone off again in several weeks, but the short cycling continues. I then replaced the thermostat. No change. What other things should I check? I am thinking it must be either a leak in the heat exchanger, or a faulty limit switch. Any help would be appreciated.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Dec 9, 2008, 01:57 PM
    On the old systems there is a fan limit control. It cuts the furnace off if it overheats and also controls the blower so when the temperature is right the blower turns on and then off. Check the fan and limit.

    Also

    It could also be the blower motor since if it will not run or turn on the unit will cut off on high temperature.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #3

    Dec 9, 2008, 09:12 PM

    Check the rating plate for the specified temperature rise (difference between the return and supply air temperatures)-usually a range is given. If you find that the rise is higher than the specified range, the furnace is overheating. This usually results from inadequate airflow or excessive gas input. Overheating will generally cause short-cycling via high limit control.
    L_to_the_W's Avatar
    L_to_the_W Posts: 13, Reputation: 1
    New Member
     
    #4

    Dec 10, 2008, 06:11 AM

    Thanks for your responses.

    KC13 - where should I take the temperature readings to determine the rise? Also, what would cause excessive gas input?
    L_to_the_W's Avatar
    L_to_the_W Posts: 13, Reputation: 1
    New Member
     
    #5

    Dec 12, 2008, 04:38 PM
    I had a chance to observe the cycling of the fan limit control, and I noticed the following:

    Limit set points:
    1.Fan off ~90 deg.
    2.Fan on ~130 deg.
    3.Limit off ~175 deg.

    Starting temp. in house is 61 deg.; Set thermostat to 68 deg.

    The furance receives the call for heat, burners turn on, limit begins to spin.
    The fan turns on normally as soon as the 'Fan On' limit is tripped.
    But as soon as the fan starts blowing air the limit quickly spins down, and within 45-60 seconds it trips the 'Fan Off'. Adjusting the 'Fan Off' set point down to about 70 deg. Seems to keep it from tripping prematurely, but this also causes the fan to run for quite some time after the gas shuts off.

    Is this indicative of a weak/faulty limit? Or is there something else causing the air to cool down too fast after the fan turns on?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Dec 12, 2008, 04:57 PM
    It is a good possibility that the bimetal used in the control has lost its tension. Time for a new one.

    It is also a possibility that the furnace is not firing at a full rate which could cause the same situation. Check the gas pressure leaving the gas valve or at the gas train tap to see if it matches the rate plate.
    L_to_the_W's Avatar
    L_to_the_W Posts: 13, Reputation: 1
    New Member
     
    #7

    Dec 12, 2008, 06:25 PM
    Thanks again hvac1000.

    Can you clarify...
    The rate plate you mentioned. Is that on the gas valve or the furnace?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Dec 12, 2008, 06:53 PM
    On the furnace. It will be in inches of water column
    L_to_the_W's Avatar
    L_to_the_W Posts: 13, Reputation: 1
    New Member
     
    #9

    Dec 12, 2008, 08:50 PM
    I just noticed something.

    When the limit control triggers the fan to run, the burners are turning off. Thus, the air cools down quite quickly, and the short cycle ensues. I assume that the burners should stay lit until the thermostat has been satisfied.. And in fact, I have seen the burners stay lit after the fan comes on, but this seems to happen sporadically and infrequently. What would cause this?
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #10

    Dec 12, 2008, 08:56 PM
    Does the limit trip before the fan starts?
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #11

    Dec 12, 2008, 09:10 PM

    At what indicated temperature does this occur (on the limit dial face)? The fan control portion of the fan/limit control isn't working right, or the switch trippers are not set correctly. As someone said, may be time for a new one.
    L_to_the_W's Avatar
    L_to_the_W Posts: 13, Reputation: 1
    New Member
     
    #12

    Dec 12, 2008, 09:21 PM
    Yeah it's weird... the limit control "appears" to be functioning properly.

    I just watched it go through a few more cycles. The burners fire up, the limit control spins until it clicks the 'fan on' set point, then the burners go off and the fan comes on, the limit spins down until the 'fan off' set point clicks, the burners come back on... (repeat). Except that on the third or fourth cycle... the burners finally stayed on when the 'fan on' set point clicked.

    Anyway... I think I'll be replacing the limit control as the next measure, unless anyone has a better idea. Thanks again for the input everyone.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #13

    Dec 12, 2008, 09:27 PM

    Try turning the "fan on" down just a little, see what that does.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #14

    Dec 12, 2008, 09:38 PM

    If you are truly thankful, fruit baskets make lovely gifts...
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #15

    Dec 12, 2008, 10:00 PM

    Huh?
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #16

    Dec 12, 2008, 10:32 PM

    Just kiddin' about the fruit baskets... it's an ESPN thing... you should understand...
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #17

    Dec 13, 2008, 12:52 AM
    Replace fan and limit control. Its old and worn out.
    L_to_the_W's Avatar
    L_to_the_W Posts: 13, Reputation: 1
    New Member
     
    #18

    Dec 18, 2008, 05:37 PM
    Well, I replaced the fan/limit control, but the problem persists.

    I'm not sure what else to do.
    My only other guess as to the problem would be a short in the wiring (or incorrect wiring) between the thermostat and furnace, or between the furnace and gas valve. (I've never changed the wiring, other than replacing the thermostat.) Seems that it has to be something electrical in nature since the burners are turning off in synch. With fan turning on.

    Any more ideas?
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #19

    Dec 18, 2008, 06:29 PM

    Wait a minute, I don't think you mentioned replacing the thermostat before... did this problem develop afterward?
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #20

    Dec 18, 2008, 07:41 PM

    When the blower comes on does the flames 'roll out' or get squirrely? If so you may very well have a cracked heat exchanger.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Amana furnace short cycling [ 2 Answers ]

The induction motor comes on then the heat it's stay's on for two mines then cut off it short cycling all nights. Is this a bad pressue switch ,or abad board

Bryant furnace short cycling [ 4 Answers ]

I have a Bryant 80 furnace , had the ignitor replaced in November. Since then the furnace will power up, ignitor and burners will go and then when the blower turns on the burners go out, the blower will go for about 90 seconds and then shut down. It will do this repeatedly sometimes as many as 30...

Furnace Keeps Short-Cycling [ 1 Answers ]

I have a Trane XL80 (Model #TUD060A936A0) that has been converted to a White-Rodgers (Model #50E47-060). When the thermostat calls for heat, the furnace short cycles until it is manually shut off. There is no indicator light on this unit to tell me what the problem may be. What else could...

WELL Pump is short cycling on and off [ 3 Answers ]

I have a well pump on a 40 60 pressure switch. When a tap is open the pump kicks on and off every 30 seconds or so. The pressure tank is small probably 40gal? When the water is flowing you can watch the pressure gauge drop in pressure, and then watch as it moves up when the pump kick in for 20...

Heil furnace short cycling of burner [ 1 Answers ]

My 1983 heil model NUGK075DG01, natural gas, forced air furnace is running but only heats the house to 67 degrees no matter how high I set the temp, the fan continuously runs (in auto on thermostat) and the burner will cycle for 3-4 min. then shut-off for 10 min.. I have powered down and back-on,...


View more questions Search